Thermal Overcurrent Circuit Breaker 3130
Single, two and three pole rocker switch/thermal trip free circuit breakers
(S-type TO CBE to EN 60934) of compact design for snap-in panel
mounting. Available either with protection on one/both/all poles or,
in the case of the double pole version, protection on one pole only.
Illumination is optional and there is a choice of rocker colours.
Approved to CBE standard EN 60934 (IEC 60934).
Typical applications
Motors, transformers, solenoids, household and office machines, electrical
tools, mobile homes, boating, construction vehicles, medical equipment
to EN 60601.
1-pole
Standard current ratings and typical internal resistance values
3130
3-pole
Technical data
Current
rating (A)
0.1
0.2
0.3
0.4
Internal resistance Current
per pole (Ω)
rating (A)
94
24
4.20
1.50
0.9
0.80
0.45
0.27
0.0785
0.0595
0.0565
Internal resistance
per pole (Ω)
0.0435
0.0325
0.0215
0.0165
0.0165
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
For further details please see chapter: Technical Information
Voltage rating
AC 240 V; 3 AC 415 V; DC 50 V
(UL: AC 250 V; 3 AC 250 V; DC 50 V)
Current ratings
0.1...20 A 1-pole
0.1...16 A 2- and 3-pole
Typical life
1-pole
AC 240 V: 0.1...20 A 30,000 operations at 1 x I
, inductive
DC 50 V:
0.1...4 A
, inductive
4.5...16 A 30,000 operations at 1 x I
, resistive
DC 28 V:
, inductive
2-pole
AC 240 V: 0.1...16 A 50,000 operations at 1 x I
, inductive
DC 50 V:
, inductive
3-pole
3 AC 415 V: 0.1...16 A 30,000 operations at 1 x I
, inductive
Ambient temperature
-30...+60 °C (-22...+140 °F)
Insulation co-ordination
rated impulse
pollution
(IEC 60664 and 60664 A) withstand voltage
degree
2.5 kV
reinforced insulation in operating area
Dielectric strength
(IEC 60664 and 60664A) test voltage
operating area
AC 3,000 V
current path/current path AC 1,500 V
Insulation resistance
> 100 MΩ (DC 500 V)
Interrupting capacity I
cn
0.1...2 A
10 x I
2.5...20 A
150 A
1-pole
2.5...16 A
250 A
2-pole
2.5...12 A
150 A
3-pole
14 + 16 A
130 A
3-pole
Interrupting capacity (UL 1077)
1, 2-pole
3-pole
1,2-pole
Degree of protection
(IEC 60529/DIN 40050)
Vibration
0.1...16 A
0.1...12 A
0.1...16 A
U
AC 250 V
3 AC 250 V
DC 50 V
nc
3500 A
5000 A
2000 A
Illumination voltage/power consumption
operating voltage
power consumption
1-pole
12 V
24 V
48 V
115 V
230 V
400 V
9 mA
9 mA
9 mA
< 1 mA
< 1 mA
2-/3-pole
Y+R
2 mA
2 mA
2 mA
0.9 mA
0.9 mA
0.9 mA
2-/3-pole
3.5 mA
3.5 mA
3.5 mA
2.8 mA
2.8 mA
2.8 mA
operating area IP40
terminal area IP00
5 g (57-500 Hz) ± 0.38 mm (10-57 Hz)
to IEC 60068-2-6, test Fc
10 frequency cycles/axis
1-pole: 25 g (11 ms) 2 + 3-pole: 20 g (11 ms)
Shock
Corrosion
Humidity
Mass
to IEC 60068-2-27, test Ea
96 hours at 5 % salt mist,
to IEC 60068-2-11, test Ka
240 hours at 95 % RH,
to IEC 60068-2-78, test Cab
approx. 45 g (three pole)
approx. 31 g (double pole)
approx. 17 g (single pole)
1815
www.e-t-a.de
Ordering information - 1-pole
Type No.
3130
single pole thermal circuit breaker
Mounting
snap in frame
Frame
standard
Number of poles
single pole, thermally protected
Frame mounting
panel thickness 1-2.5 mm (.039-.099 in)
Terminal design
P7
blade terminals DIN 46244-C-Ms-S (QC 2x.110)
H7
for terminals 1.1, 2.1 3.1 terminal screws M 3.5
for terminals 1.2, 2.2, 3.2 blade terminals (QC 2x.110)
Characteristic curve
T1
thermal 1.05-1.4 I
Actuator style
rocker switch with marking „I“ and „O“
moulded in
Actuator colour
01 Q
black opaque without illumination
02 Q
white opaque without illumination
04 Q
red opaque without illumination
14 Q R
red translucent with LED-illumination
15 Q Y
orange translucent with
LED-illumination
19 Q G
green translucent with
LED-illumination (DC only)
Illumination voltage range*
10 - 14 V DC
20 - 28 V DC
90 - 140 V AC
185 - 275 V AC
Current ratings
0,1...20 A
3130 - F 1 1 0 - P7 T1 - W 14 Q R
* N/A for non-illuminated version
3 -5A
ordering example
Ordering information - multipole
Type No.
3130
multipole thermal circuit breaker
Mounting
snap in frame
Frame
standard
version for X3130
Number of poles
2-pole thermally protected
3-pole thermally protected
2-pole, 1-pole thermally protected
Frame mounting
2-pole, version for X3130
Terminal design
P7
(characteristic curve T1)
H7
T1
thermal 1.05-1.4 I
Actuator style
moulded in
Actuator colour
01 Q
02 Q
04 Q
14 Q R
LED-illumination
15 Q Y
LED-illumination
19 Q G
LED-illumination
10 - 14 V DC
20 - 28 V DC
90 - 140 V AC
185 - 275 V AC
320 - 450 V AC
Current ratings
0,1...16 A
3130 - F 1 3 0 - P7 T1 - W 14 Q R 7 - 5 A
ordering example
Preferred types
Preferred types
3130 1-pole
3130-F110-P7T1-
W01Q-
Standard current ratings (A)
x
x
x
x
x
x
10 15 16 20
x
x
x
x
Approvals
Authority
VDE
Standard
IEC/EN
60934
Rated voltage Current ratings
AC 240 V
AC 240/415 V
DC 50 V
DC 50 V
DC 28 V
AC 250 V
AC 250 V
DC 50 V
AC 250 V
AC 250 V
DC 50 V
0.1
0.1
0.1
0.1
0.1
0.1
0.1
0.1
0.1
0.1
0.1
A…20 A (single pole)
A…16 A (multipole)
A…8 A (single pole)
A…16 A (multipole)
A…16 A (1 + 2 pole)
A…12 A (3 pole)
A…16 A (1 – 3 pole)
A…16 A (1 + 2 pole)
A…12 A (3 pole)
A…16 A (1 – 3 pole)
UL
UL 1077
CSA
C22.2 No
235
www.e-t-a.de
1815
Dimensions
3130-F110-…
OFF
ON
14.5
.571
terminal for
illumination
conductor size
0.14 mm
(AWG26),
length 180 mm
(7.09 in.)
9.5
.374
5.85
.230
3130-F130-…
OFF
ON
37.5
1.48
32.5
1.28
5.85
.230
33
1.30
I.3
I.2
LINE
I.I
I.3
I.2
LINE
I.I
33
1.30
switch only
34
1.34
(QC 2x.110 P7 or N7)
Side view
34
1.34
unit
Side view
LINE
I.I
LINE
I.I
flat head screw M3.5x5 -MS ISO 1580 (H7)
tightening torque max. 0.8 Nm
R3
Panel cut-out
-0.4
-0.2
-.016
-.008
min. 1.5
min .059
-0.2
-.016
-.008
±0.1
±.004
Panel cut-out
min. 1.5
min .059
.5
< R0
< .0
36
1.42
optional illumination
panel thickness
1-2.5 mm
(.039-.098 in.)
34
+0.2
1.34
+.008
.575
+.008
14.6
+0.2
+0.3
+.012
41
1.61
±0.1
±.004
.5
< R0
.020
panel thickness
1-2.5 mm
(.039-.098 in.)
34
+0.2
1.34
+.008
+0.3
+.012
Edges of working parts: DIN 6784
3130-F120-…
OFF
ON
26
1.02
21
.827
Internal connection diagrams
1-pole
2-pole
line 1.1
line 1.1
2.1
5.85
.230
I.3
I.2
LINE
I.I
33
1.30
34
1.34
unit
1.3
Side view
I.2
load
lamp
1 .2
load
2.2
load
LINE
I.I
3-pole
line 1.1
Panel cut-out
2.1
3.1
min. 1.5
min .059
29.5
1.16
±0.1
±.004
panel thickness
1-2.5 mm
(.039-.098 in.)
.5
< R0
.020
34
+0.2
1.34
+.008
+0.3
+.012
1.2
load
2.2
load
3.2
load
36
1.42
26.1
+0.2
1.03
+.008
This is a metric design and millimeter dimensions take precedence ( mm )
inch
1815
www.e-t-a.de
37.6
+0.2
1.48
+.008
36
1.42
Typical time/current characteristics
Multipole types: all poles symmetrically loaded.
With single pole overload, thermal tripping will be at
approx. 1.54 x I
with 2-pole devices and at
approx. 1.68 x I
with 3-pole devices.
0.1…2 A
10000
+23 °C
+73.4 °F
I.3
I.2
LINE
I.I
Installation drawing 3130-F1...
When installing the circuit breaker apply pressure on bezel only.
operating area
+60 °C
+140 °F
32
1.26
Trip time in seconds
-30 °C
-22 °F
mounting area
Accessories 3130-F130-...
Splash cover, transparent, for 3-pole version
X 221 258 01
(IP54), comprising bezel Y 306 109 01
and transparent cover Y 306 108 01
0.1
2.5…20 A 1-pole
2.5…16 A 2- and 3-pole
10000
… times rated current
+23 °C
+73.4 °F
-30 °C
-22 °F
36.5
1.44
.197
ø4.4
.173
ø11
.433
55
2.17
ø8
.315
0.1
The time/current characteristic curve depends on the ambient temperature
prevailing. In order to eliminate nuisance tripping, please multiply the circuit
breaker current ratings by the derating factor shown below. See also section
Technical information.
Ambient
temperature
Derating factor
°F
-30
0.8
-4
-20
0.84
+14
-10
0.88
+32
+73.4
+23
+40
1.08
+122
+50
1.14
+140
+60
1.23
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications
without notice is reserved.Product markings may not be exactly as the ordering codes.
Errors and omissions excepted.
www.e-t-a.de
41.5
1.63
+60 °C
+140 °F
1815
Appliance Inlet Module X3130 for 2-pole circuit breaker 3130-FA.A
The appliance inlet module X3130 with double pole circuit breaker
3130-FA.A combines three functions within a single component: A C14
appliance inlet and rocker switch with resettable overcurrent protection;
screw mounting from the front or the rear.
Technical data
Rated voltage
Rated current
Ambient temperature
Number of poles
Cable cross section
Mounting method
Terminal design
Housing material
Appliance inlet
Switch
AC 240 V
10 A (IEC)
15 A (UL/CSA)
-25°C ... 70°C
L, N + ground
max. 1.5 mm
Class I
screw-type mounting (front or rear)
blade terminals DIN 46244 A6.3 x 0.8
thermoplastics, black UL94V-0
C14 according to IEC/EN 60320-1, UL 498
circuit breaker type 3130, 2-pole
Electrical medical apparatus, laboratory equipment, professional audio
equipment and office machines.
Type No.
X3130
Appliance inlet module for circuit breaker type 3130-FA.A
Module
appliance inlet C14
Design
04
screw-type mounting
Accessories
00
without
Version
00
not wired; mounting position 3130:
I to connector
01
0 to connector (standard)
Delivery condition
module supplied with
circuit breaker FA.A
X3130 - A
04 00 01 - M
Ordering example
Dimensions
Circuit breaker 3130 (2-pole)
I.3
I.2
LINE
I.I
Approvals
ENEC, UL, CSA, CCC
ø 3.3
36.5
40.2
24
Mounting hole X3130
72
M3/Ø 3.3
Ø.130
82
63.6 ± 0.15
2.50
72 ± 0.2
2.83
1815
www.e-t-a.de
31.6 ± 0.1
1.24