Switch Mode Power Supply
S8VS
(60/90/120/180/240/480-W Models)
Models with Indication Monitor and
Simple Functions for Easy System
Commissioning
• 60-W and 90-W models with indication monitor that
conform to UL Class 2 Output standards.
• Models with screwless terminal blocks
• Status displayed on 3-digit, 7-segment display.
• Safety standards:
UL 508/60950-1,
CSA C22.2 No. 107.1/60950-1
EN 50178 (= VDE 0160)
EN 60950-1 (= VDE 0805 Teil 1)
• Input conditions: DC input is also possible
from 80 to 370 VDC (Not compliant with
EC Directives and other safety standards.)
• Mount to DIN Rail.
• Complies with SEMI F47-0706 (200-VAC input).
• RoHS-compliant.
Refer to
Safety Precautions for All Power Su
Precautions
on page 29.
Refer to
Safety Precautions for All Power Supplies
and
Safety
Precautions
on page 29.
S8VS Switch Mode Power Supply
S8VS
Model Number Structure
Model Number Legend
S8VS-
Not all combinations are possible. Refer to
List of Models
in
Ordering Information,
below.
4. Alarm output
None: Sinking (Emitter COM)
P:
Sourcing (Collector COM)
No alarm output possible with 60-W models.
Both sinking and sourcing outputs are available for 480-W models.
5. UL Class 2 Output Standards (UL 1310)
None: Does not conform.
S:
Conforms.
60-W and 90-W models conform to Class 2 output standards
(UL 1310).
The S option is available only for 90-W models.
6. Terminal Block Form
None: Screw terminal block
F:
Screwless terminal block
1. Power Ratings
060: 60 W
090: 90 W
120: 120 W
180: 180 W
240: 240 W
480: 480 W
2. Output voltage
05: 5 V
12: 12 V
24: 24 V
3. Indication monitor
A:
B:
BE:
With indication monitor (maintenance forecast monitor)
With indication monitor (total run time monitor)
With indication monitor but without alarm output (total run
time monitor)
Estimates can be provided for coatings and other specifications that are not given in the datasheet. Ask your OMRON representative for details.
List of Models
For details on normal stock models, contact your nearest OMRON representative.
S8VS
Models with Indication Monitor (Maintenance Forecast Monitor)
Power ratings
60 W
Input voltage
Output
voltage
Output current
2.5 A
Alarm
output * 2
Sinking
90 W
100 to 240
VAC
(allowable
range: 85 to
264 VAC or 80
to 370 VDC
* 1)
3.75 A
Sinking
Sourcing
Sourcing
24 V
5A
7.5 A
10 A
100 to 240
VAC
20 A
Peak current 30 A
(200 VAC)
Sinking
Sourcing
Sinking
Sourcing
Sinking
Sourcing
Sinking/
sourcing
UL Class 2
Output standards
Yes
Yes
Yes
Model number
(screw terminal block)
S8VS-06024A
S8VS-09024A
S8VS-09024AS
S8VS-09024AP
S8VS-09024APS
S8VS-12024A
S8VS-12024AP
S8VS-18024A
S8VS-18024AP
S8VS-24024A
S8VS-24024AP
S8VS-48024A
Model number
(screwless terminal block)
S8VS-06024A-F
S8VS-09024A-F
S8VS-09024AS-F
S8VS-09024AP-F
S8VS-09024APS-F
S8VS-12024A-F
S8VS-12024AP-F
S8VS-18024A-F
S8VS-18024AP-F
S8VS-24024A-F
S8VS-24024AP-F
S8VS-48024A-F
120 W
180 W
240 W
480 W
*1.
The range for compliance with EC Directives and safety standards (UL, EN, etc.) is 100 to 240 VAC (85 to 264 VAC).
*2.
In the
Alarm output
column, “sinking” indicates an emitter COM and “sourcing” indicates a collector COM.
Models with Indication Monitor (Total Run Time Monitor)
Power ratings
60 W
Input voltage
Output
voltage
Output current
2.5 A
Alarm
output * 2
90 W
100 to 240
VAC
(allowable
range: 85 to
264 VAC or 80
to 370 VDC)
3.75 A
Sinking
Sinking
Sourcing
Sourcing
24 V
5A
Sinking
Sourcing
7.5 A
Sinking
Sourcing
240 W
100 to 240
VAC
10 A
20 A
Peak current 30 A
(200 VAC)
Sinking
Sourcing
480 W
Sinking/
sourcing
UL Class 2
Output standards
Yes
Yes
Yes
Yes
Model number
S8VS-06024B
S8VS-09024BE
S8VS-09024BES
S8VS-09024B
S8VS-09024BS
S8VS-09024BP
S8VS-09024BPS
S8VS-12024BE
S8VS-12024B
S8VS-12024BP
S8VS-18024BE
S8VS-18024B
S8VS-18024BP
S8VS-24024BE
S8VS-24024B
S8VS-24024BP
S8VS-48024B
Model number
S8VS-06024B-F
S8VS-09024BE-F
S8VS-09024BES-F
S8VS-09024B-F
S8VS-09024BS-F
S8VS-09024BP-F
S8VS-09024BPS-F
S8VS-12024BE-F
S8VS-12024B-F
S8VS-12024BP-F
S8VS-18024BE-F
S8VS-18024B-F
S8VS-18024BP-F
S8VS-24024BE-F
S8VS-24024B-F
S8VS-24024BP-F
S8VS-48024B-F
120 W
180 W
*1.
*2.
In the
Alarm output
Refer to pages 24 to 25 for the options that available.
Power ratings
Item
Efficiency
Current
Input
Power factor
With 100-VAC input
With 200-VAC input
Standard
84% typical
83% typical
Maintenance
forecast monitor
83% typical
85% typical
60 W
Total run time
monitor
Standard
83% typical
84% typical
Maintenance
forecast monitor
83% typical
85% typical
90 W
S8VS
Total run time
monitor
100 to 240 VAC (allowable range: 85 to 264 VAC or 80 to 370 VDC
11)
With 100-VAC input
With 200-VAC input
50/60 Hz (47 to 450 Hz)
1.7 A max., 1.3 A typical
1.0 A max., 0.68 A typical
Conforms to EN61000-3-2
0.5 mA max.
1.0 mA max.
17.5 A max., 14 A typical
35 A max., 28 A typical
−10%
to 15% (with V. ADJ) (The voltage cannot be adjusted for the S8VS-09024@@@S-@.)
70 mV max.
90 mV max.
250 mV max.
150 mV max.
0.5% max. (at 85- to 264-VAC input, 100% load)
1.5% max. (with rated input, 0 to 100% load)
0.05%/°C max.
620 ms typical
400 ms typical
34 ms typical
158 ms typical
Yes
No
No
No
No
No
No
No
No
No
No
Yes for up to 2 Power Supplies (with external diode)
Refer to the derating curve in . (with no icing or condensation)
−25
to 65°C
25% to 85% (Storage humidity: 25% to 90%)
3.0 kVAC for 1 min. (between all inputs and outputs/ alarm outputs; detection current: 20 mA)
2.0 kVAC for 1 min. (between all inputs and PE terminals; detection current: 20 mA)
1.0 kVAC for 1 min. (between all outputs/ alarm outputs and PE terminals; detection current for standard models: 30 mA, detection
current for models with indication monitor: 20 mA)
500 VAC for 1 min. (between all outputs and alarm outputs; detection current: 20 mA)
100 MΩ min. (between all outputs/ alarm outputs and all inputs/ PE terminals) at 500 VDC
10 to 55 Hz, 0.375-mm single amplitude for 2 h each in X, Y, and Z directions
10 to 150 Hz, 0.35-mm single amplitude (5 G max.) for 80 min each in X, Y, and Z directions
150 m/s
, 3 times each in ±X, ±Y, and ±Z directions
Yes (color: green)
Conducted
Emissions
Radiated
Emissions
Models with indication monitor: Conforms to EN61204-3 EN55011 Class A and based on FCC Class A, Conforms to EN61204-3
EN55011 Class B
Standard models: Conforms to EN61204-3 EN55011 Group 1 Class B and based on FCC Class A
Models with indication monitor: Conforms to EN61204-3 EN55011 Class A, Conforms to EN61204-3 EN55011 Class B
Conforms to EN61204-3 high severity levels
UL: UL 508 (Listing; Class 2 Output: Per UL1310), UL UR: UL
60950-1 (Recognition),
cUL: CSA C22.2 No.107.1 (Class 2 Output: Per CSA C22.2 No.
223),
cUR: CSA C22.2 No.60950-1,
EN/VDE: EN 50178 (= VDE 0160), EN 60950-1
(= VDE 0805 Teil 1)
KOSHA S Mark
F47-0706 (With 200-VAC input)
330 g max.
490 g max.
UL: UL 508 (Listing)
UL Listed (S8VS-09024@@@S-@ only.): UL 508 (Listing, Class 2
UL UR: UL 60950-1 (Recognition),
cUL: CSA C22.2 No.107.1,
cUL (S8VS-09024-@@@S-@ only): CSA C22.2 No.107.1 (Class 2
Output: Per CSA C22.2 No. 223),
KOSHA S Mark
Yes (selectable)
No
Yes (selectable)
Yes (transistor output), 30 VDC max., 50 mA max.
Yes (selectable)
No
Yes (selectable)
Yes (selectable)
Yes (selectable)
Yes (selectable)
No
No
No
No
No
Yes (selectable)
Yes (selectable)
Yes (selectable)
Yes (selectable)
No
No
Yes (selectable)
460 ms typical
290 ms typical
33 ms typical
154 ms typical
460 ms typical
300 ms typical
28 ms typical
132 ms typical
660 ms typical
420 ms typical
28 ms typical
136 ms typical
1.0 A max., 0.78 A typical
2.3 A max., 1.9 A typical
1.4 A max., 1.0 A typical
1.4 A max., 1.2 A typical
Harmonic current regulation
Leakage current
Inrush current
With 100-VAC input
With 200-VAC input
With 100-VAC input
With 200-VAC input
Voltage adjustment range
Input variation influence
Output
Ripple noise voltage (at rated I/O)
Load variation influence (rated input voltage)
Temperature variation influence
Startup time
(at rated I/O)
Output hold time
(at rated I/O)
With 100-VAC input
With 200-VAC input
With 100-VAC input
With 200-VAC input
Overload protection
Overvoltage protection
2,
Output voltage indication
Output current indication
105% to 160% of rated load current (101% to 110% of rated load current for the S8VS-09024@@@S-@), inverted L voltage drop, intermittent, automatic reset
Peak-hold current indication
Additional
functions
Maintenance forecast monitor indication
Maintenance forecast monitor output
Total run time monitor indication
Total run time monitor output
Undervoltage alarm indication
Undervoltage alarm output terminals
Parallel operation
Series operation
Operating ambient temperature
Storage temperature
Operating ambient humidity
Dielectric strength
Insulation resistance
Vibration resistance
Shock resistance
Output indicator
Other
EMI
EMS
Approved standards
SEMI
Weight
*1.
Do not use an inverter output for the Power Supply. Inverters with an output frequency of 50/60 Hz are available, but the rise in the internal temperature of the Power Supply may result in
ignition or burning.
*2.
For a cold start at 25°C. Refer to
Engineering Data
on page 18 for details.
*3.
If the output voltage adjuster (V. ADJ) is turned, the voltage will increase by more than +15% of the voltage adjustment range (by more than +10% for 240-W models with indication monitor).
When adjusting the output voltage, confirm the actual output voltage from the Power Supply and be sure that the load is not damaged.
*4.
To reset the protection, turn OFF the input power for three minutes or longer and then turn it back ON.
*5.
Displayed on 7-segment LED. (character height: 8 mm)
*6.
Resolution of output voltage indication: 0.1 V, Precision of output voltage indication:
±2%
(percentage of output voltage value,
±1
digit)
*7.
Resolution of output current indication: 0.1 A; Precision of output current indication:
±5%
F.S.
±1
digit max. (specified by rated output voltage)
*8.
Resolution of peak-hold current indication: 0.1 A; Precision of peak-hold current indication:
±5%
F.S.
±1
digit max. (specified by rated output voltage);
Signal width required for peak-hold current: 20 ms
*9.
A Type and B Type: Sinking, AP Type and BP Type: Sourcing, BE Type: No alarm output.
*10.
S8VS-06024A, S8VS-09024A/AP, S8VS-12024A/AP, S8VS-18024A/AP, and S8VS-24024A/AP only
*11.
Power ratings
Item
Efficiency
Current
Input
Power factor
Leakage current
Inrush current
With 100-VAC input
With 200-VAC input
With 100-VAC input
With 200-VAC input
With 100-VAC input
With 200-VAC input
With 100-VAC input
With 200-VAC input
Standard
84% typical
87% typical
120 W
Maintenance
forecast monitor
83% typical
85% typical
Total run time
monitor
Standard
85% typical
88% typical
180 W
Maintenance
forecast monitor
85% typical
87% typical
Total run time
monitor
S8VS
11)
50/60 Hz (47 to 63 Hz)
1.9 A max., 1.5 A typical
1.1 A max.,
0.71 A typical
0.9 min.
0.5 mA max.
1.0 mA max.
−10%
to 15% (with V.ADJ)
60 mV max.
130 mV max.
50 mV max.
180 mV max.
0.05%/°C max.
550 ms typical
400 ms typical
52 ms typical
54 ms typical
Yes
No
No
No
Yes (selectable)
Yes (selectable)
Yes (selectable)
Yes (selectable)
Yes (transistor
output), 30 VDC
max., 50 mA max.
No
No
Yes (selectable)
Yes (transistor
output), 30 VDC
max., 50 mA max.
Yes (selectable)
50 mA max.
No
No
No
No
No
No
No
No
No
Yes (selectable)
50 mA max.
Yes (selectable)
Yes (selectable)
Yes (selectable)
Yes (selectable)
Yes (transistor
output), 30 VDC
max., 50 mA max.
No
No
Yes (selectable)
Yes (transistor
output), 30 VDC
max., 50 mA max.
650 ms typical
520 ms typical
56 ms typical
56 ms typical
570 ms typical
470 ms typical
58 ms typical
62 ms typical
580 ms typical
490 ms typical
70 ms typical
70 ms typical
1.1 A max., 0.72 A typical
2.9 A max., 2.2 A typical
1.6 A max., 1.1 A typical
Output
Startup time
(at rated I/O)
Output hold time
(at rated I/O)
With 100-VAC input
With 200-VAC input
With 100-VAC input
With 200-VAC input
Overload protection
2,
105% to 160% of rated load current, inverted L voltage drop, automatic reset
No
Additional
functions
Parallel operation
Series operation
Storage temperature
Dielectric strength
Shock resistance
Other
Output indicator
Conducted
Emissions
Radiated Emissions
EMS
No
No
No
No
No
No
−25
to 65°C
150 m/s
Yes (color: green)
EN55011 Class B
UL Listed: UL 508 (Listing),
cUL: CSA C22.2 No. 107.1,
cUR: CSA C22.2 No. 60950-1,
EN/VDE: EN 50178 (= VDE 0160), EN 60950-1 (= VDE 0805 Teil 1)
KOSHA S Mark
550 g max.
850 g max.
EMI
Approved standards
SEMI
Refer to page 4 for notes 1 to 11.
Weight