GE
Data Sheet
CP2725AC48TEZ-FB Compact Power Line High Efficiency Rectifier
Input: 100-120/220-240 Vac; Output: 2725W
@ 52Vdc; 5 Vdc @ 4W
The CP2725AC48TEZ-FB Rectifier has an extremely wide programmable output voltage capability and fold-back current
limiting features. High-density front-to-back airflow is designed for minimal space utilization and is highly expandable for
future growth. This custom rectifier incorporates both RS485 and dual-redundant I
C communications busses that allow it
to be used in a broad range of applications. Feature set flexibility makes this rectifier an excellent choice for a set of
applications requiring operation over a wide output voltage range.
UL is a registered trademark of Underwriters Laboratories, Inc.
CSA is a registered trademark of Canadian Standards Association.
VDE is a trademark of Verband Deutscher Elektrotechniker e.V.
This product is intended for integration into end-user equipment. All the required procedures for CE marking of end-user equipment should be
followed. (The CE mark is placed on selected products.)
** ISO is a registered trademark of the International Organization of Standards.
Efficiency 95%
Compact 1RU form factor providing 30 W/in3
2725W @ 52V from nominal 220 – 240Vac
1200W from nominal 100 – 120Vac (for V
o
> 42Vdc)
Output voltage programmable from 18V – 53Vdc
PMBus compliant dual I
C and RS485 serial busses
Power factor correction (meets EN/IEC 61000-3-2 and EN
60555-2 requirements)
Output overvoltage and overload protection
AC Input overvoltage and undervoltage protection
Over-temperature warning and protection
Redundant, parallel operation with active load sharing
Redundant +5V Aux power
Remote ON/OFF
Hot insertion/removal (hot plug)
Four front panel LED indicators
UL* Recognized to UL60950-1, CAN/ CSA
C22.2 No. 60950-
1, and VDE
0805-1 Licensed to IEC60950-1
CE mark meets 2006/95/EC directive
Internally controlled Variable-speed fan
RoHS 6 compliant
Special Foldback Curve
Wide band power amplifiers
High line operation. The unit current limits below 52V and therefore the available output power below 52V operation is reduced.
January 7, 2013
©2013 General Electric Company. All rights reserved.
GE
Electrical Specifications
Input
Startup Input Voltage
Low-line Operation
High-line Operation
Operating Voltage Range
Low-line Configuration
High-line Configuration
90
220 - 240
Data Sheet
@ 52Vdc; 5 Vdc @ 4W
Min
Typ
265
Units
Vac
Surges (no damage)
Input Frequency
Input Current
Inrush Transient
Input Leakage Current
Power Factor
20 – 90% of FL
Efficiency
>38V
Holdup
Ride thru
Power Fail Warning
47
66
0.96
93
85
ms
cycle
ms
0.98
95
Hz
Apk
At 110 Vac
At 240 Vac
Measured at 25°C for all line conditions; does not
include X-Capacitors charging.
Measured at 265Vac, 60Hz
From 50% to 100% (2725W @ HL, 1200W @ LL). load
With or’ing function, aux 5V output, dual/redundant
C and RS485 communications and POE isolation
>20% load
Test condition: input; 240Vac, 60hz, output; 52Vdc
48Vdc, Measurement starts at zero crossing of the ac
voltage, and voltage decayed to 40V.
For loads below 1200W.
Tested at nominal 115V and 230V . Complies to
CISPR24 standards
Alarm issued via PFW signal going LO 5 ms prior to
the main output decaying below 40Vdc.
Main Output
Output Power
Default Set point
Overall Regulation
Output Voltage Set Range
Output current
-1
-2
Min
1200
2725
Typ
Units
Above 52Vdc from nominal 90-120Vac upto 55°C.
Above 52Vdc from nominal 200-265Vac upto 55°C
Output floats with respect to frame ground.
0 – 45C, minimum load 2.5A
> 45C
Analog margining and RS485
Set by I
1200W @ 52V @ 90-120Vac.
2725W @ 52V @ 200-240Vac.
48
+1
+2
53
53
23
52.4
Vdc
Vdc
Vdc
At 52Vdc, 240Vrms and 25C.
Internal protection circuits may override the PFW signal and may trigger an immediate shutdown.
Includes all variations due to specified load range, drift, and environmental conditions.
January 7, 2013
Page 2
GE
Electrical Specifications (continued)
Main Output (continued)
Current Share
Output Ripple
RMS (5Hz to 20MHz)
Peak-to-Peak (5Hz to 20MHz)
External Bulk Load Capacitance
Turn-On
Delay
Rise Time - Standard (PMBus)
-Telecom (RS-485)
Overshoot
Load Step Response
Response Time
Power Limit – high line
Power limit – low line
2725
1200
> 42V
< 42V
Data Sheet
@ 52Vdc; 5 Vdc @ 4W
Min
-5
-10
Typ
Units
%FL
mVrms
mVp-p
s
ms
s
%FL
Vdc
ms
Compared to the average output current delivered by a
set of Rectifiers. Loads > 50% FL
Measured with 20MHz bandwidth under any condition of
loading. Minimum load is 1A.
External capacitance can be increased but the rectifier
will not meet its turn-ON rise time requirement.
Monotonic Turn_On from 30% to 100% of Vnom above -
5°C operation. Monotonic Turn_On from 60% to 100% of
Vnom below -5°C operation.
I/t
slew rate 1A/µs.
Settling time to within regulation requirements.
Minimum load of 2.5 amperes required.
Down to 51Vdc
The overload current limit threshold should be set
5% above the load envelope shown here
Permissible
Load
Boundary
Contract terms are for supporting all loads inside the load map. The customer will develop a control interface which
maintains the operating voltage and current so as to not exceed the load map.
System Power
Up
Units should be able to be plugged in one at a time and guarantee system start up. Units should stay in current limit
for approximately 20 seconds to guarantee restart.
Below -5°C, the rise time is approximately 5 minutes to protect the bulk capacitors.
January 7, 2013
©2013General Electric Company. All rights reserved.
Page 3
GE
@ 52Vdc; 5 Vdc @ 4W
Over-voltage
Delayed
Immediate Latchoff
Vdc
Vdc
Data Sheet
200msec delayed shutdown to be implemented.
Instantaneous shutdown above this point.
Three restart attempts may be implemented within a one minute window prior to a latched
shutdown
Over-temperature
Warning
Shutdown
Auto-recoverable
Implemented prior to commencement of an OT
shutdown
Below the maximum rating of the device being
protected
Temperature hysteresis of approximately 10°C provided between shutdown and restart.
Overcurrent events that exceed the envelope by 5% will hiccup continuously at a frequency of approximately once every 20 seconds. For voltage set-
points below 42V, a tracking Under Voltage shutdown occurs at 2 volts below set-point. UV must exhibit for more than 1 second before shutdown. UV
shutdown will exhibit the same 20 second hiccup behavior.
Auxiliary Output
Output Voltage Setpoint
Output Current
Overall Regulation
Ripple and Noise
Over-voltage Clamp
Over-current Limit
110
0.005
-10
Min
Typ
+5
Units
Vdc
mVpk-pk
Vdc
%FL
Within ±5% when load is < 0.5A.
20MHz bandwidth
January 7, 2013
Page 4
GE
@ 52Vdc; 5 Vdc @ 4W
Environmental, EMC, Reliability Specifications
Environmental
Ambient Temperature
Operating
Derating
Storage Temperature
Humidity
Altitude
Shock and Vibration
Earthquake Rating
Acoustic Noise
Harmonic Emissions
Radiated Emissions
Conducted Emissions - ac
ESD
Radiated Immunity
Electrical Fast Transient Burst
Lightning Surge,
Error Free
Damage Free
Per EN/IEC61000-3-2
Exceeds FCC and CISPR22 (EN55022) - Class A by a 6dB margin
Exceeds FCC and CISPR22 (EN55022) Class A
Telcordia GR-1089-CORE - Class A by a 6dB margin
Zone
dBA
Data Sheet
Min
-40
Typ
95
4000
13000
Units
m
ft
Air inlet from sea level to 5,000 feet.
Per 1,000 feet above 5,000 feet.
Relative humidity, non-condensing
For operation above 2500m (5000 ft.), maximum operating
temperature is derated by 2°C per 305m (1000 ft.).
IPC9592 sections 5.2.8 – 5.2.13
Per Telcordia GR-63-CORE, all floors, when installed in CP Shelf.
Noise is proportional to fan speed, load and ambient temperature.
-40
-200
Error free per EN/IEC 61000-4-2 Level 3 (6 kV contact discharge, 8 kV air discharge).
Error free per EN/IEC 61000-4-3 Level 3 (10 V/m).
Error free per EN/IEC 61000-4-4 Level 3 (2 kV, 5 kHz repetition rate)
EN/IEC61000-4-5 Level 4 (4 kV common mode, 2 kV differential mode).
ANSI C62.41 Level A3 (6 kV common and differential mode)
IPC9592A issued May 2010 ; 1 cycle interruption or 25% sag (115V, 230V – nominal for UUT) for 2 seconds the
output shall stay above 40Vdc at full load. [Note: An input sag below 80V may cause an immediate shutdown.]
Error free per EN/IEC 61000-4-6 Level 3 (10Vrms).
450,000
1500
3000
Hours
Vrms
Vrms
Vdc
Vdc
Years
At ambient of 25°C at full load per Telcordia SR-332, issue 2,
Reliability Prediction for Electronic Equipment, Method I Case III.
Per EN60950.
Consult factory for testing to this requirement
Internal Lineage standard, GR_947
POE compliant Rectifier, Per IEEE802.3.
25°C ambient, full load excluding fans.
Line sags and interruptions
Conducted Immunity
Reliability (calculated)
Isolation
Input-Chassis/Signals
Input - Output
Output-Chassis
Output-Chassis/Signals
Service Life
Designed to start and work at an ambient as low as -40°C, but may not meet operational limits until above -5°C
Radiated emissions compliance was met using a Lineage Power shelf. This shelf includes output common and differential mode capacitors that
assist in meeting compliance.
Page 5
January 7, 2013