首页 > 器件类别 > 电路保护 > 保险丝 > 特种保险丝
1003R1C5.5SW
特种保险丝 100A 5.5KV MV 3R R-RATED HOOKEYE
器件类别:电路保护    保险丝    特种保险丝
厂商名称:Littelfuse
厂商官网:http://www.littelfuse.com
厂商名称
Littelfuse
特种保险丝
发货限制
Mouser目前不销售该产品。
R-Rated
产品
Medium Voltage Fuses
主体类型
Cartridge Fuses
电流额定值
100 A
电压额定值 AC
5.5 kVAC
安装风格
Holder
端接类型
Clip
保险丝类型
Medium / Normal Blow
封装
Bulk
类型
Cylindrical Fuse
工厂包装数量
POWR-GARD
Fuse Datasheet
MEDIUM VOLTAGE FUSES
2,400-38,000 VAC • Current-Limiting
Current-limiting E- and R-rated
fuses are equipped with a
mechanical indicator or striker pin
that protrudes through the fuse
cap upon operation of the fuse.
This provides visual identification
of a blown fuse and can be used
as a trigger for external devices.
Note: Extension distance
” minimum;
extension force 2 lb. minimum.
General Information
The terms “Medium Voltage” and “High Voltage” have been
used interchangeably by many people to describe fuses
operating above 600 volts. Technically speaking, medium
voltage fuses are those intended for the voltage range from
2,400 to 38,000 Vac. High voltage fuses are for circuits
carrying voltages greater than 38,000 Vac.
E-rated fuses are considered to be general purpose fuses
and can be used to protect against low and high values
of fault current. R-rated fuses are designed for back-up
protection. They must be used in series with other devices
such as motor overload relays in order to achieve both
overload and short-circuit protection.
Medium voltage fuses are not intended to provide overload
protection in the same sense as fuses rated 600 volts or
less. Medium voltage fuse current ratings do not have the
same meanings as the ampere ratings of low voltage fuses.
All medium voltage fuses are limited in their ability to
interrupt low value overcurrents, especially those between
100% and 200% of the fuse’s continuous current rating.
They are designed to carry their rated current without
exceeding the temperature rise permitted by NEMA and
ANSI standards.
Littelfuse
offers a selection of E- and R-rated medium
voltage fuses for the protection of transformers, potential
transformers, feeders, and motor circuits. Single, double,
and triple barrel designs are available to cover a wide range
of current, voltage, and interrupting ratings. Conventional
ferrule type, clip lock, and bolt-in mounting configurations
are available for virtually any application. Hermetically sealed
fuses for use in hazardous environments are also offered.
Contact the factory or your local Littelfuse representative for
additional fuse ratings or custom mounting configurations.
24-Hour Emergency Service - Call 800-227-0029
• Power Transformer Protection
• Potential Transformer Protection
• Motor Controller Back-up Protection
• Fused Switches
• Feeder Circuits
Bolt-in Mount Fuses
littelfuse.com
1 of 10
© 2016 Littelfuse POWR-GARD
Products
Rev: 120816
POWR-GARD
Fuse Datasheet
R-RATED MEDIUM VOLTAGE FUSES
R-rated fuses provide required short-circuit protection for
medium voltage motors, motor controllers and associated
circuitry. These components have limited ability to absorb the
energy of large short-circuit currents. Medium voltage motor
controllers contain overload relays which provide both overload
protection and locked rotor protection to the motor. The
controllers are also intended to interrupt low value short-circuits
within the capability of the motor controller. This protects the
medium voltage fuse from sustained overcurrents which are
less than their minimum interrupting rating.
NEMA Standards for R-rated medium voltage power fuses
require they operate within 15-35 seconds when subjected
to an rms current 100 times the R rating. For example, a
fuse with a 2R rating will open within 15 to 35 seconds on
an applied current of 2 x 100 = 200 amperes.
Characteristics
Voltage Ratings
Current Range
2,750 V – 8,250 V
2R – 36R
Options
• Hermetically sealed for use in hazardous locations
(add “S” suffix to part number)
• Bolt-in mounting configurations
Hookeye Feature*
For hookeye attachment; add “W” suffix
to part number
Ordering Number
130-4R-1C-5.5
Max Voltage (KV)
Style:
C (Cartridge)
B (Bolt Mount)
IB (Inverted Bolt Mount)
BI (Bolt-In Mount)
*See web for Bolt Mount, Inverted Bolt Mount, and Bolt-In dimensions
Dimensions
3"DIA
6.38"
No. of Barrels
Rating (size)
Continuous Current
9.75"
Medium Voltage
Fuse Protection
POWR-GARD
medium
voltage fuses provide
for motors and
transformers rated
2,400 to 38,000 volts AC.
Visit
littelfuse.com/MediumVoltage
to
download the white paper featuring protection
tables, sizing recommendations, and applications.
Dim.A
Clip
Center
Dim.B
Figure 1
Cartridge “C”
Figure 2
DD
Figure 3
DDD
Bolt Mount “B”
Sample Part #: 130-4R-1B-5.5
Inverted-Bolt “IB”
Sample Part #: 130-4R-1IB-5.5
Bolt-In Mount “BI”
Sample Part #: 130-4R-1BI-5.5
littelfuse.com
2 of 10
Products
Rev: 120816
POWR-GARD
Fuse Datasheet
RATED
ORDERING/
CATALOG
NUMBER
702R1C2.75
1003R1C2.75
1304R1C2.75
1505R1C2.75
1706R1C2.75
2009R1C2.75
23012R1C2.75
39018R2C2.75
45024R2C2.75
ORDERING/
CATALOG
NUMBER
702R1C5.5
1003R1C5.5
1304R1C5.5
1505R1C5.5
1706R1C5.5
2009R1C5.5
23012R1C5.5
39018R2C5.5
45024R2C5.5
48026R2C5.5
55030R2C5.5
60032R2C5.5
65036R2C5.5
55030R3C5.5
60032R3C5.5
65036R3C5.5
ORDERING/
CATALOG
NUMBER
702R1C5.5X
1003R1C5.5X
1304R1C5.5X
1505R1C5.5X
1706R1C5.5X
2009R1C5.5X
23012R1C5.5X
39018R2C5.5X
45024R2C5.5X
55030R2C5.5X
ORDERING/
CATALOG
NUMBER
702R1C8.25
1003R1C8.25
1304R1C8.25
1505R1C8.25
1706R1C8.25
2009R1C8.25
23012R1C8.25
39018R2C8.25
45024R2C8.25
SIZE
2R
3R
4R
5R
6R
9R
12R
18R
24R
MAXIMUM
CONTINUOUS
CURRENT @
40 DEGREES C°
390
450
MAXIMUM
CONTINUOUS
CURRENT @
40 DEGREES C°
390
450
480
550
550
MAXIMUM
CONTINUOUS
CURRENT @
40 DEGREES C°
390
450
550
MAXIMUM
CONTINUOUS
CURRENT @
40 DEGREES C°
390
450
DIM. A
(INCHES)
7"
7"
7"
7"
7"
7"
7"
7"
7"
DIM. A
(INCHES)
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
DIM. A
(INCHES)
14"
14"
14"
14"
14"
14"
14"
14"
14"
14”
DIM. A
(INCHES)
12"
12"
12"
12"
12"
12"
12"
12"
12"
DIM. B
(INCHES)
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
DIM. B
(INCHES)
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
DIM. B
(INCHES)
17.875"
17.875"
17.875"
17.875"
17.875"
17.875"
17.875"
17.875"
17.875"
17.875”
DIM. B
(INCHES)
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
MINIMUM
INTERRUPTING
RATING RMS
AMPS
170
250
340
390
1950
MINIMUM
INTERRUPTING
RATING RMS
AMPS
170
250
340
390
1950
2100
2400
2600
2900
2400
2600
2900
MINIMUM
INTERRUPTING
RATING RMS
AMPS
170
250
340
390
1950
2400
MINIMUM
INTERRUPTING
RATING RMS
AMPS
190
225
330
440
955
1440
1910
MAXIMUM
INTERRUPTING
RATING RMS
(ASYM)*
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
MAXIMUM
INTERRUPTING
RATING RMS
(ASYM)*
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
MAXIMUM
INTERRUPTING
RATING RMS
(ASYM)*
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
MAXIMUM
INTERRUPTING
RATING RMS
(ASYM)*
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
FIGURE
NUMBER
FIGURE
NUMBER
FIGURE
NUMBER
FIGURE
NUMBER
RATED
2.75 KV
SIZE
2R
3R
4R
5R
6R
9R
12R
18R
24R
26R
30R
32R
36R
30R
32R
36R
RATED
5.5 KV
SIZE
2R
3R
4R
5R
6R
9R
12R
18R
24R
30R
RATED
5.5 KV
14”CLIP CENTERS
SIZE
2R
3R
4R
5R
6R
9R
12R
18R
24R
* RMS Asymmetrical amperes = RMS Symmetrical amperes x 1.6
For hookeye attachment add “W” suffix to part number
8.25 KV
littelfuse.com
3 of 10
Products
Rev: 120816
POWR-GARD
Fuse Datasheet
E-RATED MEDIUM VOLTAGE FUSES
E-rated fuses have time current characteristics designed to
provide current-limiting protection for power transformers,
potential transformers, power centers, feeder centers, and
unit sub stations. When properly applied, they can protect
against high and low fault currents.
NEMA Standards for E-rated medium voltage fuses require
that fuses rated 100E or less open within 300 seconds
(5 minutes) when subjected to an RMS value of 200-240%
of the fuse continuous current rating; and fuses with an
E rating larger than 100E must open within 600 seconds
(10 minutes) when subjected to an RMS current of 220-
240% of the fuse’s continuous current rating. These values
establish one point on the time-current curve.
Characteristics
Voltage Ratings
Current Range
2,750 V – 38,000 V
10E – 600E
Options
• Clip-lock (CL) available.
Dimensions
3"DIA
6.38"
9.75"
Application Note
Since these fuses are used for the protection of general
purpose circuits which may contain transformers, motors,
and other equipment producing in-rush and/or overload
currents, fuses should generally be rated at 140% of the
normal full load current, and circuits should be analyzed
to ensure that system load currents will not exceed the
current rating of the fuse.
Dim.A
Clip
Center
Dim.B
Figure 4
Figure 5
DD
Figure 6
DDD
E-RATED
ORDERING/CATALOG
NUMBER
10E1C2.75
15E1C2.75
20E1C2.75
25E1C2.75
30E1C2.75
40E1C2.75
50E1C2.75
65E1C2.75
80E1C2.75
100E-1C2.75
125E1C2.75
150E1C2.75
200E1C2.75
125E2C2.75
150E2C2.75
200E2C2.75
250E2C2.75
300E2C2.75
350E2C2.75
400E2C2.75
450E2C2.75
SIZE
10E
15E
20E
25E
30E
40E
50E
65E
80E
100E
125E
150E
200E
125E
150E
200E
250E
300E
350E
400E
450E
DIM. A (INCHES)
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
7"
DIM. B (INCHES)
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
10.875"
MAX INTERRUPTING
RATING RMS (ASYM)*
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
FIGURE
NUMBER
2.75 MAX. KV
littelfuse.com
4 of 10
Products
Rev: 120816
POWR-GARD
Fuse Datasheet
E-RATED
ORDERING/CATALOG
NUMBER
10E1C5.5
15E1C5.5
20E1C5.5
25E1C5.5
30E1C5.5
40E1C5.5
50E1C5.5
65E1C5.5
80E1C5.5
100E1C5.5
125E1C5.5
150E1C5.5
175E1C5.5
200E1C5.5
125E2C5.5
150E2C5.5
175E2C5.5
200E2C5.5
250E2C5.5
300E2C5.5
350E2C5.5
400E2C5.5
450E2C5.5
500E3C5.5
550E3C5.5
600E3C5.5
SIZE
10E
15E
20E
25E
30E
40E
50E
65E
80E
100E
125E
150E
175E
200E
125E
150E
175E
200E
250E
300E
350E
400E
450E
500E
550E
600E
DIM. A (INCHES) DIM. B (INCHES)
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
12"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
15.875"
MAX INTERRUPTING
RATING RMS (ASYM)*
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
FIGURE NUMBER
5.5 MAX. KV
E-RATED
ORDERING/CATALOG
NUMBER
5NLE10E
5NLE15E
5NLE20E
5NLE25E
5NLE30E
5NLE40E
5NLE50E
5NLE65E
5NLE80E
5NLE100E
5NLE125E
5NLE150E
5NLE175E
5NLE200E
5NLE2225E
5NLE2250E
5NLE2300E
5NLE2350E
5NLE2400E
5NLE2450E
SIZE
10E
15E
20E
25E
30E
40E
50E
65E
80E
100E
125E
150E
175E
200E
225E
250E
300E
350E
400E
450E
14”
14”
14”
14”
14”
14”
14”
14”
14”
14”
14“
14”
14”
14”
14”
14”
14”
14”
14”
14”
17
MAX INTERRUPTING
RATING RMS (ASYM)*
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
80,000
FIGURE NUMBER
5.5 MAX. KV
littelfuse.com
5 of 10
Products
Rev: 120816
基于FPGA的图像裁剪电路的设计与实现
基于FPGA的图像裁剪电路的设计与实现 ...
至芯科技FPGA大牛 FPGA/CPLD
Altium Designer不能打印
生成的pdf也不全 Altium Designer不能打印 怎的不能打印呢? AD的打印功能应该是比...
PCB板 模拟电子
射频电路PCB设计中放大器需要注意什么
在微波频段,如何保证放大器的输出信号不会反馈到输入端,多级放大器的连接需要注意什么?有没有大神解释一...
明天你好123 PCB设计
求大神帮我分析一下这两个电路
看资料说是什么巴特沃斯型滤波器,但是我找不到他们的截止频率的算法~~ 求各位大神帮忙分析一下~~~ ...
lx_csu 微控制器 MCU
高手帮忙分析,可行性(chunyang大哥请进)
看到DIY的活动,有意参加。目前只是简单的想法,使用PI的软件设计出框架,然后修改控制部分,替换开关...
lyzhangxiang DIY/开源硬件专区
C中如何直接直接嵌入汇编的方法
在学单片机...看到这个...感觉不错.发来和大家共享下... C中如何直接 直接嵌入汇编的方法...
wangda 单片机
