Embedded Power for
Business-Critical Continuity
NLP65 Series
Single, dual,
and triple output
Total Power:
Input Voltage:
# of Outputs:
Rev.11.06.08_102
NLP65 Series
1 of 4
65 - 75W
85 - 264 Vac
120 - 370 Vdc*
Single, dual,
triple
Electrical Specifications
Special Features
• Universal Input
• 3” x 5” footprint
• Low profile fits 1U applications
• EN61000-3-2 compliance
option (HCC)
• Overvoltage and short circuit
protection
• 65 W with free air convection
cooling
• EN55022, EN55011 conducted
emissions level B
• EN61000-4-2,-3,-4, -5, -6
immunity compliant
• RoHS compliant
• LPX80 enclosure kit available
• 2 year warranty
Input
Input voltage range:
Universal input,
(See Note 2)
NLP65-76xx version only
120 Vac
230 Vac
120 Vac, 60 Hz
230 Vac, 50 Hz
120 Vac, with PFC
230 Vac, with PFC
120 Vac, without PFC
230 Vac, without PFC
UL/IEC127
Main output
Auxiliary outputs
At turn-on
Main output
25% step
at 0.1 A/µs
Main outputs
Cyclic operation
Single and multiple
85-264 Vac
120-370 Vdc
47-63 Hz
17 A max.
32 A max.
0.7 mA
1.4 mA
1.05 A rms
0.51 A rms
1.40 A rms
0.80 A rms
S3.15 A, 250 Vac In live and neutral
±2.0%
±5.0%
1.0 s, max
5.0% or 250 mV
max. dev., 1ms max.
recovery to 1%
±0.02%/°C
125%, ±10%
Continuous
(See Note 6)
Input frequency range:
Input current:
(cold start)
Safety ground
leakage current:
Input current:
Input fuse:
Output
Total regulation:
(line and load)
Rise time:
Transient response:
Safety
VDE0805/EN60950/IEC950
File No. 1040100-3336-0096
License No. 114404
UL1950 File No. E136005
CSA C22.2 No. 950
File No. LR41062C
China Compulsory
Certification 60950
Temperature coefficient:
Overvoltage protection:
Short circuit protection:
Minimum output current:
*NLP65-76xx version only
Embedded Power for
All specifications are typical at nominal input, full load at 25° C unless otherwise stated.
EMC Charateristics
(11, 12)
Conducted emissions:
ESD air:
ESD contact:
Surge:
Fast transients:
Radiated immunity:
Conducted immunity:
EN55022, FCC part 15
EN61000-4-2, level 3
EN61000-4-2, level 4
EN61000-4-4, level 3
EN61000-4-3, level 3
EN61000-4-6, level 3
Level B
Perf. criteria 1
Perf. criteria 1
Perf. criteria 1
Perf. criteria 1
Perf. criteria 2
Perf. criteria 2
Rev.11.06.08_102
NLP65 Series
2 of 4
General Specifications
Hold-up time:
Efficiency:
Isolation voltage:
Switching frequency:
120 Vac, 60 Hz
230 Vac, 50 Hz
120 Vac, 65 W
Input/output
Input/chassis
Fixed
16 ms @ 65 W
78 ms @ 65 W
72% typical
3000 Vac
1500 Vac
100 kHz, ±5 kHz
Approvals and standards: EN60950, VDE0805
(see Notes 9, 13)
IEC950, UL1950, CCC60950
CSA C22.2 No. 950
Weight:
MTBF demonstrated:
283 g (10 oz)
MIL-HDBK-217F
150,000 hours min
Environmental Specifications
Thermal performance:
(see Notes 1, 3, 10)
Operating ambient,
0 °C to +70 °C
(See derating curve)
Non-operating
-40 °C to +85 °C
50 °C to 70 °C ambient,
Derate to
convection cooled
50% load
0 °C to 50 °C, ambient,
65 W
convection cooled
0 °C to 50 °C ambient,
75 W
20 CFM forced air (See Note 10)
Peak (0 °C to +50 °C, 60 s) See table
Non-condensing
Operating
Non-operating
5-500 Hz
per MIL-STD-810E
5% to 95% RH
10,000 feet max
30,000 feet max
2.4 G rms peak
516.4 Part IV
DERATING CURVE
Output Power (Watts)
75W
20 CFM FORCED AIR COOLING
65W
NATURAL
CONVECTION
COOLING
38W
32W
Relative humidity:
Altitude:
Vibration (see Note 5):
Shock:
0°C
10°C 20°C 30°C 40°C 50°C 60°C 70°C
Embedded Power for
Output Current
Output
+5 V (IA)
+12 V (IB)
–12 V
+5 V (IA)
+15 V (IB)
–15 V
+5 V
+24 V
+12 V
+5 V (IA)
+24 V (IB)
+5 V (IA)
+12 V (IB)
+5 V
+12 V
+15 V
+24 V
Max (1)
7.5 A
2.5 A
0.65 A
7.5 A
2.2 A
0.65 A
7.0 A
1.5 A
0.7 A
7 A
2 A
7 A
2.5 A
10 A
5.4 A
4.4 A
2.7 A
Peak (3)
9.1 A
3.3 A
0.81 A
9.1 A
2.9 A
0.85 A
9.1 A
2.6 A
1.0 A
9.1 A
2.6 A
9.1 A
3.3 A
13 A
7 A
5.7 A
3.5 A
Fan (10)
8 A
3 A
0.8 A
8 A
2.5 A
0.8 A
8.0 A
2.0 A
1.0 A
8 A
2 A
8 A
3 A
12 A
6.5 A
5.3 A
3.5 A
Ripple (4)
50 mV
150 mV
120 mV
50 mV
150 mV
150 mV
50 mV
240 mV
120 mV
50 mV
240 mV
50 mV
150 mV
50 mV
120 mV
150 mV
240 mV
Total
Non-harmonic
Harmonic
Regulation (6)
Corrected
Corrected
±2.0%
NLP65-7608J
NLP65-9608J
±5.0%
±5.0%
±2.0%
±5.0%
±5.0%
±2.0%
±5.0%
±5.0%
±2.0%
±5.0%
±2.0%
±5.0%
±2.0%
±2.0%
±2.0%
±2.0%
NLP65-7605J
NLP65-7612J
NLP65-7615J
NLP65-7624J
NLP65-9605J
NLP65-9612J
NLP65-9615J
NLP65-9624J
NLP65-X605GJ
NLP65-X612GJ
NLP65-X615GJ
NLP65-X624GJ
NLP65-7629J
NLP65-9629J
NLP65-X629GJ
NLP65-7620J
NLP65-9620J
NLP65-X620GJ
NLP65-3322J
(15)
NLP65-7610J
NLP65-9610J
NLP65-X610GJ
Ground
Pin (12, 14, 17)
NLP65-X608GJ
Rev.11.06.08_102
NLP65 Series
of 4
Natural convection cooling. Models NLP65-X629J, NLP65-X608J, NLP65-
X610J must not exceed 62.5 Watts continuous output power with natural
convection. Model NLP65-X620J not to exceed 65 Watts continuous output
power with natural convection. Model NLP65-3322J must not exceed 60 Watts
continuous output power with natural convection.
When the input voltage is less than 90 Vac the operating temperature range is
C to +40
C. The ripple and regulation specifications may not be met.
Peak output current lasting less than 60 seconds with duty cycle less than 5%.
During peak loading, output voltage may exceed total regulation limits.
Figure is peak-to-peak for convection power rating. Output noise
measurements are made across a 20 MHz bandwidth using a 6 inch twisted
pair, terminated with a 10 µF electrolytic capacitor and a 0.1 µF ceramic
capacitor.
Three orthogonal axes, random vibration 10 minutes for each axes, 2.4 G rms 5
Hz to 500 Hz.
A minimum load on the main output is required for proper start up. For
multiple outputs and single +5V output, the minimum load on the +5 V is
0.2 A. For single outputs greater than +5 V the minimum load is 0.1 A. To
maintain stated regulation then:
for single output units
I ≥ 0.2 A
for multiple output units
0.25 ≤ I(A)/I(B) ≤ 5, for I(A) ≥ 0.2 A.
For optimum reliability, no part of the heatsink should exceed 120
o
C, and no
semiconductor case temperature should exceed 130
o
C.
CAUTION: Allow a minimum of 1 second after disconnecting line power when
making thermal measurements.
This product is only for inclusion by professional installers within other
equipment and must not be operated as a stand alone product.
Maximum continuous output power for all multiple output models must not
exceed 75 Watts (70 watts for NLP65-3322J)with 20 CFM forced air cooling.
Conducted emissions testing were performed using the standard EN55022 set-
up with a stand alone NLP65 unit placed on a grounded metal plate with a line
choke on the AC input and ground wires (i.e. the wires are looped through an
EMI suppression toroid).
For system compliance it is usually necessary to install an ‘off-the-shelf’ AC
inlet with an integral line filter in the system chassis or to install a line choke
on the input wires as close as possible to AC entry point of the system chasssis.
Please contact the applications group for assistance with EMI compliance.
The NLP65 units with the suffix ‘G’ is the ground pin and ground choke option.
J2, L6 and JP10 are included. J2 is a safety agency approved grounding pin, L6
is a ground choke and JP10 is a jumper. This option is intended for use in non-
metallic chassis applications where grounding is not possible via the mounting
screws. The ground choke is provided to assist system EMC compliance. When
performing conducted emissions testing on stand alone units, the ‘G’ option
is required to meet level B. To order simply add the suffix ‘G’ to the standard
model number, e.g. NLP65-7608GJ, NLP65-9608GJ. This option is available for
both the PFC and non-PFC versions.
All models require a minimum mounting stand-off of 0.25 inches (6.35 mm) in
the end use product.
The NLP65-9608J is available with an enclosure. To order an enclosed version,
see model numbering options below.
No PFC version, EN61000-3-2 is not applicable to this model.
The ‘J’ suffix indicates that these parts are Pb-free (RoHS 6/6) compliant.
17
NOTICE: Some models do not support all options. Please contact your local
Emerson Network Power representative or use the on-line model number
search tool at http://www.powerconversion.com.
Model Numbering Options
The enclosure version includes: IEC connector, on/off switch, wire harness
output connector and fitted cover. To order, please add the suffix ‘E’ the model
number, e.g. NLP65-9608EJ. See NLP65 enclosure for details.
A Safety earth ground pin and ground choke are available as an option.
To order, please add the suffix ‘G’ the model number, e.g. NLP65-X608GJ.
To order an enclosure kit (unfitted), order the part number LPX80.
Embedded Power for
Mechanical Drawing
5.00
(127.00)
4.550
(115.57)
0.225
(5.715)
Americas
5810 Van Allen Way
Carlsbad, CA 92008
USA
Telephone: +1 760 930 4600
Facsimile: +1 760 930 0698
Rev.11.06.08_102
NLP65 Series
4 of 4
Europe (UK)
J1
(64.770)
J3
Waterfront Business Park
Merry Hill, Dudley
West Midlands, DY5 1LX
United Kingdom
Telephone: +44 (0) 1384 842 211
Facsimile: +44 (0) 1384 843 355
3.00
(76.20)
J2
C19
T1
Asia (HK)
14/F, Lu Plaza
2 Wing Yip Street
Kwun Tong, Kowloon
Hong Kong
Telephone: +852 2176 3333
Facsimile: +852 2176 3888
For global contact, visit:
Mounting
Hole Diameter
0.156 (4.00)
MAXIMUM COMPONENT
HEIGHT 1.26 (32.00)
TOLERANCE: .xxx
.xx
ALL DIMENSIONS IN INCHES (mm)
0.005"
0.02"
techsupport.embeddedpower@
emerson.com
While every precaution has been taken to ensure
accuracy and completeness in this literature, Emerson
Network Power assumes no responsibility, and disclaims
all liability for damages resulting from use of this
information or for any errors or omissions.
INPUT
PIN CONNECTIONS
J1
Pin 1
Pin 2
Pin 3
Pin 1
AC Line
No Pin
AC Neutral
Safety Ground
Emerson Network Power.
The global leader in enabling
business-critical continuity.
Input and output connectors Mating connectors
AC (J1) connector type
Molex 26-60-4030 type.
DC (J3) connector type
Molex 26-60-4060 type.
AC (J1) mating connector type
Molex 09-50-3031 or equivalent with Molex
08-50-0105 or equivalent crimp terminals.
DC (J3) mating connector type
Molex 09-50-3061 with Molex 2478 phosphor
bronze crimp terminals or equivalent.
AC Power
Connectivity
DC Power
Embedded Computing
Embedded Power
Monitoring
Outside Plant
Power Switching & Controls
J2 (ON ‘G’ SUFFIX ONLY)
Note: The input and output connectors are the same as those used on NFS40,
NFN40, NAL40, NAN40 and NLP40.
J3
OUTPUT PIN CONNECTIONS
SINGLE
DUAL
V (A)
V (A)
V (A)
Return
Return
Return
V (B)
V (A)
V (A)
Return
Return
N/C
TRIPLE
V (B)
V (A)
V (A)
Return
Return
V (C)
Pin 1
Pin 2
Pin 3
Pin 4
Pin 5
Pin 6
Precision Cooling
Racks & Integrated Cabinets
Services
Surge Protection
EmersonNetworkPower. com
Emerson Network Power and the Emerson
Network Power logo are trademarks and
service marks of Emerson Electric Co. ©2008