首页 > 器件类别 > 半导体 > 嵌入式处理器和控制器
E5CSV-Q1TD-F AC/DC24
CONTROL TEMP RELAY/VOLT OUT 24V
器件类别:半导体    嵌入式处理器和控制器
厂商名称:OMRON
厂商官网:https://www.omron.com
器件标准:
类型
温度控制器(RTD,型 J,K,L,N,R,T,U)
输入范围
-99°C ~ 1700°C
输出类型
继电器,电压(外部 SSR)
控制方法
开/关,成比例(PID)
每行字符数
3.5
显示类型
LED - 红色字符
显示字符 -  高度
0.531"(13.50mm)
电压 - 电源
24VAC/DC
面板开口尺寸
方形 - 45.00mm x 45.00mm
安装类型
面板安装
端子类型
螺丝端子
侵入防护
IP66 - 防尘,耐水
特性
传感器故障检测
工作温度
-10°C ~ 55°C
重量
0.265 磅(120.2g)
Temperature Controllers
E5CSV
CSM_E5CSV_DS_E_7_5
Easy Setting Using DIP Switch and Simple
Functions in DIN 48
48 mm-size Temperature
Controllers
• Easy setting using DIP switch.
• Models with two alarms added to Series, ideal for temperature
alarm applications.
• Universal-input (thermocouple/platinum resistance thermometer)
models also available.
• Clearly visible digital display with character height of 13.5 mm.
• Models available with black in addition to white cases.
• RoHS compliant.
For the most recent information on models that have been certified for
safety standards, refer to your OMRON website.
Refer to
Safety Precautions for All Temperature
Controllers.
Refer to
E5CS/E5CSV Operation
for
operating procedures.
Model Number Structure
Model Number Legend
Models with Terminal Blocks
E5CSV-@@@@-@
1 2 3 4
3. Input
KJ: Thermocouple
P: Platinum resistance thermometer
T: Thermocouple/platinum resistance
thermometer (universal-input)
4. Power Supply Voltage
Blank: 100 to 240 VAC
D:
24 VAC/VDC
5. Case Color
Blank: Black
W:
Light gray
1. Control Outputs
R: Relay
Q: Voltage for driving SSR
2. Alarm Outputs
Blank: No alarm
1:
1 alarm
2:
2 alarms
A functional explanation is provided here for illustration, but models are not necessarily available for all possible combinations. Refer to
Ordering Information
when ordering.
Examples
Relay control output, without alarm, thermocouple/platinum-resistance thermometer multi input, black case : E5CSV-RT
Relay control output, one alarm output, platinum resistance thermometer input, black case, light gray case
: E5CSV-R1P-W
E5CSV
List of Models
Case Color: Light Gray, Thermocouple or Platinum Resistance Thermometer,
Power Supply Voltage: 100 to 240 VAC
E5CSV
48
48mm
Control
modes
Alarms
Outputs
Relay
Voltage (for driving SSR)
Model with
thermocouple
E5CSV-R1KJ-W
E5CSV-Q1KJ-W
Model with platinum
resistance
thermometer
E5CSV-R1P-W
E5CSV-Q1P-W
Terminal block ON/OFF or
PID
Case Color: Light Gray, Thermocouple, Power Supply Voltage: 24 VAC/VDC
E5CSV
48
48mm
Control
modes
PID
Alarms
Relay
Outputs
Model with
thermocouple
E5CSV-R1KJD-W
Case Color: Light Gray, Universal-input, Power Supply Voltage: 100 to 240 VAC
Control
modes
Alarms
Outputs
E5CSV
48
48mm
PID
2 (See note.)
Relay
Relay
Relay
Model with universal-
input (thermocouple
or platinum resistance
thermometer)
E5CSV-RT
E5CSV-QT
E5CSV-R1T
E5CSV-Q1T
E5CSV-R2T
E5CSV-Q2T
There is no alarm output 2 mode switch. The default setting for alarm output 2 is for the upper limit alarm mode. To change the setting,
change the alarm type for alarm output 2 in initial setting level 5. For details, refer to the
“E5CSV/E5CS-U Digital Temperature Controller
User’s Manual”
(Cat. No. H140-E1-01).
Case Color: Black, Universal-input, Power Supply Voltage: 24 VAC/VDC
Control
modes
Alarms
Outputs
E5CSV
48
48mm
PID
2 (See note.)
Relay
Relay
Relay
input (thermocouple
thermometer)
E5CSV-RTD
E5CSV-QTD
E5CSV-R1TD
E5CSV-Q1TD
E5CSV-R2TD
E5CSV-Q2TD
User’s Manual”
Accessories (Order Separately)
Protective Cover
Hard Protective Cover
Y92A-48B
Model
DIN Track Mounting Adapter
Model
Y92F-52
Terminal Cover
Model
E53-COV10
Rubber Packing
Model
Y92S-29
The Rubber Packing is provided with the Digital Controller.
Terminal Cover
(For Controllers after the design change scheduled for October 2010)
Model
E53-COV17
The E53-COV10 Terminal Cover cannot be mounted to
Controllers that are manufactured after the design change
E5CSV
Ratings
Supply voltage
Operating voltage range
Power consumption
Sensor input
Control
output
Relay output
100 to 240 VAC, 50/60 Hz
24 VAC, 50/60 Hz; 24 VDC
85% to 110% of rated supply voltage
100 to 240 VAC: 5 VA
24 VAC: 3 VA, 24 VDC: 2 W
Thermocouple input type:
K, J, L
Platinum resistance thermometer input type:
Pt100, JPt100
Universal-input (thermocouple/platinum resistance thermometer) type: K, J, L, T, U, N, R, Pt100, JPt100
SPST-NO, 250 VAC, 3A (resistive load)
ON/OFF or 2-PID (with auto-tuning)
SPST-NO, 250 VAC, 1A (resistive load)
Digital setting using front panel keys
7-segment digital display (character height: 13.5 mm) and deviation indicators
Setting change prohibit (key protection)
Input shift
Temperature unit change (°C/°F)
Direct/reverse operation
Temperature range, Sensor switching (K/J/L, Pt100/JPt100)
Switching is performed between a thermocouple and platinum resistance thermometer for universal-input models.
Control period switching
8-mode alarm output
Sensor error detection
−10
to 55°C (with no condensation or icing); with 3-year guarantee:
−10
to 50°C
25% to 85%
−25
to 65°C (with no condensation or icing)
Voltage output (for driving the SSR)
12 VDC, 21 mA (with short-circuit protection circuit)
Control method
Alarm output
Setting method
Indication method
Other functions
Ambient operating temperature
Ambient operating humidity
Storage temperature
Note: 1.
Do not use an inverter output as the power supply. (Refer to
Safety Precautions for All Temperature Controllers.)
2.
Models for 24 VAC/DC can also be manufactured.
Characteristics
Setting accuracy
Indication accuracy
(ambient temperature of 23°C)
Influence of temperature
Influence of voltage
Influence of EMS. (at EN61326-1)
Hysteresis (for ON/OFF control)
Proportional band (P)
Integral time (I)
Derivative time (D)
Alarm output range
Control period
Sampling period
Insulation resistance
Dielectric strength
Vibration
resistance
Shock resistance
Life expectancy
Weight
Degree of protection
Memory protection
EMC
Thermocouple (See note 1.):
(±0.5% of indication value or ±1°C, whichever is greater) ±1 digit max.
Platinum resistance thermometer (See note 2.): (±0.5% of indication value or ±1°C, whichever is greater) ±1 digit max.
R thermocouple inputs:
(±1% of PV or ±10°C, whichever is greater) ±1 digit max.
Other thermocouple inputs:
(±1% of PV or ±4°C, whichever is greater) ±1 digit max.
Platinum resistance thermometer inputs: (±1% of PV or ±2°C, whichever is greater) ±1 digit max.
0.2% FS (0.1% FS for universal-input (thermocouple/platinum resistance thermometer) models)
1 to 999°C (automatic adjustment using auto-tuning/self-tuning)
1 to 1,999 s (automatic adjustment using auto-tuning/self-tuning
1 to 1,999 s (automatic adjustment using auto-tuning/self-tuning)
Absolute-value alarm: Same as the control range
Other:
0 to input setting range full scale (°C or
°F)
Alarm hysteresis:
0.2°C or
°F
(fixed)
2/20 s
500 ms
20 MΩ min. (at 500 VDC)
2,000 VAC, 50/60 Hz for 1 min between current-carrying terminals of different polarity
Malfunction
10 to 55 Hz, 20 m/s
for 10 min each in X, Y, and Z directions
Destruction
10 to 55 Hz, 0.75-mm single amplitude for 2 hr each in X, Y, and Z directions
Malfunction
100 m/s
min., 3 times each in 6 directions
Destruction
300 m/s
Electrical
100,000 operations min. (relay output models)
Approx. 120 g (Controller only)
Front panel: Equivalent to IP66; Rear case: IP20; Terminals: IP00
EEPROM (non-volatile memory) (number of writes: 1,000,000)
EMI Radiated:
EMI Conducted:
ESD Immunity:
EN 55011 Group 1 Class A
EN 61000-4-2: 4 kV contact discharge (level 2)
8 kV air discharge (level 3)
Radiated Electromagnetic Field Immunity:
EN 61000-4-3: 10 V/m (80-1000 MHz, 1.4-2.0 GHz amplitude modulated) (level 3)
10 V/m (900 MHz pulse modulated)
Conducted Disturbance Immunity:
EN 61000-4-6: 3 V (0.15 to 80 MHz) (level 2)
Noise Immunity (First Transient Burst Noise): EN 61000-4-4
Burst Immunity:
2 kV power-line (level 3), 1 kV I/O signal-line (level 3)
Surge Immunity:
EN 61000-4-5: Power line:
Normal mode 1 kV; Common mode 2 kV
Output line (relay output): Normal mode 1 kV; Common mode 2 kV
Voltage Dip/Interrupting Immunity:
EN 61000-4-11 0.5 cycle, 100% (rated voltage)
UL 61010-1 (listing)
CSA C22.2 No.1010-1
EN61326-1 (See note 3.), EN61010-1, IEC61010-1
VDE 0106 Part 100 (finger protection), when the terminal cover is mounted.
Approved standards
Conformed standards
Note: 1.
The following exceptions apply to thermocouples.
U, L: ±2°C ±1 digit max.
R: ±3°C ±1 digit max. at 200°C or less
2.
The following exceptions apply to platinum resistance thermometers.
Input set values 0, 1, 2, 3 for E5CSV: 0.5% FS ±1 digit max.
3.
Industrial electromagnetic environment (EN/IEC 61326-1 Table 2)
E5CSV
Temperature Range
Thermocouple Input Models
Input
999
J/L
Temperature
range
(selected
using switch)
(Default setting: 2)
1,000
900
800
700
Platinum Resistance Thermometer Input Models
(Default setting: 3)
Universal-input (Thermocouple/Platinum Resistance Thermometer) Models
Using Thermocouple Sensors, Control Mode Switch 5: OFF
Input
1,700
1,600
1,500
1,400
1,300
1,200
1,100
1,000
900
800
700
−100
(Default setting: 0)
Using Platinum Resistance Thermometers, Control Mode Switch 5: ON
Input
Setting number
Minimum setting unit
1°C
1°C
The shaded value indicates the default
setting status.
Temperature
range
(selected
using switch)
Input
−100
JPt100/Pt100
−50
50.0
0.0
−20
99.9
0.0
Setting number
1°C
0.1°C
1°C
0.1°C
1°C
0.1°C
setting status.
U
Temperature
range
(selected
using switch)
1,300
1,300
850
850
0.0
199.9
0.0
199.9
0.0
−99
−99
−99
−99
−99
−99
Setting number
1°C
0.1°C
1°C
0.1°C
1°C
0.1°C
1°C
setting status.
Pt100
850
JPt100
Temperature
range
(selected
using switch)
1,000
900
800
700
−100
99
−99
0.0
−99
−99
0.0
99
−99
Setting number
1°C
0.1°C
1°C
0.1°C
1°C
setting status.
E5CSV
External Connection Diagram
output
models
(See note 1.)
Relay output
models
Alarm output
output
Relay output
VDC,
21 mA
Thermocouple
input
Alarm output 2 (See note 3
Alarm output 1 (See note 3
Platinum resistance
thermometer input
100 to 240
VAC,
50/60 Hz
(24
VAC/VDC)
(See note 2.)
Thermocouple/
universal-input
Note: 1.
The voltage output (12 VDC, 21 mA) is not electrically isolated from the internal circuits. When using a grounding thermocouple, do not
connect output terminals 1 or 2 to ground. Otherwise, unwanted current paths will cause measurement errors.
2.
Models with 100 to 240 VAC and 24 VAC/VDC are separate. Models using 24 VDC have no polarity.
3.
The number of alarm outputs depends on the model.
Nomenclature
E5CSV Models with Terminal Blocks
Output indicator
Deviation indicators
Mode indicators
Mode Key
Lock Release Key
Temperature display
Alarm indicators
Up Key
Down Key