首页 > 器件类别 > 电源/电源管理
NMP1K2-C#EKCH-00
NMP CONFIGURABLE POWER SUPPLY 12
器件类别:电源/电源管理
厂商名称:MEAN WELL
厂商官网:http://www.meanwell.com
器件标准:
类型
封闭式
输出数
电压 - 输入
90 ~ 264 VAC,120 ~ 370 VDC
电压 - 输出 1
5V
电压 - 输出 2
12V
电压 - 输出 3
48V
电压 - 输出 4
5V
电流 - 输出(最大值)
36A, 20A, 5A, 36A
功率(W)
1080W
应用
ITE(商业),医疗
电压 - 隔离
4kV
效率
88.5%
工作温度
-30°C ~ 70°C(有降额)
特性
可调输出,负载均分,PFC,远程开关,遥测,待机输出,通用输入
安装类型
底座安装
大小/尺寸
9.84" 长 x 5.00" 宽 x 1.61" 高(250.0mm x 127.0mm x 41.0mm)
认可
CB,CE,cURus,EAC,TUV
650W/1200W Modular Power
NMP
series
EN 60601-1
IEC 60601-1
(NMP1K2)
ANSI/AAMI ES60601-1
EN60601-1
IEC60601-1
Medical equipment
Diagnostic or biological facilities
MRI, CT and PET scanners
Test or measurement systems
Telecommunication equipment
Factory facility and aging equipment
Laser equipment
Medical (2x MOPP) safety approval
Suitable for BF application with appropriate system
consideration (
Touch current < 100uA/264VAC
1U low profile
Universal AC input / Full range
Output voltage and current programmable
Built-in parallel function / output programmable / global
enable / remote local ON-OFF / auxiliary DC output /
over temperature alarm / DC OK
Cooling by thermostatically controlled fan with fan alarm
function
Protections: Short circuit / Overload / Over voltage /
Over temperature for all output modules
5 years warranty
NMP family is a 1U low profile modular and configurable type power supply from MEAN WELL. This family
comprises two power wattage for the line-up, 650W and 1200W, and the output modules deliver up to 240W
with adjustable options for the major working voltages used in the industries 5V, 12V, 24V, 48V. NMP family
complies with
safety approval, the medical standard (2x MOPP between primary to secondary) offering the best
flexibility for various types of applications.
File Name:NMP-SPEC 2018-04-26
NMP
series
Output Configuration Guide
NMP
SLOT 1 SLOT 2 SLOT 3 SLOT 4 SLOT 5 SLOT 6
650/ 1K2 (650W/ 1200W)
Parallel or option code (See Table 1.)
Example: NMP 1K2 - C
SLOT 1 O/P: 5V@ 36A
SLOT 2 O/P: 12V@ 20A
SLOT 3 O/P: 24V@ 10A
SLOT 4 O/P: 24V@ 10A
SLOT 5 Blank slot
(with BLANK-NMS240)
SLOT 6 O/P: 48V@ 5A
K -
※650W
(4 SLOTS)
1200W (6 SLOTS)
Table 1. Parallel or option code
00
01
02
03
04
05
06
07
08
09
SLOT 1
SLOT 2
SLOT 3
SLOT 4
SLOT 5
SLOT 6
※Code
00, 01, 02, 03, 06, 07, 10 for NMP650
※Code
00~15 for NMP1K2
SPECIFICATION
Front-End
MODEL
VOLTAGE RANGE
FREQUENCY RANGE
POWER FACTOR
INPUT
EFFICIENCY(Typ.)
AC CURRENT
INRUSH CURRENT
LEAKAGE CURRENT
TOTAL OUTPUT POWER
OUTPUT
PROTECTION OVER TEMPERATURE
REMOTE CONTROL
FUNCTION
ALARM SIGNAL
AUXILIARY POWER(AUX)
WORKING TEMP.
WORKING HUMIDITY
ENVIRONMENT STORAGE TEMP., HUMIDITY
TEMP. COEFFICIENT
VIBRATION
SAFETY STANDARDS
ISOLATION LEVEL
WITHSTAND VOLTAGE
ISOLATION RESISTANCE
Note.4
Note.5
NMP
NMP1K2 (6 Slots)
series
NMP650 (4 Slots)
90 ~ 264VAC
47 ~ 63Hz
PF>0.95/230VAC
PF>0.98/115VAC at full load
120 ~370VDC
91%, full case load with H / K module at nominal 24V / 48V only 90.5%, full case load with H / K module at nominal 24V / 48V only
8 8 . 5 % , full case load with each type of module at nominal voltage
6.7A/230VAC
3.5A/230VAC
7.5A/115VAC
40A/230VAC
25A/115VAC
40A/230VAC
Earth leakage current <400uA / 264VAC, Touch current <100uA/264VAC
1200W max.
650W max.
Shut down o/p voltage, recovers automatically after temperature goes down
RC+/RC-: Short, Power ON
RC+/RC-: Open, Power OFF
TTL signal output for over temperature alarm. Please refer to the Function Manual.
5V @ 2A; tolerance
10%; ripple: 50mVp-p(max.)
5V @ 1.5A ; tolerance
10%; ripple: 50mVp-p (max.)
-30 ~ +70
(Derate at 50
, refer to "Derating Curve")
20 ~ 90% RH non-condensing
-40 ~ +85
, 10 ~ 95% RH non-condensing
0.03%/
(0 ~ 50
10~500Hz, 2G 10min./1 cycle, 60 min. each along X, Y, Z axes.
ANSI/AAMI ES60601-1, Ed. 3.1; TUV EN 60601-1, Ed. 3.1; IEC 60601-1, Ed. 3.1; EAC TP TC 004 approved;
Design refer to UL62368-1, TUV EN62368-1
Primary-Secondary: 2x MOPP, Primary-Earth: 1x MOPP
I/P-O/P: 4KVAC
I/P-FG: 2KVAC
O/P-FG: 0.5KVAC
Test Level / Note
I/P-O/P, I/P-FG, O/P-FG: 100M Ohms / 500VDC / 25
/ 70% RH
Standard
Conducted
Radiated
Harmonic Current
Voltage Flicker
EN60601-1-2, EN55024
ESD
RF field
EFT/ Burst
Surge
Conducted
Magnetic Field
Voltage Dips and Interruptions
Standard
EN61000-4-2
EN61000-4-3
EN61000-4-4
EN61000-4-5
EN61000-4-6
EN61000-4-8
EN61000-4-11
Test Level / Note
Level 4, 15KV air; Level 4, 8KV contact
Level 3, 10V/m
Level 3, 2KV
Level 4, 4KV/Line-FG; 2KV/Line-Line
Level 2, 3V
Level 4, 30A/m
100% dip 1 periods, 30% dip 25 periods,
100% interruptions 250 periods
250*127*41mm (L*W*H)
2Kg (typ.); 6pcs / 13Kg / 0.88CUFT
13.5A/115VAC
25A/115VAC
EN55032 (CISPR32) / EN55011 (CISPR11) Class B
EN61000-3-2
EN61000-3-3
Class A
EMC EMISSION
SAFETY &
EMC
(Note 5)
EMC IMMUNITY
OTHERS
DIMENSION
PACKING
250*89*41mm (L*W*H)
1.45Kg (typ.); 9pcs / 14Kg / 0.98CUFT
Output Module (240W)
MODEL
CONFIGURATION CODE
DC VOLTAGE
RATED CURRENT
CURRENT RANGE
NMS-240-05
5V
36A
0 ~ 36A
NMS-240-12
12V
20A
0 ~ 20A
240W
150mVp-p
6~15V
±1.0%
±0.3%
±0.5%
NMS-240-24
24V
10A
0 ~ 10A
240W
150mVp-p
15~30V
±1.0%
±0.2%
±0.5%
10ms/230VAC @ total output power
NMP
NMS-240-48
48V
5A
0 ~ 5A
240W
250mVp-p
30~55V
±1.0%
±0.2%
±0.5%
series
180W
RATED POWER
OUTPUT
(NMS-240) RIPPLE & NOISE (max.)
Note.2
100mVp-p
3 ~ 6V
VOLTAGE ADJ. RANGE
VOLTAGE TOLERANCE
Note.3
±2.0%
±0.5%
LINE REGULATION
LOAD REGULATION
SETUP, RISE TIME
HOLD UP TIME (Typ.)
OVERLOAD
PROTECTION
OVER VOLTAGE
OVER TEMPERATURE
REMOTE ON/OFF CONTROL
REMOTE SENSE
OUTPUT VOLTAGE PROGRAMMABLE(PV)
FUNCTION
±1.0%
1500ms, 60ms at full load
16ms/230VAC @ 75% total output power
105 ~ 125% rated output power
Protection type: constant current limiting protection
6.1 ~ 8V
15.1 ~ 20V
30.1 ~ 37V
56 ~ 66V
Protection type : Shut down o/p voltage, re-power on to recover
RC+/RC-: Open, Power ON
RC+/RC-: Short, Power OFF
Compensate voltage drop on the load wiring up to 0.5V.
6 ~ 15V
3 ~ 6V
15 ~ 30V
30 ~ 55V
Adjustment of output voltage is allowable. Please refer to the Function Manual.
OUTPUT CURRENT PROGRAMMABLE(PC)
Adjustment of constant current level is allowable. Please refer to the Function Manual.
5V@10mA; tolerance
10%, ripple: 50mVp-p (max.)
CURRENT SHARING(CS)
DC OK SIGNAL
DIMENSION
PACKING
Output modules turn on=4.5 ~ 5.5V, turn off=0 ~ 0.5V. Please refer to the Function Manual.
118.5*37.9*18mm (L*W*H)
0.142Kg (typ.); 72pcs / 11.2Kg / 1.04CUFT
OTHERS
NOTE
1. All parameters NOT specifically mentioned are measured at 230VAC input, rated load and 25
of ambient temperature.
2. Ripple & noise are measured at 20MHz of bandwidth by using a 12" twisted pair-wire terminated with a 0.1uf & 47uf parallel capacitor.
3. Tolerance: includes set up tolerance, line regulation and load regulation.
4. NMP650: The efficiency changes by installing different output modules. The following combination is chosen when fitting different types of module:
5V (Voltage code C)*1, 12V (Voltage code E)*1, 24V (Voltage code H)*1, 48V (Voltage code K)*1. (650W max.)
NMP1K2: The efficiency changes by installing different output modules. The following combination is chosen when fitting different types of module:
5V (Voltage code C)*1, 12V (Voltage code E)*1, 24V (Voltage code H)*2, 48V (Voltage code K)*2. (1200W max.)
The hold up time of the combination above is 16ms/230vac @ 75% total output power
10ms/230VAC @ total output power.
5. De-rating may be needed under low input voltages. Please check the derating curve for more details.
6. Under parallel operation ripple of the output voltage may be higher than the SPEC at light load condition.
7. The ambient temperature derating of 3.5
/1000m with fanless models and of 5
/1000m with fan models for operating altitude higher than 2000m (6500ft).
BLOCK DIAGRAM
NMP1K2 & NMP650
NMP
series
PFC fosc : 85KHz(NMP1K2)
70KHz(NMP650)
PWM fosc : 100KHz
I/P
EMI FILTER
ACTIVE INRUSH
CURRENT LIMITING
RECITIFERS
& PFC
POWER
SWITCHING
NMS-240
O/P
NMS-240
NMS-240
6 SLOTS
NMP1K2
NMS-240
4 SLOTS
NMP650
O.T.P
O.L.P
PFC
CONTROL
PWM
CONTROL
MCU
ALARM
CONTROL
RECTIFIERS
CONTROL ON/OFF
T-ALARM
REMOTE
ON/OFF
FAN
AUX
POWER
RECTIFIERS
& FILTER
AUX POWER
5V/2A(NMP1K2)
5V/1.5A(NMP650)
NMS-240
PWM fosc : 175KHz
+S
POWER
SWITCHING
RECTIFIERS
& FILTER
POWER
SWITCHING
+V
-V
-S
O.L.P
O.V.P
PWM
CONTROL
O.C.P
O.T.P
RECTIFIERS
CONTROL
ON/OFF
DETECTION
CIRCUIT
DC OK & LED
PV
PC
REMOTE
ON/OFF
CURRENT
SHARE
CS
RECTIFIERS
FILTER
AUX POWER
(5V/10mA)