首页 > 器件类别 > 电路保护 > 电路保护
W91-X112-50
W91-X112-50=M6/M7/M9/W6/W7
器件类别:电路保护    电路保护
厂商名称:TE Connectivity(泰科)
厂商官网:http://www.te.com
器件标准:
W91-X112-50 在线购买
供应商:
器件:W91-X112-50
价格:-
最低购买:-
库存:点击查看
点击购买
是否Rohs认证
符合
厂商名称
TE Connectivity(泰科)
unknown
Factory Lead Time
19 weeks
电路保护类型
MAGNETIC CIRCUIT BREAKER
Catalog 1308242
Issued 3-03 (PDF Rev. 03-10)
W6/W9
series
Magnetic Hydraulic
P&B Circuit Breakers
• Designed for the international market. UL Recognized (UL1077 and
UL1500), CSA Accepted and VDE approved.
• Ratings to 50 amps.
• Heavy duty #10-32 stud connections. (W9)
• Quick-connect or screw terminals. (W6)
• Optional 10 amp auxiliary switch.
• Several delay curve options.
• Choice of toggle or rocker actuator per pole or per unit (W6).
• Optional relay/remote trip pole available.
• Trip-free operation.
Typical Resistance and Impedance
Current
(Amps)
0.2
5.0
10.0
20.0
30.0
40.0
50.0
DC
Resistance
(Ohms)
90
1.2
0.28
0.04
0.013
0.004
0.0027
0.002
0.0015
50/60 Hz.
Impedance
(Ohms)
90
1.2
0.28
0.04
0.013
0.005
0.004
0.002
0.0015
Agency Approvals
UL:
Recognized as Supplementary Protector under UL 1077. Available
models meet Ignition Protection requirements in accordance with
UL1500. File E69543.
CSA:
Accepted as a Supplementary Protector. File LR15734.
VDE:
Approved to VDE 0642/EN 60 934 (Circuit Breakers for Equipment)
License No. 73782.
Tolerance: 0.1 - 4.99 ± 15%; 5 - 9.99 ± 20%; 10 - 15 ± 25%; 16 - 30 ± 50%.
Mechanical/Environmental Data
Operating Temperature:
-40°C to +85°C.
Humidity:
Meets requirements of Mil-STD-202 method 103.
Shock:
Tested per Mil-STD-202, method 213, test condition C
(100g @ 6 ms).
Vibration:Tested
per Mil-STD-202, method 201, 10-55 Hz., 0.06"
(1.52mm) total excursion in 2 planes.
Fungus And Moisture Resistance:
Special moisture resistant finish
applied to all ferrous parts.
Plastic parts are made of inherently
fungus resistant material.
Marking:
International “1” and “0” symbols are marked on the toggle for
both W6 and W9. W9 units have “ON” and “OFF” molded into
the area at the base of the toggle. On a special order basis,
graphics can be imprinted on the rockers of rocker actuated W6
units. VDE approved versions of rocker actuated W6 breakers
have their rockers imprinted with “1” and “0.”
Mounting:
Units are mounted with two #6-32 screws from the front of
the panel. Metric models for use with M3 x 0.5 screws are
available. To maintain published performance specifications,
units should not be mounted more than 90° from their normal
upright position.
Weight:
Approximately 2.5 ounces per pole.
Users should thoroughly review the technical data before selecting a product part
number. It is recommended that users also seek out the pertinent approvals files of
the agencies/laboratories and review them to confirm the product meets the
requirements for a given application.
Electrical Data
Auxiliary Switch:
See Auxiliary Switch Ratings Table 2 for details.
Calibration:
Breakers will hold 100% of rated current.
Breakers may trip between 101% and 124% of rated load
(134% for AC/DC units).
Breakers must trip at 125% of rated load and above (135%
for AC/DC units).
Dielectric Strength:
50/60 Hz., 1500V: DC, 1100V.
Insulation Resistance:
100 Megohms at 500VDC.
Endurance:
10,000 on/off cycles - 6000 at rated load, 4000 at no load.
Units tested at six cycles per minute, 1 second on and 9
seconds off at 25°C ambient.
Relay Trip Coil:
(Ratings applicable to all W6 models with this option)
24 to 277VAC, 150mA minimum available current;
6 to 48VDC, 300mA minimum available current.
Approvals and Ratings Table 1
W6 Series
Maximum
65
277
277
277/480
UL1077/CSA (All Circuit Functions)
(Hz)
DC
50/60
50/60
50/60
Phase
3Ø-Wye
Current
Rating
(Amps)
0.2 - 50
0.2 - 20
21 - 50
0.2 - 20
Interrupting
Capacity
(Amps)
2,000
5,000
2,500
5,000
W6 or W9 Series
Maximum
65
250
250
415/240
VDE (Circuit Function X)
Phase
Current
Rating
(Amps)
0.2-50
0.2-30
31-50
0.2-30
Interrupting
Capacity
(Amps)
2,000
5,000
2,000
5,000
(Hz)
DC
50/60
50/60
50/60
W9 Series
Maximum
65
277
277/480
(Hz)
DC
50/60
50/60
Phase
3Ø-Wye
Current
Rating
(Amps)
0.2 - 50
0.2 - 50
0.2 - 20
Interrupting
Capacity
(Amps)
2,000
5,000
5,000
W6 or W9 Series
Maximum
48
125/250
250
UL1500 (Circuit Function X)
Phase
3Ø-Wye
Current
Rating
(Amps)
0.2 - 50
0.2 - 50
0.2 - 50
Interrupting
Capacity
(Amps)
3,000
1,000
1,000
(Hz)
DC
50/60
50/60
UL/CSA
Switch
Number
50/60 Hz.
125
Current
(Amps)
Terminals
WxTxL
.093 x .020 x .250
(2.36 x .51 x 6.40)
Revised 03-10
www.tycoelectronics.com
Dimensions are in inches over
(millimeters) unless otherwise
specified.
Dimensions are shown for reference
purposes only. Specifications and
availability subject to change.
USA: 1-800-522-6752
Canada: 1-905-470-4425
Mexico: 01-800-733-8926
C. America: 52-55-1106-0803
South America: 55-11-2103-6000
Hong Kong: 852-2735-1628
Japan: 81-44-844-8013
UK: 44-8706-080208
Catalog 1308242
Time vs. Current Trip Curves For W6 Series and W9 Series
AC 50/60 Hz.
DC & 50/60 Hz.
400 Hz.
10,000
CURVE 0 INSTANTANEOUS
TRIP TIMES
OVERLOAD @ 50/60 Hz & DC @ 400 Hz.
125%
150%
200%
400%
600%
800%
100 ms max.
55 ms max.
30 ms max.
15 ms max.
12 ms max.
12 ms max.
May Trip
100 ms max.
30 ms max.
15 ms max.
12 ms max.
12 ms max.
10,000
CURVE 2 STANDARD DELAY 50/60 Hz.
OVERLOAD TRIP TIMES
(SEC.)
125%
200%
400%
600%
800%
1000%
10 - 150
2.2 - 20
.2 - 2
.03 - .75
.007 - .15
.005 - .04
10,000
CURVE 3 SHORT DELAY 50/60 Hz.
OVERLOAD TRIPTIMES
(SEC.)
125%
200%
400%
600%
800%
1000%
1 - 15
.15 - 1.5
.03 - .25
.007 - .15
.003 - .08
.003 - .04
TIME IN SECONDS
.01
TIME IN SECONDS
TIME IN SECONDS
.01
.01
.001
100 200 300 400 500 600 700 800 900 1000 1
125 150
LOAD CURRENT AS A PERCENT
OF BREAKER RATING
.001
100 1200
125 150
OF BREAKER RATING
.001
125 150
OF BREAKER RATING
10,000
MOTOR START / LONG DELAY
CURVE 10 HIGH INRUSH 50/60 Hz. AC
OVERLOAD TRIP TIMES
(SEC.)
125%
40 - 500
200%
9 - 100
400%
2 - 20
600%
.8 - 10
800%
.1 - 4.5
1000%
.009 - 2
10,000
CURVE 12 HIGH INRUSH 50/60 Hz.
OVERLOAD TRIP TIMES
(SEC.)
125%
200%
400%
600%
800%
1000%
10 - 150
3 - 25
.5 - 2.5
.15 - 1
.015 - .7
.009 - .35
10,000
CURVE 13 HIGH INRUSH 50/60 Hz.
OVERLOAD TRIP TIMES
(SEC.)
125%
200%
400%
600%
800%
1000%
.8 - 30
.15 - 2.5
.03 - .3
.02 - .15
.009 - .12
.009 - .09
TIME IN SECONDS
TIME IN SECONDS
TIME IN SECONDS
.01
.01
.01
.001
100 1200
125 150
OF BREAKER RATING
.001
100 1200
125 150
OF BREAKER RATING
.001
100 1200
125 150
OF BREAKER RATING
DC
10,000
CURVE 2 STANDARD DELAY DC
OVERLOAD TRIP TIMES
(SEC.)
125%
200%
400%
600%
800%
1000%
2 - 55
.60 - 8
.1 - 1.5
.02 - .5
.004 - .05
.004 - .025
10,000
CURVE 3 SHORT DELAY DC
OVERLOAD TRIP TIMES
(SEC.)
125%
200%
400%
600%
800%
1000%
.6 - 7
.16 - 1.5
.03 - .25
.01 - .13
.004 - .05
.003 - .015
10,000
CURVE 53 DC HIGH INRUSH
OVERLOAD TRIP TIMES
(SEC.)
125%
80 - 700
200%
15 - 150
400%
2 - 20
600%
.70 - 10
800%
.10 - 3
1000%
.01 - .1
.01
.01
TIME IN SECONDS
TIME IN SECONDS
TIME IN SECONDS
.01
.001
100 1200
125 150
OF BREAKER RATING
.001
125 150
OF BREAKER RATING
.001
125 150
OF BREAKER RATING
AC/DC
10,000
CURVE 34 DC, 50/60 Hz. STANDARD DELAY
OVERLOAD TRIP TIMES
(SEC.)
135%
200%
400%
600%
800%
1000%
1 - 90
.60 - 20
.095 - 2
.02 - .95
.002 - .45
.002 - .09
TIME IN SECONDS
.01
.001
100 1200
125 150
135
OF BREAKER RATING
For instantaneous curves for all voltages refer to Curve 0 Instantaneous under the AC 50/60 Hz. heading.
Pulse Tolerance Specifications
Pulse tolerance is defined as a single pulse of a half sine
wave (1/2 cycle or 8 milliseconds) that will not trip the
breaker. An inertia wheel for increased pulse tolerance is
available by specifying “P” after the time delay curve
number in the ordering information. The table at right lists
pulse tolerance values of standard and inertia delay models.
Time
Delay
Curve
Pulse Tolerance Value
Standard
7.5
Inertia
Delay
AC
50/60 Hz.
To determine pulse tolerance multiply breaker rating by value in table. For
example, a 2A breaker with time delay curve 3 has a standard pulse tolerance
of 12A (2A x 6). The same breaker with an inertia delay has a pulse tolerance
of 36A (2A x 18).
Revised 03-10
specified.
USA: 1-800-522-6752
UK: 44-8706-080208
Catalog 1308242
Ordering Information
W6 Series
Typical Part No.
1. Circuit Breaker Mounting:
W = #6-32 mounting threads.
M = M3.0 x 0.5 mounting threads.
2. Number of Poles:
67 = Single pole
W 67- X
68 = Two pole
69 = Three pole
70 = Four pole
3. Circuit Function: (Only X is VDE approved)
A = Series trip with auxiliary switch (.093” QC)
X = Series trip
D = Series trip with auxiliary relay trip pole (requires extra pole package, 3 pole (4 pole package) max., must
specify #10-32 screw terminals below, but relay trip pole will be equipped with .250” QC term. only, not UL),
relay trip pole will be on the right side of the breaker when viewed from the front.
4. Actuator:
One actuator per pole
1 = Black toggle
3 = Black rocker
4 = White rocker
2 = White toggle
One actuator per unit
8 = White toggle
7 = Black toggle
5 = Red rocker
6 = Grey rocker
9 = Red toggle
J = Black rocker
5. Termination:
Q = .250” QC (DIN 46 244) [30A Max. UL/CSA; 25A Max. VDE]
S = #8-32 screw [30A Max.]
T = #10-32 screw [50A Max.]
U = #8-32 screw, nickel plated, bent inward 30° [30A Max.]
V = #10-32 screw, nickel plated, bent inward 30° [50A Max.]
Notes:
#10-32 termination must be used for
all
ratings of greater than 30 amps.
#10-32 termination must be specified for circuit function D, but relay trip pole will be equipped with .250” QC.
6. Maximum Line Voltage: (See Table 1 for current ranges)
UL/CSA
1 = 277VAC, 50/60 Hz.
TYPES
2 = 277/480VAC, 50/60 Hz. [20A Max.] (Requires insulating barriers, see outline dimension drawing)
5 = 65VDC
7 = AC/DC 277VAC, 50/60 Hz. or 65VDC
(Time delay curve 34 must be specified.)
8 = AC/DC 120VAC, 120/240VAC, 48VDC
(Agency Approval M [UL1500] and time delay curve 34 must be specified.)
VDE
TYPES
1 = 250VAC, 415/240VAC
5 = 65VDC
7 = AC/DC 250VAC, 415/240VAC, 65VDC
7. Time Delay Curve:
0 = Instantaneous
2 = Standard delay
3 = Short delay
53 = DC high inrush
10 = AC high inrush motor start / long delay
12 = AC high inrush version of #2
13 = AC high inrush version of #3
34 = Combination AC/DC standard delay
Notes:
Curves may be specified with increased pulse tolerance for 1/2 cycle by adding "P" after curve.
See delay curve section for availability and details.
8. Amp Rating:
0.20
0.50
0.25
0.75
3.0
3.5
4.0
5.0
6.0
7.0
7.5
8.0
9.0
10.0
11.0
12.0
15.0
20.0
25.0
30.0
35.0
40.0
45.0
50.0
Consult factory for
other values.
9. Agency Approval:
Blank = UL1077/CSA breaker
V = VDE approved breaker without auxiliary switch
M = UL1077/UL1500 ignition protected breaker
Authorized distributors are more likely to stock the following items.
W67-A2Q12-5
W67-A2Q12-10
W67-X2Q10-3
W67-X2Q10-5
W67-X2Q12-2
W67-X2Q12-3
W67-X2Q12-5
W67-X2Q12-7
W67-X2Q12-10
W67-X2Q12-15
W67-X2Q12-20
W67-X2Q12-30
W67-X2Q13-1
W67-X2Q13-2
W67-X2Q13-3
W67-X2Q13-10
W67-X2Q13-15
W67-X2Q13-20
W67-X2Q13-25
W67-X2Q13-30
W67-X2Q50-5
W67-X2Q50-10
W67-X2Q52-5
W67-X2Q52-10
W67-X2Q52-15
W67-X2Q52-20
W67-X2Q52-30
W67-X2Q110-15
W67-X2Q110-20
W68-X2Q12-3
W68-X2Q12-5
W68-X2Q12-7
W68-X2Q12-10
W68-X2Q12-15
W68-X2Q12-20
W68-X2Q12-25
W68-X2Q12-30
W68-X2Q13-15
W68-X2Q110-10
W68-X2Q110-20
W69-X2Q12-5
W69-X2Q12-10
W69-X2Q12-15
W69-X2Q12-20
W69-X2Q12-25
W69-X2Q12-30
W69-X2Q110-20
W69-X2Q110-30
Revised 03-10
specified.
USA: 1-800-522-6752
UK: 44-8706-080208
Catalog 1308242
W9 Series
2. Number of Poles:
91 = Single pole
Typical Part No.
91- X
92 = Two pole
93 = Three pole
94 = Four pole
X = Series trip
D = Series trip with auxiliary relay trip pole (requires extra pole package, 3 pole max., not UL)
4. Actuator:
One actuator per pole:
1 = Black toggle
2 = White toggle
5. Maximum Line Voltage: (See Table 1 for current ranges)
UL/CSA
TYPES
5 = 65VDC
VDE
TYPES
5 = 65VDC
6. Time Delay Curve:
0 = Instantaneous
2 = Standard delay
3 = Short delay
53 = DC high inrush
Notes:
7. Amp Rating:
0.20
0.75
0.25
3.0
3.5
4.0
5.0
6.0
7.0
7.5
8.0
9.0
10.0
11.0
12.0
15.0
20.0
25.0
30.0
35.0
40.0
45.0
50.0
Consult factory for other values
8. Agency Approval:
Blank = UL1077/CSA approved breaker
W91-X112-1
W91-X112-2
W91-X112-3
W91-X112-5
W91-X112-7
W91-X112-10
W91-X112-15
W91-X112-20
W91-X112-40
W91-X112-50
W91-X113-5
W91-X113-10
W91-X113-15
W91-X150-5
W91-X152-10
W91-X152-15
W91-X152-20
W91-X152-30
W91-X152-40
W91-X152-50
W91-X1110-20
W92-X112-1
W92-X112-2
W92-X112-3
W92-X112-5
W92-X112-7
W92-X112-10
W92-X112-15
W92-X112-20
W92-X112-25
W92-X112-30
W92-X112-40
W92-X112-50
W92-X113-15
W92-X113-20
W92-X1110-20
W92-X1110-30
W93-X112-5
W93-X112-10
W93-X112-15
W93-X112-20
W93-X112-25
W93-X112-30
W93-X112-40
W93-X112-50
W93-X1110-20
W93-X1110-30
Revised 03-10
specified.
USA: 1-800-522-6752
UK: 44-8706-080208
Catalog 1308242
Outline Dimensions - Toggle Actuator Models
W6 Series
.235
(5.97)
2.043
(51.89)
1.640
(41.66)
.66
(16.8)
.245
(6.22)
ON
LINE
Panel Mounting Cutout
Ø .625 +.010
-.000
15.88 +0.25
-0.00
1 PER POLE
.750
(19.05)
1.660
(42.16)
29°
1.520
(38.61)
30°
OFF
1.048
(26.62)
LOAD
Ø .156 [2 PLACES PER POLE]
(3.96)
W6 Series – One Actuator Per Pole
1 Pole
Ø .590
(15.00)
.750
(19.05)
2 Pole
1.500
(38.10)
3 Pole
2.250
(57
.15)
4 Pole
3.000
(76.20)
2.000
(50.80)
1.22
(31.00)
1.660
(42.16)
1.05
(26.67)
6.32 TH'D. .14 (3.56) DP TYP
M3 X 0.5 OPTIONAL
Multi-pole models furnished with separate handle tie hardware.
W6 Series – One Actuator Per Unit
1 Pole
Ø .590
(15.00)
.750
(19.05)
2 Pole
1.500
(38.10)
3 Pole
2.250
(57
.15)
4 Pole
3.000
(76.20)
2.000
(50.80)
1.22
(31.00)
(42.16)
1.05
(26.67)
M3 X 0.5 OPTIONAL
4-pole models furnished with separate
480V Model with Barriers
2.250
(57.15)
.269
(6.83)
2.778
(70.56)
Model with Aux. Relay Trip Pole
2.530
(64.26)
W68 -D model shown. Note that the
auxiliary relay trip pole is on the right.
#10-32 screw terminals must be
specified with this option; however,
the terminals on the relay trip pole
are 0.250” quick connects.
The relay pole is self-opening, so the
trip current can remain energized
indefinitely.
3-pole model shown.
.266
(6.76)
Termination Options
Notes:
1. Terminal protrusion dimensions are
referenced from back of mounting panel.
2. Main terminals are male quick connect
type .250 (6.35) wide x .031 (.79) thick x
.377 (9.58) long. Optional 8-32 x .250
(6.35) or 10-32 x .250 (6.35) screw type.
3. Panel mounting cutout detail mtg. detail
tol.: ± .005 (.13) unless noted. Add
additional cutouts to correspond to
number of poles. Outline drawing
tolerance ± .015 (.38) unless noted.
UL/CSA Models
W/Screw Terminals
.235
(5.97)
LINE
UL/CSA Models
W/Terminals Bent 30°
VDE Models
W/Screw Terminals
UL/CSA/VDE Models
W/Aux. Switch
2.380
(60.45)
2.032
(51.61)
LINE
LINE
LINE
(26.97) .827
(21.00)
.416
(10.56) C
NO
NC
1.520
(38.61)
LOAD
LOAD
LOAD
LOAD
Revised 03-10
specified.
USA: 1-800-522-6752
UK: 44-8706-080208
