Protection type : Current limiting, delay shut down o/p voltage, re-power on to recover
110 ~ 135% Follow to output set up point
Protection type : Shut down o/p voltage, re-power on to recover
>100 / measure by heat sink, near transformer
Protection type : Shut down o/p voltage, recovers automatically after temperature goes down
-20 ~ +65 (Refer to output load derating curve)
20 ~ 90% RH non-condensing
-20 ~ +85
, 10 ~ 95% RH
0.04% / (0 ~ 50 )
10 ~ 200Hz, 2G 10min./1cycle, 60min. each along X, Y, Z axes
UL60950, TUV EN60950-1 approved
I/P-O/P:3KVAC
I/P-FG:1.5KVAC
O/P-FG:0.5KVAC
/ 70% RH
82%
84%
85%
86%
89%
89%
0.5%
1.0%
0.5%
0.5%
0.5%
0.5%
0.5%
0.5%
0.5%
0.5%
0.5%
0.5%
SETUP, RISE, HOLD UP TIME
500ms, 200ms, 16ms at full load
260 ~ 370VDC see the derating curve
90%
90%
ISOLATION RESISTANCE
I/P-O/P, I/P-FG, OP/FG:100M Ohms / 500VDC / 25
EMI CONDUCTION & RADIATION
Compliance to EN55022 (CISPR22) class A
Compliance to EN61000-3-2,3
HARMONIC CURRENT
EMS IMMUNITY
POWER GOOD SIGNAL
SPECIAL FUNCTION
COOLING
MTBF
DIMENSION
PACKING
Compliance to EN61000-4-2,3,4,5,6,8,11, light industry level, criteria A
Open collector of NPN transistor
DC Voltage Adj., remote sensing, remote control, parallel operation(refer to control terminal instruction manual)
By fan, >20% load or >50 fan on
37.4K hrs min. MIL-HDBK-217F(25
290*120*132mm (L*W*H)
5kg; 4pcs /21kg /CARTON
OTHERS
NOTE
1. All parameters NOT specially mentioned are measured at 230VAC input, rated load and 25 of ambient temperature.
2. Ripple & noise are measured at 20MHz of bandwidth by using a 12" twisted pair-wire terminated with a 0.1uf & 47uf parallel capacitor.
3. Tolerance : includes set up tolerance, line regulation and load regulation.
4. Current limiting 3 times(1.5s,3.0s,5.0s)Then intelligent auto recovery before shut down
5. The power supply is considered a component which will be installed into a final equipment. The final equipment must be re-confirmed that it still meets
EMC directives.
File Name: SCP-1K2-SPEC
2008-05-06
900~1200W Parallel (N+1) With PFC Function
Mechanical Specification
SCP-1K2
series
Unit:mm
290
AC INPUT
#6-32-4
M3(NUT) 3H-4
TB1
1 2 3 4 5 6 7 8
Vadj
103
LED
POS+
NEG-
LED
251
M3(NUT) 3H-4
Air flow
direction
Terminal Pin No. Assignment
Pin No.
Assignment
AC/L
AC/N
FG
Control terminal Pin No. Assignment (TB1) : Dinkle 51HDBC-O8P or equivalent