QS5.DNET
Q-Series
24V, 3.8A, NEC C
LASS
2, D
EVICE
ET
OWER
UPPLY
OWER
UPPLY
AC 100-240V Wide-range Input
DeviceNet
Approved
NEC Class 2 Compliant
Width only 40mm
Efficiency up to 92%
Active Power Factor Correction (PFC)
DC Input from 88 to 360Vdc
Negligible low Inrush Current Surge
Short-term Operation down to 60Vac and up to 300Vac
Full Power Between -25°C and +60°C
DC-OK Relay Contact
Quick-connect Spring-clamp Terminals
3 Year Warranty
ENERAL
ESCRIPTION
The QS5.DNET power supply is a derivate of the
Dimension QS5 family, which is specially designed to
meet the DeviceNet
requirement. The QS5.DNET exists
beside the QS10.DNET, which is the right choice to
supply networks with the thick cables.
The specialties of DeviceNet
power supplies are:
The nominal and overload currents are sized for the
ratings of the DeviceNet
cables.
Large load capacitors can be charged in a very short
period of time.
After turn on, the output voltage increases according
to the DeviceNet
timing specification.
The upper level of the output level is limited to
protect the network.
The most outstanding features are a high efficiency,
compact size, wide-range input voltage, a very low
inrush surge and a DC-ok contact. High immunity to
transients and power surges and a low electromagnetic
emission makes usage in nearly every environment
possible.
Unique quick-connect spring-clamp terminals allow a
safe and fast installation. A large international approval
package makes this unit suitable for nearly every
situation.
HORT
FORM
ATA
Output voltage
Adjustment range
Output current
Output power
Output ripple
Input voltage
Mains frequency
AC Input current
Power factor
AC Inrush current
Efficiency
Losses
Temperature range
Derating
Hold-up time
Dimensions
DC 24V
fixed
3.8A
91.2W
< 50mVpp
AC 100-240V
50-60Hz
0.85 / 0.45A
0.98 / 0.90
typ. 9 / 11A peak
91.4 / 92.0%
8.6 / 7.9W
-25°C to +70°C
2W/°C
typ. 44 / 85ms
40x124x117mm
not adjustable
continuous
continuous
20Hz to 20MHz
+10%/-15%
±6%
at 120 / 230Vac
at 120 / 230Vac
at 120 / 230Vac
at 120 / 230Vac
at 120 / 230Vac
operational
+60 to +70°C
at 120 / 230Vac
WxHxD
RDER
UMBERS
Power Supply
Accessory
QS5.DNET
ZM1.WALL
ZM12.SIDE
UF20.241
24V DeviceNet
unit
Wall mount bracket
Side mount bracket
Buffer unit
ARKINGS
IND. CONT. EQ.
UL 508
UL 60950-1
Class I Div
Marine
EMC, LVD
Mar. 2013 / Rev. 2.2 DS-QS5.DNET-EN
All parameters are specified at 24V, 3.8A, 230Vac, 25°C ambient and after a 5 minutes run-in time unless otherwise noted.
www.pulspower.com Phone +49 89 9278 0
Germany
1/21
QS5.DNET
Q-Series
24V, 3.8A, NEC C
LASS
2, D
EVICE
ET
OWER
UPPLY
NDEX
Page
1.
2.
3.
4.
5.
6.
7.
8.
9.
10.
11.
12.
13.
14.
15.
16.
17.
18.
19.
20.
Intended Use .......................................................3
Installation Requirements...................................3
AC-Input...............................................................4
DC-Input...............................................................5
Input Inrush Current ...........................................5
Output .................................................................6
Hold-up Time.......................................................7
DC-OK Relay Contact ..........................................7
Efficiency and Power Losses................................8
Reliability .............................................................9
Functional Diagram...........................................10
Terminals and Wiring........................................10
Front Side and User Elements...........................11
EMC....................................................................12
Environment ......................................................13
Protection Features ...........................................14
Safety Features ..................................................14
Dielectric Strength ............................................14
Approvals...........................................................15
Fulfilled Standards ............................................15
Page
21. Used Substances ............................................... 16
22. Physical Dimensions and Weight ..................... 16
23. Accessories ........................................................ 17
23.1. ZM1.WALL Wall Mounting Bracket .......17
23.2. ZM12.SIDE Side Mounting Bracket ........17
23.3. UF20.241 Buffer Module ..........................17
24. Application Notes............................................. 18
24.1. Peak Current Capability ...........................18
24.2. Back-feeding Loads ..................................18
24.3. External Input Protection.........................19
24.4. Charging of Batteries ...............................19
24.5. Output Circuit Breakers............................19
24.6. Parallel Use to Increase Output Power....20
24.7. Parallel Use for Redundancy ....................20
24.8. Series Operation .......................................20
24.9. Inductive and Capacitive Loads................20
24.10. Operation on Two Phases ........................20
24.11. Use in a Tightly Sealed Enclosure ............20
24.12. Mounting Orientations ............................21
The information presented in this document is believed to be accurate and reliable and may change without notice.
No part of this document may be reproduced or utilized in any form without permission in writing from the publisher.
ERMINOLOGY AND
BREVIATIONS
PE and
T.b.d.
AC 230V
symbol
PE is the abbreviation for
Protective Earth
and has the same meaning as the symbol
This document uses the term “earth” which is the same as the U.S. term “ground”.
To be defined, value or description will follow later.
A figure displayed with the AC or DC before the value represents a nominal voltage with
standard tolerances (usually ±15%) included.
E.g.: DC 12V describes a 12V battery disregarding whether it is full (13.7V) or flat (10V)
A figure with the unit (Vac) at the end is a momentary figure without any additional
tolerances included.
As long as not otherwise stated, AC 230V parameters are valid at 50Hz mains frequency.
A key word indicating flexibility of choice with no implied preference.
A key word indicating a mandatory requirement.
A key word indicating flexibility of choice with a strongly preferred implementation.
Earth, Ground
230Vac
50Hz vs. 60Hz
may
shall
should
Germany
2/21
QS5.DNET
Q-Series
24V, 3.8A, NEC C
LASS
2, D
EVICE
ET
OWER
UPPLY
1. I
NTENDED
U
SE
This device is designed for installation in an enclosure and is intended for the general use such as in industrial control,
office, communication, and instrumentation equipment.
Do not use this power supply in aircraft, trains, nuclear equipment or similar systems where malfunction may cause
severe personal injury or threaten human life.
This device is designed for use in hazardous, non-hazardous, ordinary or unclassified locations.
2. I
NSTALLATION
EQUIREMENTS
This device may only be installed and put into operation by qualified personnel.
This device does not contain serviceable parts. The tripping of an internal fuse is caused by an internal defect.
If damage or malfunction should occur during installation or operation, immediately turn power off and send unit to
the factory for inspection.
Mount the unit on a DIN-rail so that the output terminals are located on the top and input terminals are located on
the bottom of the unit. For other mounting orientations see de-rating requirements in this document. See chapter
24.12.
This device is designed for convection cooling and does not require an external fan. Do not obstruct airflow and do
not cover ventilation grid (e.g. cable conduits) by more than 30%!
Keep the following installation clearances: 40mm on top, 20mm on the bottom, 5mm on the left and right sides are
recommended when the device is loaded permanently with more than 50% of the rated power. Increase this clearance
to 15mm in case the adjacent device is a heat source (e.g. another power supply).
WARNING
Risk of electrical shock, fire, personal injury or death.
- Do not use the power supply without proper grounding (Protective Earth). Use the terminal on the input block for
earth connection and not one of the screws on the housing.
- Turn power off before working on the device. Protect against inadvertent re-powering.
- Make sure that the wiring is correct by following all local and national codes.
- Do not modify or repair the unit.
- Do not open the unit as high voltages are present inside.
- Use caution to prevent any foreign objects from entering the housing.
- Do not use in wet locations or in areas where moisture or condensation can be expected.
- Do not touch during power-on, and immediately after power-off. Hot surfaces may cause burns.
Germany
3/21
QS5.DNET
Q-Series
24V, 3.8A, NEC C
LASS
2, D
EVICE
ET
OWER
UPPLY
3. AC-I
NPUT
AC input
AC input range
nom.
min.
min.
min.
max.
nom.
typ.
typ.
typ.
AC 100-240V
85-264Vac
60-85Vac
264-300Vac
264Vac
50–60Hz
82Vac
78Vac
58Vac
AC 100V
1.02A
0.99
1.48
120ms
18ms
38ms
100mV
suitable for TN-, TT- and IT mains networks
continuous operation
full power for 200ms, no damage between 0 and 85Vac
< 500ms
continuous, IEC 62103
±6%
steady-state value, see Fig. 3-1
dynamic value
AC 120V
0.85A
0.98
1.55
110ms
18ms
38ms
100mV
AC 230V
0.48A
0.90
1.71
85ms
18ms
38ms
100mV
Allowed voltage L or N to earth
Input frequency
Turn-on voltage
Shut-down voltage
Input current
Power factor *)
Crest factor **)
Start-up delay
Rise time
Turn-on overshoot
typ.
typ.
typ.
typ.
typ.
typ.
max.
at 3.8A, see Fig. 3-3
at 3.8A, see Fig. 3-4
at 3.8A
see Fig. 3-2
0mF, 3.8A, see Fig. 3-2
3.8mF, 3.8A, see Fig. 3-2
see Fig. 3-2
*) The power factor is the ratio of the true (or real) power to the apparent power in an AC circuit.
**) The crest factor is the mathematical ratio of the peak value to RMS value of the input current waveform.
Fig. 3-1
Input voltage range
Fig. 3-2
Turn-on behavior, definitions
max.
500ms
OUT
full
power
for
200ms
Rated
input range
Input
Shut-down
Turn-on
IN
60V
85V
264V 300Vac
Start-up
delay
Rise
Time
Fig. 3-3
Input current vs. output load at 24V
Fig. 3-4
Power factor vs. output load
1.2A
0.6
0.4
0.2
Input
Current, typ.
Power Factor, typ.
ac
0V
1 0
ac
0.9
0.85
0.8
100Vac
120Vac
ac
230V
230V
ac
Output Current
0.5 1.0 1.5 2.0 2.5 3.0 3.5 4.0A
0.75
Output Current
Germany
Overshoot
Output
- 5%
4/21
QS5.DNET
Q-Series
24V, 3.8A, NEC C
LASS
2, D
EVICE
ET
OWER
UPPLY
4. DC-I
NPUT
DC input
DC input range
DC input current
Allowed Voltage L/N to Earth
Turn-on voltage
Shut-down voltage
nom.
min.
typ.
max.
typ.
typ.
DC 110-300V
88-360Vdc
0.91A / 0.33A
375Vdc
80Vdc
76Vdc
±20%
110Vdc / 300Vdc, at 3.8A
IEC 62103
steady state value
steady state value
Fig. 4-1
Wiring for DC Input
Battery
Power Supply
AC
PE
Load
Instructions for DC use:
a) Use a battery or similar DC source.
For other sources contact PULS
b) Connect +pole to L and –pole to N.
c) Connect the PE terminal to a earth wire or to the machine
ground.
DC
5. I
NPUT
NRUSH
URRENT
An active inrush limitation circuit limits the input inrush current after turn-on of the input voltage and after short
input voltage interruptions.
The charging current into EMI suppression capacitors is disregarded in the first microseconds after switch-on.
AC 100V
15A
peak
8A
peak
1A
s
AC 120V
15A
peak
9A
peak
1A
s
AC 230V
15A
peak
11A
peak
1A
s
Inrush current
Inrush energy
max.
typ.
max.
over entire temperature range
Fig. 5-1
Input inrush current, typical behavior
Input Current
Input Voltage
Input:
Output:
Ambient:
Upper curve:
Middle curve:
Lower curve:
Time basis:
230Vac
24V, 3.8A
25°C
Input current 5A / DIV
Input voltage 500V / DIV
Output voltage 20V / DIV
40ms / DIV
Output Voltage
Germany