首页 > 器件类别 > 热门应用 > 机电/工控/自动化
SCR9L
LED LAMP ALARM RELAY
器件类别:热门应用    机电/工控/自动化
厂商名称:Littelfuse
厂商官网:http://www.littelfuse.com
SCR9L 在线购买
供应商:
器件:SCR9L
价格:-
最低购买:-
库存:点击查看
点击购买
Flashers and Tower Lighting Controls
Tower and Obstruction Lighting Controls
SCR9L
Universal Lamp Alarm Relay
The SCR9L is a universal lamp alarm relay designed to sense the
failure of flashing or steady LED beacon lamps or obstruction
lamps. The SCR9L energizes when one or more lamps fail. It
will monitor the operation of one to eight beacon or obstruction
lamps. All monitored lamps must be the same wattage and
voltage. When connected to a site monitoring system, it
provides the remote lamp monitoring protection required by the
FAA-AC No: 150/5345-43E.
Operation
When a lamp fails, the SCR9L senses a decrease in current flow.
After a 10s trip delay, the onboard LED glows and the two alarm
outputs energize. The outputs and the LED are reset when the
failed lamps are replaced and the unit is recalibrated. The SCR9L
will sense an open flasher, it will not sense a continuously ON
flasher (see FB Series). Removing input voltage de-energizes the
output and the LED‘s. It does not change the calibration.
Wiring Diagram
BEACON LAMP CONNECTION DIAGRAM
L1
N/L2
Features & Benefits
Self calibrating
Failsafe beacon
monitoring
Number of lamps
monitored is switch
selectable up to 8
Universal voltage
120 to 230VAC
V = Voltage
B = Beacon Lamps
SS = Selector Switch
L = LED Indicator
F = Flasher
AXL = Auxiliary
Load/Alarm
OL = Obstruction Lamps
SI = Sensor Input
H = “3“ Spare AC Hot
Connection (2A max.)
BENEFITS
Designed for use with all types of LED beacon and
obstruction lamps
Relay will also provide an alarm signal on a failed
flasher (open)
User selection allows quick set up and easy
adaption to multiple applications
Designed for use in most applications
Provides remote beacon monitoring when
connected to a site monitoring system, as is
required by the FAA
Provides visual relay status of operation, alarm, trip
delay, and calibration
Protects against shock, vibration, and humidity
Isolated, 10A, SPDT
alarm output contacts
LED indication
Fully encapsulated
OBSTRUCTION LAMP
CONNECTION DIAGRAM
L1
N/L2
Accessories
C103PM (AL) DIN Rail
35 mm aluminum DIN rail available in a 36 in.
(91.4 cm) length.
P1023-20 DIN Rail Adapter
Allows module to be mounted on a 35 mm DIN
type rail with two #10 screws.
© 2016 Littelfuse Protection Relays & Controls
www.littelfuse.com/scr9L
Rev: 1-A-062316
SCR9L
Calibration
Alarm relays must be calibrated at initial installation and when
LED lamps are replaced. Due to LED lamp aging, recalibration is
recommended every 12 months.
1. Remove input voltage
2. Move calibration switch to off position
3. Re-apply input voltage
4. LED will flash red to indicate the unit is ready for calibration
5. Visually inspect structure’s lighting to make sure all lamps
and flashers (if used) are operating properly
6. Remove input voltage
7 Adjust lamp selector switches for the correct number of
lamps to be monitored (see adjustment diagram below)
8. Re-apply input voltage
9. LED should flash red
10. Move calibrate switch to ON position
11. The LED will alternate flashing red and green
12. LED will glow steady green within 30 secs.
Calibration is complete
Calibration Failed
If the LED double blinks red, calibration failed. Remove input
voltage and repeat steps 6-8.
Notes:
a. Monitoring a mixture of LED beacons and LED obstruction
lamps is not possible with the SCR9L.
b. This alarm relay is not designed to monitor
incandescent lamps.
c. Applying input voltage when the calibrate switch is in the
OFF position, erases the previous calibration settings. The
LED will flash Red. The output relays are OFF and the unit
will not sense lamp failures.
d. Only one temperature compensated LED beacon can
be monitored with this product. A combination of
temperature compensated and standard LED beacons
cannot be monitored.
Indicator Table
Green
Green Flashing
Red
Red/Green Flashing
Red Flashing
Input ON & Calibrated
Trip Delay
Lamp Failure
Calibrating
Not Calibrated
Sensors
Calibration Range
(total all Lamps)
Absolute Max Current
(total all Lamps)
Single Lamp Current
Time Delay
Trip Delay
Input
Input Voltage/Tolerance
AC Line Frequency
Output
Line Voltage Output (SPNO)
150mA - 8.0A
15A max. (may not calibrate above 8A)
150mA - 8.0A (total all lamps < 8.0A)
Factory fixed
≅10s
Adjustment Example
SCR9L
120 to 230VAC ±15%
50/60Hz
To operate a spare lamp or alarm
5A @ 240VAC or 30VDC resistive;
1/4 hp @ 125VAC; 1/2 hp @ 250VAC
Isolated Alarm Output (SPDT)
10A @ 240VAC or 30VDC resistive;
Auxilliary Input Voltage (H)
≤ 2A @ 230VAC
Mechanical
Mounting
One #10 (M5 x 0.8) screw
Dimensions
76.7 mm (3”);
51.3 mm (2.02”);
41.7 mm (1.64”)
Termination
IP20 screw terminals for up to 14 AWG
(2.45 mm
) wire or two 16 AWG
(1.3 mm
) wires
Protection
Circuitry
Encapsulated
Environmental
Operating / Storage
Temperature
-40° to 60°C / - 40° to 85°C
Weight
3.9 oz (111 g)
7.
OFF ON
Example Shown: SCR9L two lamps are ON during
normal operation.
Rev: 1-A-062316