SIMM Series Input Modules
6.2 mm wide and 65 mm deep
* DIN Rail mounted
* LED input status indicator
* Bridges enable quick linking of common voltage
* Identification zone on front face
* IP20
Part numbers
84145061
84145062
24Vac/dc
19.2-30Vac/dc
20 mA
30Vac/36Vdc
50 mA
-25 to 60°C
-40 to 80°C
8 ms
10 ms
10 Hz
> 10 x 10
6 x 10
1.23 oz
SPDT
84145064
95-121Vac/dc
5 mA
30Vac/36Vdc
50 mA
84145066
240
195-253Vac/dc
5 mA
30Vac/36Vdc
50 mA
84145071
5 - 28
19.2-30Vac/dc
20 mA
30Vac/36Vdc
50 mA
-25 to 60°C
-40 to 80°C
8 ms
10 ms
10 Hz
> 10 x 10
6 x 10
1.23 oz
SPST (N.O.)
Input Characteristics (at ambient 25 C°)
Nominal voltage
Operating voltage range
Max input current
24Vac/dc
19.2-30Vac/dc
20 mA
30Vac/36Vdc
50 mA
-25 to 60°C
-40 to 80°C
8 ms
10 ms
10 Hz
> 10 x 10
6 x 10
1.23 oz
SPDT
Output characteristics (at ambient 25 C°)
Max Voltage
Max current
General characteristics
Operating temperature range
Storage temperature range
Turn-On time
Turn-Off time
Switching frequency
Mechanical Life (operations)
Electrical Life (number of operation)
Weight
Contact Material
Contact Arrangement
-25 to 60°C
-25 to 60°C
-40 to 80°C
-40 to 80°C
8 ms
8 ms
10 ms
10 ms
10 Hz
10 Hz
> 10 x 10
> 10 x 10
6 x 10
6 x 10
1.23 oz
1.23 oz
AgSnO2 gold plated
SPDT
SPDT
Exceeding the value given for the output relay current will remove the gold plating
from the contacts and therefore we cannot guarantee correct operation at low currents.
Dimensions:
SPDT
SPST
Wiring Diagram and Thermal Curves:
84145061 / 062 / 064 / 066
Accessories
84145050
Front Panel marker ( 88 per bag )
84145052
10 postion jumper - Blue
84145071
84145051
2 Pole "Common" Jumper
84145053
10 postion jumper - Red
Products and specifications subject to change without notice.
Consult factory for applications assistance. www.crouzet-usa.com
SIMM Series Output Modules
* DIN Rail mounted
* IP20
Part numbers
84145001
84145004
110Vac/dc
70-130Vac/dc
7 mA
30Vac/dc
5-48Vdc
0.5A
Transistor
-20 to 60°C
-40 to 80°C
30 ms
20 ms
10 Hz
1.13 oz
84145021
24Vdc
10-44Vdc
6mA
3Vdc
24-250Vac
0.5A
Triac
-20 to 60°C
-40 to 80°C
10 ms
10 ms
20 Hz
1.13 oz
84145005
230Vac
90-230Vac
8.5 mA
40Vac
5-48Vdc
0.5A
Transistor
-20 to 60°C
-40 to 80°C
45 ms
15 ms
10 Hz
1.13 oz
84145024
110Vac/dc
70-130Vac/dc
6mA
35Vac/dc
24-250Vac
0.5A
Triac
-20 to 60°C
-40 to 80°C
10 ms
10 ms
20 Hz
1.13 oz
84145010
5Vdc
4-5.5Vdc
6 mA
2Vdc
5-48Vdc
2A
Transistor
-20 to 60°C
-40 to 80°C
1 ms
5 ms
10 Hz
1.06 oz
84145025
230Vac
140-250Vac
7mA
80Vac
24-250Vac
0.5A
Triac
-20 to 60°C
-40 to 80°C
10 ms
10 ms
20 Hz
1.13 oz
84145011
24Vdc
10-44Vdc
6 mA
3Vdc
5-48Vdc
2A
Transistor
-20 to 60°C
-40 to 80°C
1 ms
5 ms
10 Hz
1.06 oz
84145031
24Vdc
10-44Vdc
6 mA
3Vdc
24-250Vac
1A
Triac
-20 to 60°C
-40 to 80°C
8.33 ms
8.33 ms
20 Hz
.95 oz
84145015
230Vac
90-230Vac
7mA
40Vac
5-48Vdc
2A
Transistor
-20 to 60°C
-40 to 80°C
1 ms
10 ms
10 Hz
1.06 oz
Nominal voltage
Max input current
Drop out voltage
24Vdc
10-44Vdc
6 mA
5Vdc
5-48Vdc
0.5A
Transistor
-20 to 60°C
-40 to 80°C
20 us
100 us
1k Hz
1.13 oz
84145020
Output Characteristics (at ambient 25 C°)
Max current
Output Type
General Characteristics
Turn-On time
Turn-Off time
Switching frequency
Weight
Part numbers
Nominal voltage
Max input current
Drop out voltage
5Vdc
4-6.2Vdc
6mA
2Vdc
24-250Vac
0.5A
Triac
-20 to 60°C
-40 to 80°C
10 ms
10 ms
20 Hz
1.13 oz
84145001 / 004 / 005
84145020 / 021 / 024 / 025
Max current
Output Type
Turn-On time
Turn-Off time
Switching frequency
Weight
Derating Curves:
84145010 / 011 / 015
Dimensions:
Solid State Output:
84145031
84145031
Consult factory for applications. www.crouzet-usa.com
* DIN Rail mounted
* IP20
Part numbers
84145041
84145042
24Vac/dc
19.2-30Vac/dc
20 mA
1-250Vac
6A
-25 to 60°C
-40 to 80°C
8 ms
10 ms
10 Hz
> 10 x 10
6 x 10
1.23 oz
SPDT
84145043
110Vac/dc
95-125Vac/dc
5 mA
1-250Vac
6A
-25 to 60°C
-40 to 80°C
8 ms
10 ms
10 Hz
> 10 x 10
6 x 10
1.23 oz
AgSnO2
SPDT
84145046
230Vac
195-253Vac/dc
1-250Vac
6A
-25 to 60°C
-40 to 80°C
8 ms
10 ms
10 Hz
> 10 x 10
6 x 10
1.23 oz
SPDT
Nominal voltage
Max input current
24Vdc
19.2-30Vdc
20 mA
1-250Vac
6A
-25 to 60°C
-40 to 80°C
8 ms
10 ms
10 Hz
> 10 x 10
6 x 10
1.23 oz
SPDT
Max current
Turn-On time
Turn-Off time
Switching frequency
Weight
Contact Material
Contact Arrangement
Dimensions:
Relay Output:
84145041 / 042 / 043 / 046
Accessories
84145050
84145052
84145051
84145053
Hybrid power relays - RHP
s
s
s
s
20 A in a case only 17.5 mm wide
Service life > 5 million operations at full load
Silent operation
Functions: contactor – impulse relay – day/night
contactor
s
Clips onto a 35 mm DIN rail
s
UL/©UL (listed) approval pending
s
NF-USE label pending
s
“CE” / Low Voltage Directive conformity
Operating principles
Contactor
The contactor output is closed when the control voltage is present at the
control input terminals.
The contactor output is open when there is no voltage at the control input
terminals.
The LED is lit when the output is active.
Impulse relay
The impulse relay output changes state on each impulse at the control
input terminals, and remains in that state between each impulse. The
output changes state on the rising edge of the control state change.
The pushbutton on the front can be used to select an operating mode:
Automatic (LED lit): Impulse relay function (Auto)
Forced operation (LED flashing): output closed (ON)
Stop (LED not lit): output open (OFF)
Day/night contactor
terminals.
Automatic (LED lit): Day/night contactor function (Auto)
When the control changes state, the day/night contactor reverts to
automatic mode.
Conformity with standards
IEC/EN 60947-4-3 (industrial environment)
IEC/EN 60669-2-1 (domestic environment)
IEC/EN 60601-1 (medical environment)
IEC/EN 60947-7-1 (connection for industrial env.)
IEC/EN 60998-2-1 (connection for domestic env.)
Insulation coordination:
Installation category: 3
Degree of pollution: 3
According to IEC 60664-1: 4KV/3
Breakdown voltage according to IEC/EN60669-2-1:
2 KV/1Min / 1mA / 50 Hz
Insulation resistance according to IEC/EN60669-2-1:
> 5MΩ/500VDC / 1Min
Vibrations according to IEC/EN60068-2-6: frequencies: 10 to 55Hz
amplitude: 0.35 mm
Part numbers (and voltages)
Contactor control
a
Contactor control
c
Impulse relay control
a
Day/night contactor control
c
84 138 001
84 138 000
84 138 101
84 138 201
0…32 V c
0 to 1 V
c
4 to 32 V
c
50 ms
Input characteristics
Thresh- OFF control
olds
ON control
Minimum duration
of the control
90…260 V a
50 / 60 Hz
0 to 46 V
a
76 to 260 V
a
50 ms
Max. current
Overload current 20 A
Min. current
Contact
Number of operations
Leakage current
Acoustic
in steady state
noise
on switching
Terminal block clamping
capacity:
Terminal tightening torque
Storage temperature
Relative humidity
Casing material
Degree of protection
(according to IEC 60529)
Weight (g)
90…260 V
a
20 A in AC1 / AC51 / AC7a
AC-51 : 1,25 x Ie – 60s : 50 - 30
(IEC 60947-4-3)
100 mA in AC1 / AC51 / AC7a
50 / 60 Hz
N.O.
> 5 000 000
< 5 mA
< 35 dB at 1 m
< 50 dB at 0.5 m
2 x 1.5 mm
with ferrule
2 x 2.5 mm
without ferrule
1 x 4 mm
without ferrule
1 Nm max. M3 screw (IEC60947-1)
-5 °C to +55 °C
-40 °C to +85 °C
90 to 95 % without condensation
Self-extinguishing
IP 50 casing
IP 20 terminal block
70 approx.
Connection
A1
N I
1 3
I N
1 3
A1
90...
260V
2 4
A2
A1
90…260 V
a/4…32
c
2 4
LOAD
A2
A2
Dimensions
81
44
17,5
To order, specify:
Standard products
Part number
Example : Solid state relays - RHP - 84 138 001
Two-phase (dual) solid state relays - GD range
Courtesy of Steven Engineering, Inc.
Ÿ
230 Ryan Way, South San Francisco, CA, 94080-6370
Ÿ
Main Office: (650) 588-9200
Ÿ
Outside Local Area: (800) 258-9200
Ÿ
www.stevenengineering.com
s
s
s
s
s
s
s
s
s
s
For controlling three-phase supplies
Controls two or three phases of the supply
Applied to star or delta-connected two-phase
resistances with neutral not connected
Rating 25 A and 40 A
Output voltages from 24 to 280 V and 36 to 530 V
Back-to-back SCRs
Zero voltage switching
Input to output insulation voltage: 4000 V
Protection by RC filter
UL - cUL approval and CE marking
Part numbers
24-280
67
1.6
260
> 0.5
24-280
1.6
1260
0.25
> 0.5
36-530
1200
1.6
1260
0.25
> 0.5
Two-phase relays 25 A
Switching
Output
voltage
Zero voltage
24 - 280 V
a
Instantaneous 24 - 280 V
a
Two-phase relays 40 A
Switching
Output
voltage
Zero voltage
24 - 280 V
a
a
Zero voltage
36 - 530 V
a
Instantaneous 36 - 530 V
a
Zero voltage
24 - 280 V
a
a
Zero voltage
36 - 530 V
a
a
Zero voltage
24 - 280 V
a
a
Zero voltage
36 - 530 V
a
a
Heatsinks
Heat transfer compound
DIN rail adaptor
Quick-blow fuses
Thermal dissipation curves
25 A
Output specifications
Voltage range (Vrms max)
Peak voltage (t=1 min.) (Vpeak)
Maximum current (Vpeak)
Maximum current(mArms)
Minimum current (mArms)
Max. 1-cycle surge
T=25°C (A peak)
Max. 1-second surge
T=25°C (A peak)
On-state voltage drop
at Imax and T=25°C (Vpeak)
t (t=10ms) A
s
Thermal resistance -
Junction to casing (°C/W)
Static (off-state) dv/dt (Vµs)
Supply frequency range (Hz)
cos
ϕ
(Zero voltage)
Input
voltage
4 - 15 V
c
4 - 15 V
c
Input
voltage
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
4 - 15 V
c
Connection
diagram
Connection
diagram
84 130 211
Input specifications
Input voltage(V)
Drop-out voltage (V
c)
Maximum current
(at Vmax) (mA)
Response time (close)
Zero voltage switching (ms)
Instantaneous switching (ms)
Response time (open)
4-15
c
84 130 231
84 130 240
84 130 241
84 130 250
84 130 251
84 130 260
84 130 261
84 130 270
84 130 271
84 130 280
84 130 281
Accessories
(see catalogue pages 4/30 to 4/32)
18 373 112
26 532 764
Characteristics
Operating temperature (°C)
Storage temperature (°C)
Input to output insulation voltage (Vrms)
Breakdown voltage (Vrms)
Input/output capacitance (pF)
Material
Casing
Baseplate
Weight (g)
Equivalent circuits
-20 à +80
-40 à +100
4000
2500
Self-extinguishing
(UL 94 V0)
Aluminium
450
2°
C/W
5 °C
/W
/W
/W
40 A
A1
/W
C/
1,5
A2
C/
C/
B1
/W
B2
To order, specify:
Standard products
Standard products,
non stocked
Part number
Accessory
Exemple: Two-phase solid state relay 25 A 84 130 210 - DIN rail adaptor 26 532 764
4/23