首页 > 器件类别 > 无源元件 > 电阻器
AUSUP130E2
AUSUP130E2
器件类别:无源元件    电阻器
厂商名称:SCHURTER
厂商官网:http://www.schurterinc.com/
器件标准:
是否Rohs认证
符合
Objectid
400659940
not_compliant
ECCN代码
EAR99
CIRCUIT BREAKERS FOR EQUIPMENT
TA45: 2 pole, push button actuated
• Thermal release
• Positively trip-free
The 2 pole, push button actuated version of the TA45 line of thermal
CBE’s can be used for various purposes. Basically it is a CBE for
automatic interruption of overloads with facilities for regular manual
ON/OFF switching operations under normal load conditions. It is
capable of interrupting moderate short circuit currents without the aid
of back-up protection.
A special version is available as a «CBE-switch», in which the means
for automatic overcurrent interruption (the bimetal relases), are
omitted.
Another available version of this line utilizes an under-voltage release
to protect persons against injuries caused by unexpected events like
the automatic restarting of motors after a power failure. This release
can be combined with the thermal release required for overcurrent
protection. Protection against injuries is also provided by another CBE
of this line, which prevents the starting of a machine should a
protective cover be removed from dangerous parts of the machine.
Available options:
• CBE for overcurrent protection
1 or 2 protected poles (thermal)
• CBE with undervoltage release:
The CBE will open automatically when the voltage drops below the
trip level. Only when the supply voltage has reached the reset
level, the CBE can be reclosed manually.
• CBE switch with mechanical lock-out latch:
A spring loaded pin will trip the CBE if a protective cover of the
equipment is removed. The CBE can not be switched ON until the
protective cover is refitted.
• CBE with remote trip release:
The remote trip release permits the CBE to be tripped by a external
contact (sensor) energizing the trip coil.
• CBE with auxiliary contact:
All types of the line can be outfitted with an auxiliary contact
(changeover contact).
TA45 is positively trip-free. The rated current range is 0,1 to 20 A at
AC 230 V / DC 60 V. The CBE comes with snap-in mounting or
flange mounting. A locking device suitable for padlocks prevents
unauthorized switching ON of the CBE. The TA45 is approved in all
major industrial countries and complies with the CBE-standard
EN60934.
In conjunction with its accessories the TA45 product line of Schurter
paves the way for new unconventional applications.
Motors
Power supplies
Processing machines
etc.
238
Schurter, Inc. • Phone 707-778-6311 •
• Fax 707-778-6401 •
E-mail info@schurterinc.com •
Website http://www.schurterinc.com
Phone 707-778-6311
Fax 707-778-6401 •
E-mail info@schurterinc.com Website http://www.schurterinc.com
CIRCUIT BREAKERS FOR EQUIPMENT TA45, 2 POLE
Effect of ambient
temperature
The unit is calibrated for an ambient tem-
perature of +23°C. To determine the rated
current for a lower or higher ambient
temperature, use a correction factor from
the table below:
*Ambient
temperature [°C]
–10
–5
+30
+40
+55
Correction factor
0,89
0,91
0,92
1,00
1,03
1,08
1,16
Example
Rated current at +23°C
Ambient temperature
Correction factor
Chosen rated current at
+40°C ambient temperature
5 A x 1,08 = 5,5 A
5,0 A
+40°C
1,08
*Temperature must be measured at the rear of the
breaker next to the terminals after equipment operating
temperature has been reached.
Tripping characteristics
In <3 A
3 A
In <18 A
In
≥18
[ min ] [ sec ]
10'000
Rated current
TA45
In <3 A
1 pole protected
[ min ] [ sec ]
10'000
Rated current
TA45
3 A
In <18 A
[ min ] [ sec ]
10'000
Rated current
TA45
In
≥18
1 pole protected
2`000
1`00
Ambient temp.
2`000
1`00
Ambient temp.
1 pole protected
2 pole protected
+23
2 pole protected
+23
2`000
1`00
Ambient temp.
2 pole protected
+23
Tripping time
Tripping time
0,3
0,2
0,1
1,05 1,32
Tripping time
0,3
0,2
0,1
1,05 1,32
0,3
0,2
0,1
1,05 1,32
Multiple of rated current
[ x In
[ x In
[ x In
Schurter, Inc. • Phone 707-778-6311 • Fax 707- 778-6401 • E-mail info@schurterinc.com • Website http://www.schurterinc.com
239
PG 3
CIRCUIT BREAKERS FOR EQUIPMENT TA45, 2 POLE, PUSH BUTTON
Technical data
Rated voltage Ue
Rated current In
Conditional short circuit current Inc
Short circuit capacity Icn
See approvals page 241
AC 240 V; DC 60 V
AC/DC 0,1 A – 20 A
EN 60934, PC1, AC 240 V
1000 A
AC 240 V with In<3 A
AC 240 V with In
≥3
DC 60 V with In<3 A
DC 48 V with In
≥3
(number
(number
(number
(number
of
of
of
of
cycles: 3)
cycles: 3)
cycles: 3)
cycles: 3)
10 In
300 A
10 In
120 A
Degree of protection
Accessible range
With accessories
Terminal side
With accessories
IP40
IP54, IP65
IP00
IP40
Dielectric strength
Accessible range
AC 4000 V
Insulation resistance
DC 500 V
>100 MΩ
Endurance
Number of cycles at
Number of cycles at
Number of cycles at
In (AC 240 V; DC 60 V)
6 x In (AC 240 V)
4 x In (DC 60 V)
50’000 x
40 x
40 x
Permissible ambient temperature
-10°C to +55°C
Resistance to vibration
IEC 68-2-6, test Fc, 1mm amplitude 5-60 Hz, 60-500 Hz
>10 g
Shock resistance
IEC 68-2-6, test Ea
>30 g
Type of tripping
• Thermal positively trip-free
• Undervoltage release
• Remote trip
• Mechanical lock-out latch
Weight
approx. 35 g
240
Schurter, Inc. • Phone 707-778-6311 • Fax 707-778-6401 • E-mail info@schurterinc.com • Website http://www.schurterinc.com
Technical data (continued)
Auxiliary contact (changeover)
Rated voltage
DC 28 V
DC 60 V
(30V per pole)
max. 2 A
resistive load
AC 240 V
Rated current
Max. 10 A
resistive load
max. 2 A
cos
ϕ
0,7 (PF 0,7)
Max. operating voltage
1,1 Ue
5V
12 V
24 V
48 V
120 V
240 V
Rated operating voltage Ue
Current consumption (±10%)
10,5mA 16,5 mA 17,0 mA 3,2 mA
3,7 mA
2,8 mA
Highest reset level
0,85 Ue
0,20 Ue
20 ms – 50 ms
≥4
kV
Lowest trip level
Trip delay
Impulse withstand voltage (1,2 / 50 µs)
Remote trip
Permissible impulse duration
of the make contact (n/o)
(Between terminal C and P1)
unlimited
Electrical load
Current max. 12 mA / power max. 1,1 W
Approvals
Rated current range
AC
UL
1077
0,1 – 20 A
Rated voltage
AC
240 V
Rated voltage
DC
60 V (30V per pole)
CSA
22.2 No. 235
0,1 – 20 A
240 V
60 V (30V per pole)
VDE
EN60934
CEE24/VDE0630
EN60934
0,1 – 20 A
16A*
0,1 – 20 A
240 V
250V
250 V
60 V (30V per pole)
SEMKO
60 V (30V per pole)
SEV
EN60934
0,1 – 20 A
240 V
60 V (30V per pole)
* without thermal release
241
PG 3
Order code 2 pole, push button actuated
Basic type
Without thermal overload protection
Shunt terminal
P2
P1
P2
1110
P1 1011
Terminal type
Quick connect terminal
Screw type terminal (lineside P1, P2)
Dimension
Push button gasket IP40
Push button gasket IP65
Page
245
ABK
ABS
Page
249
AHK
AHS
246
AEK
AES
250
AJK
AJS
247
AUK
AUS
251
ALK
ALS
248
AXK
AXS
252
APK
APS
Snap-in type
Flange type
Dimension
Order example
ABL
Colors
Switch front
ON Button
OFF Button
J28
U2
U
black
yellow
grey
green
green
green
red
red
red
Push button legend
Without thermal overload protection: code C00
With thermal overload protection: rated current In (A)
Surface
Illustration
Color of print
Other amperages available on request.
embossed
printed
printed
printed
printed
printed
printed
printed
printed
l
OFF OFF
ON
In
white
black
white
black
white
black
white
black
0,1
0,2
0,3
0,4
0,5
0,6
0,7
0,8
0,9
1,0
1,1
1,2
J01
J02
J03
J04
J05
J06
J07
J08
J09
J10
J11
J12
In
1,3
1,4
1,5
1,6
1,7
1,8
1,9
2,0
2,1
2,2
2,3
2,5
J13
J14
J15
J16
J17
J18
J19
J20
J21
J22
J23
J25
In
2,8
3,0
3,5
4,0
4,5
5,0
6,0
6,5
7,0
7,5
8,0
9,0
J28
030
035
040
045
050
060
065
070
075
080
090
In
10,0
11,0
12,0
13,0
14,0
15,0
16,0
17,0
18,0
19,0
20,0
140
170
180
190
ON
l
l
ON
l
ON
l
242
Phone 707-778-6311
Fax 707-778-6401 •
OFF OFF
【Atmel SAM R21创意大赛周计划】基于Atmel SAM R21的四轴无线双向遥测系统研究
项目内容: 四轴飞行器无疑是当今最热门的电子科技产品。本项目的目的就是为了实现四轴飞行器与地面站的无...
zhous 单片机
需要给段码液晶配一个驱动,请大家帮忙,谢谢!
背景:之前搞测评的时候,看错了datasheet,以为支持裸片液晶,买了一个段码液晶(实际不支持)...
韵湖葱白 DIY/开源硬件专区
请教一下LCD得显示问题,已附带图片
求助,谢谢。 请教一下LCD得显示问题,已附带图片 ?什么问题?字都没有,让大家猜问题的吗? ...
一百年后的自己 51单片机
常小兵上海调研引发3G猜想 CDMA1X不输日韩
据《通信产业报》了解的情况,一段时间来,中国联通技术部总经理张智江多次前往上海,总结上海联通的实验...
mdreamj RF/无线
MSP430矩阵及独立键盘
在学习MSP430的时候,总是有很多东西记不住,同时又是英文的资料,好多东西也是没怎么看透,英文虽...
Aguilera 微控制器 MCU
