首页 > 器件类别 > 电路保护 > 电路保护
3120-F311-P7T1-W02A-0.5A
1 POLE(S), 0.5A, 250 V(AC), 50 V(DC), PANEL MOUNT, THERMAL CIRCUIT BREAKER,
器件类别:电路保护    电路保护
厂商名称:E-T-A [E-T-A Circuit Breakers]
Objectid
1145921335
compliant
YTEOL
执行器类型
ROCKER
主体宽度
21 mm
主体高度
33 mm
主体长度或直径
54 mm
电路功能
MANUAL ON/OFF
电路保护类型
安装特点
PANEL MOUNT
极数
60 °C
-30 °C
额定分断能力
5 A
额定电流
0.5 A
额定电压(交流)
250 V
额定电压(直流)
50 V
参考标准
CCC; CSA; UL; VDE
表面贴装
NO
端子形状
QUICK CONNECT
Thermal Overcurrent Circuit Breaker 3120-F...
An extremely versatile range of rocker switch/thermal circuit breakers
(S-type TO CBE to EN 60934 with trip free mechanism) offering the choice
of single pole, double pole with single pole protection, and double pole
with protection on both poles. Designed for snap-in panel mounting with
versions available for three different panel cut-out sizes. Illumination is
optional and there is a range of colours and markings for the rocker.
Add on modules:
Under voltage release coil (for double pole versions only).
Magnetic trip coil for short circuit protection.
Magnetic trip coil for remote relay trip.
Auxiliary contacts for status signalling.
Approved to CBE standard EN 60934 (IEC 60934).
Meets the requirements regarding fire resistance of EN 60335-1 : 2007-02
Safety of household and similar electrical appliances.
3120-F3...F5
Typical applications
Technical data
Motors, transformers, solenoids, extra low voltage wiring systems, office
machines, electro-medical equipment, power supplies, communications
systems, medical equipment to EN 60601.
Standard current ratings and typical internal resistance values
Current rating
(A)
0.1
0.2
0.3
0.4
0.8
Internal
resistance
per pole (Ω)
94
24
4.20
2.90
1.50
0.9
0.80
0.45
0.27
0.0785
0.0595
0.0565
Current rating
(A)
Internal
resistance
per pole (Ω)
0.0435
0.0435
0.0325
0.0215
0.0165
0.0165
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
Dielectric strength
(IEC 60664 and 60664A)
operating area
between poles (2-pole)
Insulation resistance
Interrupting capacity I
cn
3120-F7
For further details please see chapter: Technical Information
Voltage rating
AC 240 V; DC 50 V
(AC 415 V to special order)
(UL: AC 250 V; DC 50 V)
Current ratings
0.1...20 A
(up to 30 A to special order, single pole only)
Typical life
AC 240 V:
DC 50 V:
DC 28 V:
AC 415 V:
AC 240 V:
0.1...20 A
0.1...4 A
4.5...16 A
0.1...20 A
0.1...16 A
0.1...16 A
17...20 A
DC 50 V:
0.1...16 A
17...20 A
Ambient temperature
Insulation co-ordination
(IEC 60664 and 60664 A
1-pole
30,000 operations at 1 x I
, inductive
, inductive
, resistive
, inductive
2-pole
10,000 operations at 1 x I
, inductive
50,000 operations at 1 x I
, inductive
, inductive
, inductive
, inductive
-30...+60 °C (-22...+140 °F)
rated impulse
pollution
withstand voltage
degree
2.5 kV
reinforced insulation in operating area
Illumination voltage/power consumption
operating voltage
12 V DC
24 V DC
115 V AC
230 V AC
power consumption
Y+R
2 mA
2 mA
0.9 mA
0.9 mA
3.5 mA
3.5 mA
2.8 mA
2.8 mA
test voltage
AC 3,000 V
AC 1,500 V
> 100 MΩ (DC 500 V)
0.1...2 A 10 x I
2.5...20 A 250 A 2-pole, or 150 A 1-pole
Interrupting capacity (UL 1077)
1, 2-pole
1, 2-pole
Degree of protection
(IEC 60529/DIN 40050)
Vibration
0.1...20 A
0.1...20 A
U
AC 250 V
DC 50 V
nc
5000 A
1000 A
Approvals
Authority
VDE (EN 60934)
Voltage ratings
AC 240 V; DC 28 V
DC 50 V
DC 50 V
AC 250 V; DC 50 V
AC 250 V; DC 50 V
Current ratings
0.1...20 A
0.1...20 A
2-pole
0.1...10 A
1-pole
0.1...20 A
0.1...20 A
Shock
Corrosion
Humidity
Mass
UL, CSA
CCC
operating area IP40
(IP54 with water splash protection)
terminal area IP00
8 g (57-500 Hz), ± 0.61 mm (10-57 Hz)
to IEC 60068-2-6, test Fc
10 frequency cycles/axis
30 g (11 ms)
to IEC 60068-2-27, test Ea
96 hours at 5 % salt mist,
to IEC 60068-2-11, test Ka
240 hours at 95 % RH,
to IEC 60068-2-78, test Cab
approx. 33 g (double pole)
approx. 27 g (single pole)
Issue D
www.e-t-a.de
Ordering information
Type No.
3120
rocker switch/circuit breaker
Mounting
snap in frame
Size of frame
to fit mounting cut-out 50.5 x 21.5 mm
panel thickness: 1-6.35 mm (.039-.250 in)
to fit mounting cut-out 44.5 x 22 mm
panel thickness: 1-4 mm (.039-.157 in)
to fit mounting cut-out 45 x 33.7 mm
panel thickness: 1.2-2.4 mm (.047-.094 in)
Number of poles
2-pole, unprotected, switch only
1-pole, thermally protected
2-pole, thermally protected
2-pole, 1-pole thermally protected
Mounting frame design (F3 & F5)
collar height 1 mm
collar height 9 mm
collar height 2 mm with water splash protection (IP54)
Mounting frame design (F7)
black
black with snap-on splash cover
Terminal configuration
P7
blade terminals, standard for curve T1
(thermal circuit breaker)
H7
as P7, terminals 11 and 21 with flat head screws M3.5
– standard for units with undervoltage release module
N7
as P7, but with additional shunt terminals 12(i) and 22(i) –
standard for version Q1 (switch only)
Dimensions
Style F7.R
15.5
.610
48
±0.2
1.89
±.008
44.2
-0.2
1.74
-.008
8.9
.350
33
1.30
12(i)
12(k)
LINE
.827
10.7
.421
3.5
.138
15.5
.610
41
1.61
blade terminals DIN 46244-C-Ms-S
(QC 2 x .110)
flat head screw ISO1580 M3.5x5-MS
tightening torque max. 0.8 Nm
Style F7.T
34
1.34
18.6
.732
44.8
1.76
Characteristic curve
T1
thermal 1.01 - 1.4 x I
Q1
switch only
Actuator style
standard rocker (F3 & F5)
specially designed rocker (F7)
Colour and Illumination
01 .
rocker black opaque
without illumination
02 .
rocker white opaque
04 .
rocker red opaque without illumination
14 . R
rocker red translucent with
LED-illumination
15 . Y
rocker orange translucent with
LED-illumination
19 . G
rocker green translucent with
LED-illumination
Rocker markings for F3 and F5
Q: as D, but
moulded in
X: without markings
A D F X
Rocker markings for F7
»I« and »O« moulded in
Illumination voltage range
10 - 14 V DC
20 - 28 V DC
90 - 140 V AC
185 - 275 V AC
Current ratings
0.1...20 A
ON
0 OFF
1.30
12(i)
12(k)
LINE
.827
10.7
.421
3.5
.138
15.5
.610
41
1.61
(QC 2 x .110)
Preferred types
Preferred types
Preferred types
0.5 1
F3/1-pole protected
3120-F311-P7T1-
W02D-
x
EW
Standard current ratings (A)
x
x
x
8 10 12 15 16 20
x
x
x
x
Preferred types
0.5 1
F3 /2-pole protected
3120-F321-P7T1-
W01D-
x
x
x
x
x
x
x
8 10 12 15 16 20
x
x
x
x
x
x
3120 - F 7 2 R - P7 T1 - A 14 Q R 4 - 10 A
ordering example
3120 - F . 0 . - N7 Q1 - W ..
. . . - 20 A
(switch)
Preferred types
0.5 1
F5/2-pole protected
3120-F521-P7T1-
W01D-
x
x
x
x
x
x
8 10 12 15 16 20
x
x
x
x
x
x
Preferred types
EW
Preferred types Standard current ratings (A)
F7/2-pole
0.5 1 1.5 2 3 4 5 6 8 10 12 15 16 20
protected
3120-F72R-P7-
x
x
x
x
x
x
x
x
x
x
x
x
x
x
T1-A14QQR4-
www.e-t-a.de
Issue D
11.5
.453
Internal connection diagrams
2-pole,
thermally protected on both poles
line
21
Mounting style variants
Style F 3.3
collar height 9 mm (.354 in.)
19.5
.768
54
2.13
2-pole,
thermally protected on one pole only
line
21
12(i)
12(k)
22(i)
22(k)
12(i)
12(k)
22(i)
33
1.30
load
load
line
Netz
21
21
.827
10.7
.421
3.5
.138
12(i)
12(k) load
22(i)
12(i)
Last
22(i)
(QC 2x.110)
flat head screw M3.5x5-MS ISO1580
15.5
.610
41
1.61
1-pole,
thermally protected
2-pole,
unprotected
12(i) 12(k)
Style F 3.4
collar height 2 mm (.079 in.), with water splash protection
Dimensions
Style F3.1
collar height 1 mm/.039 in.
27
1.06
19.5
.768
56
2.21
Actuating force max. 35 N
optional illumination in ON position
OFF position
54
2.13
3.8
.150
33
1.30
12(i) 12(k)
21
.827
10.7
.421
3.5
.138
(QC 2x.110)
15.5
.610
41
1.61
33
1.30
Style F 5.1
Optional illumination
48
1.89
12(i)
12(k)
3.5
.138
.421
21
15.5
.610
.827
(QC 2x. 110)
33
1.30
12(i) 12(k)
1.61
21
.827
10.7
.421
3.5
.138
15.5
.610
41
1.61
(QC 2x.110)
Installation drawing
Cut-out dimensions
When installing the circuit breaker apply pressure on bezel only
operating area
Cut-out for mounting style -F3
with rocker and push button
- 0.4
-.016
- 0.2
-.008
style -F5/-F7
- 0.4
with rocker
-.016
- 0.2
-.008
min. 2.5
min .098
1-4 mm
.039-.157 in.
min. 2
min .079
.039-.250
1-6.35
max. R2
max .079
±0.05
±.002
max. R1.5
max .059
±0.05
±.002
15.5
.610
mounting area
+1
panel mm 1.2
+0.4
1.6
+0.8
+.016
.063
+.031
.094
+.039
thickness inch .047
+1.1
+0,2
+2.2
dimension mm 45
- 0.05
45
- 0.05
45
- 0.05
+.008
1.77
+.043
+.087
“A”
inch 1.77
- .002
- .002
1.77
- .002
Edges of working parts: ISO 13715
.276 .394
This is a metric design and millimeter dimensions take precedence ( mm )
inch
Issue D
www.e-t-a.de
.846
+.008
21.5
+0.2
max. R0.3
max .012
.866
+.012
22
+0.3
12(i)
12(k)
+0.3
1.99
+.012
max. R0.3
max .012
44.5
+0.2
1.75
+.008
Typical time/current characteristics
single or double pole load
0.1…2 A
10000
+60 °C
+140 °F
+23 °C
+73.4 °F
-30 °C
-22 °F
Trip time in seconds
2.5…20 A
10000
… times rated current
+60 °C
+140 °F
+23 °C
+73.4 °F
-30 °C
-22 °F
The time/current characteristic curve depends on the ambient temperature
prevailing. In order to eliminate nuisance tripping, please multiply the circuit
breaker current ratings by the derating factor shown below. See also section
Technical information.
Ambient
temperature
Derating factor
°F
-30
0.8
-4
-20
0.76
+14
-10
0.84
+32
+73.4
+23
+40
1.08
+122
+50
1.16
+140
+60
1.24
www.e-t-a.de
Issue D
Accessories
Insulated cover
Y 303 068 01
Rear terminal shroud black
(IP64)
Y 304 275 01
40.5
1.59
1.75
-0.25
.069
+.020
-.010
+0.5
.098
20.5
.807
Terminal adapter
Y 303 862 01
R3
.157
.531
3.7
.146
ø8
.315
2.76
+.197
0.9
.035
Water splash cover, transparent
(IP66)
for style -F5..
X 221 619 01
48
1.89
blade terminal DIN 46244-C-Ms-S
(QC 2x.110)
Spacer for 3120-F3...
Y 303 675 01/02
58
2.28
50.5
1.99
ø8
.315
22
.866
28
1.10
3.4
.134
ø4.4
.173
* Y 303 675 01 suitable for
panel thickness < 2 mm (.079 in)
* Y 303 675 02 suitable for
panel thickness < 4 mm (.157 in)
Spacer for 3120-F5...
Y 303 676 01
52
2.05
44.5
1.75
73
2.87
6-way frame for 3120-F5... upon request
sharp-edged
without bends
Blanking piece in -F3 frame
Y 303 885 31
54
2.13
31
1.22
matt finish
16.5
.650
0.8
.031
.098
22.5
.886
28
1.10
41
1.61
21
.827
33
1.30
36
1.42
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications
without notice is reserved.Product markings may not be exactly as the ordering codes.
Errors and omissions excepted.
Issue D
www.e-t-a.de
16.5
.650
