首页 > 器件类别 > 光电子/LED > 光电
RM1A48D50
RELAY SSR 50A 480V
器件类别:光电子/LED    光电
厂商名称:Carlo Gavazzi
器件标准:
RM1A48D50 在线购买
供应商:
器件:RM1A48D50
价格:-
最低购买:-
库存:点击查看
点击购买
是否Rohs认证
符合
compliant
控制电流
0.005 A
控制电压
4.5 V
输入类型
DC
70 °C
-20 °C
输出电路类型
SCR
总高度
28.8 mm
总长度
58.2 mm
Base Number Matches
Solid State Relays
Industrial, 1-Phase ZS (IO) w. LED and Built-in Varistor
Types RM 23, RM 40, RM 48, RM 60
• Zero switching (RM1A) or instant-on
switching (RM1B) AC Solid State Relay
• Direct copper bonding (DCB) technology
• LED indication
• Built-in varistor
• Clip-on IP 20 protection cover
• Self-lifting terminals
• Housing free of moulding mass
• 2 input ranges: 3-32* VDC and 20-280VAC/22-48VDC
• Operational ratings: Up to 100AACrms and 600VACrms
• Blocking voltage: Up to 1400V
p
• Opto-isolation: > 4000VACrms
s
Product Description
The industrial, 1-phase relay
with antiparallel thyristor
output is the most widely
used industrial SSR due
to its multiple application
possibilities.
The
relay
can be used for resistive,
inductive and capacitive
loads. The zero switching
relay switches ON when the
sinusoidal curve crosses zero
and switches OFF when the
current crosses zero.
The instant-on relay with DC
control input can be used
for phase control. The built-
in varistor secures transient
protection for the heavy
industrial applications, and
the LED indicates the status
of the control input. The
clip-on cover is securing
touch protection to IP 20.
Protected output terminals
can handle cables up to
16mm
Ordering Key
Solid State Relay
Number of poles
Switching mode
Rated operational voltage
Control voltage
Rated operational current
RM 1 A 23 D 25
Type Selection
Switching
mode
A: Zero Switching (ZC)
B: Instant-on switching (IO)
(DC Control only)
Rated operational
voltage
23: 230VACrms
40: 400VACrms
48: 480VACrms
60: 600VACrms
Control voltage
A: 20-280VAC / 22-48VDC
D: 3-32VDC*
*4 to 32VDC for 400, 480 and 600VAC types
*4 to 32VDC for RM1B types
Rated operational
current
25: 25AACrms
50: 50AACrms
75: 75AACrms
100: 100AACrms
Selection Guide
Rated opera-
tional voltage
230VACrms
Blocking Control
voltage
voltage
650V
p
3 - 32VDC
20 to 280VAC
22 to 48VDC
4 - 32VDC
20 to 280VAC
22 to 48VDC
4 - 32VDC
20 to 280 VAC
22 to 48VDC
4 - 32VDC
20 to 280VAC
22 to 48VDC
Rated operational current with suitable heatsink
25A
50A
75A
RM1A23D25
RM1A23A25
RM1A40D25
RM1A40A25
RM1A48D25
RM1A48A25
RM1A60D25
RM1A60A25
RM1A23D50
RM1A23A50
RM1A40D50
RM1A40A50
RM1A48D50
RM1A48A50
RM1A60D50
RM1A60A50
RM1A23D75
RM1A23A75
RM1A40D75
RM1A40A75
RM1A48D75
RM1A48A75
RM1A60D75
RM1A60A75
100A
RM1A23D100
RM1A23A100
RM1A40D100
RM1A40A100
RM1A48D100
RM1A48A100
RM1A60D100
RM1A60A100
400VACrms
850V
p
480VACrms
1200V
p
600VACrms
1400V
p
Specifications are subject to change without notice (13.06.2018)
RM1A, RM1B
General Specifications
RM1.23...
Operational voltage range
RM1A...
RM1B...
Blocking voltage
Zero voltage turn-on
Operational frequency range
Power factor
Approvals
CE-marking
Isolation
Input to Output
input and Output to case
* Heatsink must be connected to ground
RM1.40...
42 to 440VACrms
42 to 440VACrms
850V
p
≤ 10V
45 to 65Hz
> 0.5 @ 400VACrms
UR, cUR, CSA, CCC, EAC
RM1.48...
42 to 530VACrms
42 to 530VACrms
1200V
p
≤ 10V
45 to 65Hz
> 0.5 @ 480VACrms
RM1.60...
42 to 660VACrms
42 to 660VACrms
1400V
p
≤ 10V
45 to 65Hz
> 0.5 @ 600VACrms
24 to 265VACrms
42 to 265VACrms
650V
p
≤ 10V
45 to 65Hz
> 0.5 @ 230VACrms
Yes
4000 Vrms
4000 Vrms
Yes
4000 Vrms
4000 Vrms
Yes
4000 Vrms
4000 Vrms
Yes *
4000 Vrms
4000 Vrms
Input Specifications
RM1...D..
Control voltage range
RM1A23...
RM1A40... RM1A48... RM1A60...
RM1B...
Pick-up voltage @ Ta = 25˚C
RM1A23...
RM1B ...
Reverse voltage
Drop out voltage
Input current @ max input voltage
RM1A
RM1B
Response time pick-up
RM1A
RM1B
Response time drop-out
RM1...A..
3 - 32VDC
4 - 32VDC
4 - 32VDC
2.5VDC
3.5VDC
3.5VDC
32VDC
1.2VDC
≤12 mA
≤15 mA
≤1/2 cycle
≤0.1ms
≤1/2 cycle
20 - 280VAC, 22 - 48VDC
18VAC/DC
18VAC/DC
6VAC/DC
≤ 20mA
≤ 12ms
≤ 40ms
Output Specifications
RM1....25
AC51 @ Ta=25°C
AC53a @ Ta=25°C
Min. operational current
Rep. overload current t=1 s
Non-rep. surge current t=10 ms
Off-state leakage current @
rated voltage and frequency
t for fusing t=10 ms
Critical dV/dt off-state min.
Endurance testing acc. to UL508
25Arms
5Arms
150mA
< 55AACrms
325A
p
< 3mArms
< 525A
s
1000V/µs
100,000 cycles
RM....50
50Arms
15Arms
250mA
< 125AACrms
600A
p
< 3mArms
< 1800A
s
1000V/µs
100,000 cycles
RM1....75
75Arms
20Arms
400mA
< 150AACrms
1150A
p
< 3mArms
< 6600A
s
1000V/µs
100,000 cycles
RM1....100
100Arms
30Arms
500mA
< 200AACrms
1900A
p
< 3mArms
<18000A
s
1000V/µs
6,000 cycles
Note: UL requirement for General Use Endurance testing is 6,000 cycles
RM1A, RM1B
Motor Ratings*: HP (UL508)
230VAC
RM1..25
RM1..50
RM1..75
RM1..100
* with suitable heatsink
400VAC
3HP
5HP
10HP
15HP
480VAC
3HP
7.5HP
10HP
20HP
600VAC
5HP
10HP
15HP
25HP
1.5HP
3HP
5HP
7.5HP
Electromagnetic Compatibility
EMC Immunity
Electrostatic Discharge (ESD)
Immunity
Air discharge, 8kV
Contact, 4kV
Electrical Fast Transient
(Burst) Immunity
Output: 2kV, 5kHz
Input: 1kV, 5kHz
Electrical Surge Immunity
Output, line to line, 1kV
Output, line to earth, 2kV
Input, line to line, 1kV
Input, line to earth, 2kV
EN60947-4-3
IEC/EN 61000-4-2
Performance Criteria 2
IEC/EN 61000-4-4
Performance Criteria 1
IEC/EN 61000-4-5
Radiated Radio Frequency
Immunity
10V/m, 80 - 1000 MHz
10V/m, 1.4 - 2.0GHz
3 V/m, 2.0 - 2.7GHz
Conducted Radio Frequency
Immunity
10V/m, 0.15 - 80 MHz
Voltage Dips Immunity
0% for 0.5, 1 cycle
40% for 10 cycles
70% for 25 cycles
80% for 250 cycles
Voltage Interruptions Immunity
0% for 5000ms
IEC/EN 61000-4-3
IEC/EN 61000-4-6
IEC/EN 61000-4-11
IEC/EN 61000-4-11
EMC Emission
Radio Interference
Voltage Emission (Conducted)
0.15 - 30MHz
EN60947-4-3
IEC/EN 55011
Class A (industrial) with filters
IEC/EN 60947-4-3
Class A (no filtering needed up
to 75AAC)
Radio Interference
Field Emission (Radiated)
30 - 1000MHz
IEC/EN 55011
Class B
Notes:
- Control input lines must be installed together to maintain products’ susceptibility to Radio Frequency interference.
- Performance Criteria 1: No degradation of performance or loss of function is allowed when the product is operated as intended.
- Performance Criteria 2: During the test, degradation of performance or partial loss of function is allowed. However, when the test is complete the product
should return operating as intended by itself.
- Performance Criteria 3: Temporary loss of function is allowed, provided the function can be restored by manual operation of the controls.
RM1A,RM1B
Thermal Specifications
RM1...25
Operating temperature range
Storage temperature range
Junction temperature
th
junction to case
Rth junction to ambient
-20° to 70°C
-40° to 100°C
≤ 125°C
≤ 0.80°C/W
≤ 20.0°C/W
RM1...50
-20° to 70°C
-40° to 100°C
≤ 125°C
≤ 0.50°C/W
≤ 20.0°C/W
RM1.60.50
-20° to 70°C
-40° to 100°C
≤ 125°C
≤ 0.72°C/W
≤ 20.0°C/W
RM1...75
-20° to 70°C
-40° to 100°C
≤ 125°C
≤ 0.35°C/W
≤ 20.0°C/W
RM1...100
-20° to 70°C
-40° to 100°C
≤ 125°C
≤ 0.30°C/W
≤ 20.0°C/W
Housing Specifications
Weight
25A, 50A
75A, 100A
Baseplate
25A, 50A
75A, 100A
Potting compound
Approx. 60g
Approx. 100g
Aluminium
Copper, nickel-plated
None
Relay
Mounting screws
Mounting torque
Control terminal
Mounting screws
Mounting torque
Power terminal
Mounting screws
Mounting torque
M5
1.5-2.0Nm
M3 x 9
0.5Nm
M5 x 9
2.4Nm
Connection Specifications
Connection terminals
L1, T1
A1, A2
Stripping length (X)
Connection Type
Rigid (solid & stranded)
UR rated data
Flexible with end sleeve
12 mm
M5 screw with captivated washer
8 mm
M3 screw with captivated washer
1x 2.5 - 6.0 mm²
1x 14 - 10 AWG
1x 1.0 - 4.0 mm²
1x 18 - 12 AWG
2x 2.5 - 6.0 mm²
2x 14 - 10 AWG
2x
2x
2x
2x
2x
2x
2x
2x
1.0 - 2.5 mm²
2.5 - 4.0 mm²
18 - 14 AWG
14 - 12 AWG
1.0 - 2.5 mm²
2.5 - 6.0 mm²
18 - 14 AWG
14 - 10 AWG
1x 0.5 - 2.5 mm²
1x 18 - 12 AWG
1x 0.5 - 2.5 mm²
1x 18 - 12 AWG
2x 0.5 - 2.5 mm²
2x 18 - 12 AWG
2x 0.5 - 2.5 mm²
2x 18 - 12 AWG
Flexible without end sleeve
1x 1.0 - 6.0 mm²
1x 18 - 10 AWG
Torque specification
Aperture for termination lug
Pozidrive 2
2.4 Nm (21.2 lb-in)
12 mm
Pozidrive 1
0.5 Nm (4.4 lb-in)
7.5 mm
RM1A, RM1B
Functional Diagram
Dimensions
A1
REGULATION
ZC
T1
ZC
IO
A2(~ )
L1
LED
APPLY
HEATSINK
COMPOUND
* Varistor across input applies to AC control versions only.
All dimensions in mm
Connection Diagram
L1
L2/N
LOAD
* Depends on system requirements
Control Input
Output Power Dissipation
RM..100
Power dissipation in W
RM..75
RM..50
RM.60..50
RM..25
90
95
Load current per pole in AACrms
电流互感器得到的电流失真
DL-CT1005A的电流互感器,得到的波形明显失真,这是因为什么呢?原理图、波形如下,功放LM3...
356416515 测试/测量
分享 LM3S2965-EVM开发版原理图和用户手册
TI Cortex-M3 LM3S2965-EVM开发板用户手册与原理图,供大家参考! 分享 ...
microli 微控制器 MCU
请问有大神用过下面的RF吗
433MHzRFTransceiver-v1.1 请问有大神用过下面的RF吗 ...
wang_gdut RF/无线
给单片机初学者的几点建议!
你有了学习单片机的愿望,接下来的问题就是从何学起,如何学? 对于在校学生有老师指导,开始时的迷茫会少...
zhaobqing163 单片机
求助:CCS3 .3编译错误:Don\'t know how to build file
初学DSP,在使用CCS3.3时,添加的头文件包含在Document里,怎么加到include里? ...
藤堂香澄 DSP 与 ARM 处理器
【2024 DigiKey 创意大赛】+总结
一、作品简介 本项目是利用自己设计一款功能强大的PCB扩展板,与现有的Espres...
meiyao DigiKey得捷技术专区