Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-...
Single or multipole hydraulic-magnetic circuit breakers with trip-free-
mechanism and toggle actuation. A choice of switching characteristics
ensures suitability for a wide range of applications. Industry standard
dimensions and panel mounting. Auxiliary contacts optional. Low
temperature sensitivity at rated load.
Approved to CBE standard EN 60934 (IEC 60934) S-type HM CBE.
Typical applications
In the business fields Communication and Transport: power supplies,
switchgear, instrumentation and process control engineering.
8345
1-pole
2-pole
Standard current ratings and typical internal resistance values
Current
rating (A)
0.05
0.1
Trip curves and internal resistance (Ω) per pole
K1, M1, T1,
K2, M2, T2
452
376
0.26
0.10
0.042
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
0.01
0.01
0.01
0.01
0.01
0.01
94
0.90
0.20
0.10
0.040
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
0.01
0.01
0.01
0.01
0.01
0.01
Technical data
Voltage rating
Current rating range
3 AC 415 V; AC 277/480 V;
AC 120/240 V; AC 240 V; DC 80 V,
0.05...125 A single and multipole
150...180 A single pole, two poles
connected in parallel
higher ratings upon request
AC 240 V 6 A; DC 28 V 3 A
DC 65 V 1 A; DC 80 V 0.5 A
10,000 operations at 1 x I
-40...+85 °C (-40...+185 °F)
2.5 kV/2
reinforced insulation in operating area
test voltage
AC 3,000 V
AC 1,500 V
AC 3,000 V
AC 1,500 V
> 100 MΩ (DC 500 V)
operating area IP40
terminal area IP00
10 g (57-2000 Hz) ±0,76mm (10-57Hz)
at 0.9 I
10 g at 1 x I
10 g at 0.8 x I
in all planes.
(57-2000 Hz) ±0.76 mm (10-57 Hz)
to IEC 60068-2-6, test Fc
10 frequency cycles/axis
100 g (11 ms) at 1 x I
100 g (11 ms) at 0.8 x I
to IEC 60068-2-27, test Ea
96 hours at 5% salt mist,
to IEC 60068-2-11, test Ka
240 hours at 95 % RH,
to IEC 60068-2-3, test Ca
approx. 90 - 120 g per pole
depending on version
Auxiliary circuit
Typical life
Ambient temperature
Insulation co-ordination
(IEC 60664)
Dielectric strength
operating area
pole to pole
main to auxiliary circuit
switching to trip circuit
Insulation resistance
Degree of protection
(IEC 60529)
Vibration
with toggle down:
directions 1, 2, 3, 4, 5:
with curves F1, F2:
Interrupting capacity
to EN 60934, UL 489 and UL 1077
IEC 60934 – test series E
voltage
number of poles
DC 80 V
1+2
AC 240/415 V
1-6
AC 240 V
UL 489 – test sequence Z
voltage
number of poles
DC 80 V
1+2
AC 120 V
AC 120/240 V
AC 240 V
1 (2)
UL 1077
voltage
number of poles
DC 80 V
1+2
AC 277/480 V
1-6
max. (A)
0.02...125
0.02...80
0.02...20
cn
(A)
10,000
6 x I
5,000
Shock
direction 6:
with curves F1, F2:
Corrosion
Humidity
Mass
max. (A)
0.5...125
0.5...80
0.5...80
0.5...20
cn
(A)
10,000
5,000
5,000
5,000
Approvals
VDE (EN 60934)
UL 489
UL 1077
CCC
1- to 6-pole
1- to 6-pole
1- to 4-pole
max. (A)
0.02...125
0.02...70
cn
(A)
10,000
5,000
06/07
(101106)
www.e-t-a.com
Ordering information
Type No.
8345
Mounting
flange mounting, with rectangular aperture with mounting nut 6-32UNC
flange mounting, with rectangular aperture with mounting nut M3
flange mounting, with round aperture with mounting nut 6-32UNC
flange mounting, with round aperture with mounting nut M3
Configuration
without barrier
with small barrier
with large barrier (request for multipole AC applications with
approvals to UL 489, UL 1077, IEC)
Number of poles
single pole unprotected
single pole protected
two pole protected
three pole protected
four pole protected
one pole protected, two poles connected in parallel
characteristic curves E/H/R upon request
one pole protected, three poles connected in parallel
one pole protected, four poles connected in parallel
one pole protected, five poles connected in parallel
Actuator configuration
all poles with standard toggle
reduced number of standard toggles
without actuator
Terminal design
screw terminals M5 ≤ 50 A
solder terminals ≤ 75 A
blade terminals ≤ 35 A
round connectors 6 mm
stud terminals M5 ≤ 60 A
stud terminals 10-32UNF-3A ≤ 60 A
U
stud terminals M6 ≤ 125 A
stud terminals 1/4-20UNC-3A ≤ 125 A
laminated round terminals ≤ 125 A
Terminal hardware
without
with washer and nut
Phillips screws
Characteristic curve
K1
short delay DC
K2
short delay AC
M0
medium delay AC/DC
M1
medium delay DC
M2
medium delay AC
Q0
switch only
T1
long delay DC
T2
long delay AC
Illumination
without
Version
standard
Colour configuration
B1
black actuator
B2
white actuator
B8
blue actuator
Marking
A1
A2
A3
A4
front plate
without
actuator base
without
without
8345 - C 0 1 A - U 3 M1 - . D B1 A1
Rated voltage
AC or ≤ 80 V DC
DC ≤ 80 V
AC ≤ 277 V
(only for configurations
0 and 1)
Current ratings
0.05...125 A
higher current ratings
upon request
Approvals (optional)
UL 489
8345 - C 0 1 A - U 3 M1 - . D B1 A1 B - 60 A - .
ordering example
Remote trip coil available to special order!
Ordering information for auxiliary contact module
Type number
X8345
Module
Auxiliary contacts
01
in all poles
02
in pole 1 only
03
in poles 1 + 3 only
04
in pole 2 only
Auxiliary contact version
auxiliary contacts standard, gold-flushed
(asymmetrical terminals not for UL 489)
auxiliary contacts, tin-plated (symmetrical terminals)
Auxiliary contact function
W1
1 changeover
W2
2 changeover
Terminal design
02
microswitch with blade terminals
DIN 46244-A2.8-0.5
mounted to base unit
X8345 -
S 01 H W1 02 M
ordering example
, characteristic curve without
N,
characteristic curve, without
wiring diagram on side
B1
without
ON-OFF
B2
ON-OFF
B3
ON-OFF
B4
, characteristic curve, ON-OFF
8345 - C 0 1 A - U 3 M1 - . D B1 A1 ...
www.e-t-a.com
06/07
(101106)
Dimensions
Mounting version B/C
48
1.89
28.6
1.13
LINE
Installation drawing
Flange mounting rectangular aperture
pole
number of poles 1 to 4
0.1
.752
.004
OFF
LOAD
63.5
2.50
ON
operating area
(reinforced insulation)
mounting terminal
area
area
67.7
2.67
mounting thread M3 or 6-32
all dimensions referred to the top edge
mounting depth 4.2 mm/.165 in.
max. insertion depth 5.5 mm
max. tightening torque 0.33 Nm
Cut-out dimensions:
LOAD
1-pole
19.2
.756
multipole
76.5
3.01
66.8
2.63
47.7
1.88
LINE
45
1.77
29
1.14
52.4
2.06
36.8
1.45
ø4
.157
9.6
3.5
0.1
(M3)
.378
+0.1
(6-32UNC)
.138
.004
(M3)
+.004
.157
-.006
(6-32UNC)
A 1 toggle per pole, mounting version B/C
19.2
.756
28.7
1.13
n x 19.2
n x .756
OFF
OFF
OFF
OFF
OFF
OFF
OFF
OFF
OFF
OFF
Mounting version E/F
Flange mounting round aperture
pole
48
1.89
28.6
1.13
LINE
B reduced number of toggles per unit, mounting version B/C
19.1
0.1
.752
.004
OFF
OFF
OFF
63.5
2.50
ON
Z without toggles
4-pole
67.7
2.67
LOAD
OFF
OFF
OFF
Cut-out dimensions:
1-pole
3.5
0.1
(M3)
+0.1
(6-32UNC)
.138
.004
(M3)
+.004
.157
-.006
(6-32UNC)
57.3
2.25
38.2
1.50
A 1 toggle per pole, mounting version E/F
OFF
OFF
OFF
OFF
OFF
OFF
OFF
OFF
OFF
OFF
ø15.4
.606
15.45
.608
44.75
1.76
ø15.4
.606
19.2
.756
n x 19.2
n x .756
B reduced number of toggles per unit, mounting version E/F
OFF
OFF
This is a metric design and millimeter dimensions take precedence ( mm )
inch
06/07
(101106)
www.e-t-a.com
Terminal design / Dimensions
P - with blade terminals
49.2
1.94
9.5
.374
W - laminated round terminals
LOAD
LINE
LOAD
LINE
blade terminal A6.3-0.8
(QC .250) DIN 46244
12.2
.480
L - with screw terminals
49.2
1.94
.374
9.5
ø6.3
ø.248
49.2
1.94
27.6
1.09
NC NO
plug-in hole
6.3
+0.1
.248
+.004
LOAD
LINE
Number of poles / Dimensions
9.4
.370
terminal with flat head screw M5
tightening torque max. 1.2 Nm
ø6
.236
49.2
1.94
tightening torque:
M8 max. 6 Nm
.157
M8
LOAD
LOAD
LINE
LINE
P 1-pole protected, 2-poles connected in parallel
for rating currents from 150 to 200 A
M - with solder terminals
LOAD
LINE
19.9
.783
4.2
.165
49.2
1.94
93.2
3.67
18.8
.740
tightening torque:
M6 max. 3 Nm
R - round connectors
D = 6 mm (dia .236) (version H) asymmetrical
terminals (not for UL 489)
LOAD
LINE
Internal connection diagrams
19.2
.756
NC NO
1.94
1-pole
protected magnetically
line 1
unit 1
multipole
line 1
S/U/T/V - with auxiliary contacts (version H)
asymmetrical terminals (not for UL 489)
49.2
1.94
11.2
.441
28
1.10
I > 12
17
I>
.756
LOAD
LINE
17
.669
NC NO
unit 2
5.08
.295
auxiliary contact
module
(change over)
17.4
.685
13.9
.547
LOAD
LINE
NC NO C
NC NO C
7.5
.295
17.5
.689
7.5
.295
16.6
.653
17
.669
inch
www.e-t-a.com
auxiliary contacts version K symmetrical terminals
I > 12
unit 4
16.5
.649
10.2
.402
12.8
.504
tightening torque:
10-32 UNF, M5 max. 2 Nm
1/4-20 UNC, M6 max. 3 Nm
1-pole protected
hydraulic-magnetically
line 1
unit 3
I > 12
(101106)
Typical time/current characteristics at +23 °C / +73.4 °F
(trip time at rated current and all poles symmetrically loaded)
Curve K1 (short delay) for DC
10000
Trip time in seconds
0.01
0.001
… times rated current
Curve M0 (medium delay) for AC/DC
10000
0.01
0.001
Curve K2 (short delay) for AC 50/60 Hz
10000
0.01
0.001
Curve M1 (medium delay ) for DC
10000
0.01
0.001
Curve T1 (long delay) for DC
10000
0.01
0.001
Curve M2 (medium delay) for AC 50/60 Hz
10000
0,01
0.001
Curve T2 (long delay) for AC 50/60 Hz
10000
0.01
0.001
All curves will only be maintained if the escutcheon is mounted on a vertical surface.
Other characteristic curves to special order ( e. g. pulse delayed, for high inrush currents or capacitive loads).
06/07
(101106)
www.e-t-a.com