首页 > 器件类别 >
ADAM-5018SK
8-ch Ultra High Speed Analog Input Module
厂商名称:Advantech
厂商官网:http://www.advantech.com/
ADAM-5017UH
ADAM-5018
ADAM-5018P
Module
7-ch Thermocouple Input Module
with Independent Input Range
ADAM-5017UH
2002/95/EC
COMPLIANT
ADAM-5018
2002/95/EC
COMPLIANT
ADAM-5018P
2002/95/EC
COMPLIANT
General
ƒ
Certification
ƒ
Connectors
CE
1 x Plug-in screw terminal
(# 14 ~ 22 AWG)
ƒ
Enclosure
ABS+PC
ƒ
Power Consumption
2.2 W (max.)
General
ƒ
Certification
ƒ
Connectors
CE, FM
(# 14 ~ 22 AWG)
ƒ
Enclosure
ABS+PC
ƒ
Power Consumption
0.63 W (max.)
General
ƒ
Certification
ƒ
Connectors
CE, FCC class A
(# 14 ~ 22 AWG)
ƒ
Enclosure
ABS+PC
ƒ
Power Consumption
0.63 W (max.)
Analog Input
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
Accuracy
±0.1% or better
Bandwidth
200 kHz
Channels
8 differential
Differential Non-linear ±1 LSB
Input Impedance
Voltage: 2 MΩ
Current: 120
(Build-in)
Integral Non-linear
±1 LSB
Input Range
±10 V, +0 ~ 10 V,
0 ~ 20 mA, +4 ~ 20 mA
Low pass filter
Configured by User
Resolution
12-bit
Sampling Rate
Depends on base unit
ADAM-5000/485 & 5000E:
100 Samples/sec max (Total): one ADAM-5017UH
installed
ADAM-5000/TCP & 5000L/TCP:
100 Samples/sec max (Total) :one ADAM-5017UH
installed
ADAM-5510 :
200K Samples/sec max (Single Channel): one ADAM-
5017UH installed
ADAM-5550 & ADAM-5560:
1K Samples/sec max(single channel): one ADAM-
5017UH installed
*Depending on the performance of client server or
controller
Signal Input
200 kHz for both voltage
Bandwidth
and current inputs
Thermocouple Input
ƒ
Accuracy
Voltage mode: ±0.1% or
better
Current mode: ±0.2% or
better
Bandwidth
13.1 Hz @ 50 Hz
15.72 Hz @ 60 Hz
Channels
7 (differential, each channel
can be configured with
different range)
CMR @ 50/60 Hz
92 dB min
Input Impedance
20 MΩ. (Build-in 120
Register for Current Input)
lnput Range and Types
Thermocouple
760°C
1,370°C
400°C
1,000°C
1,750°C
1,750°C
1,800°C
Current
±20 mA, 4 ~ 20 mA
±15 mV (0.2%), ±50 mV,
±100 mV, ±500 mV
±1 V, ±2.5 V
Resolution
16-bit
Sampling Rate
10 samples/sec. (total)
Span Drift
±25 PPM/°C
Zero Drift
±6 μV/°C
High Common Mode
200 V
DC
Thermocouple Input
ƒ
Accuracy
ƒ
Bandwidth
ƒ
ƒ
ƒ
ƒ
±0.1% or better
13.1 Hz @ 50 Hz
15.72 Hz @ 60 Hz
Channels
7 differential
CMR @ 50/60 Hz
92 dB min
Input Impedance
2 MΩ
lnput Range
±15 mV, ±50 mV, ±100 mV,
±500 mV,
±1 V, ±2.5 V, ±20 mA
lnput Type
mV, V, mA, thermocouple
Resolution
16-bit
Sampling Rate
Span Drift
±25 PPM/ °C
Zero Drift
±6 μV/ °C
T/C Type and Temperature Range
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
ƒ
Protection
ƒ
Isolation Voltage
3,000 V
DC
1) The voltage difference between any two pins must not
exceed 15 V
2) Distinct range settings allowed on each channel
Note: Not support ADAM-5510KW series
Protection
ƒ
Fault and
Overvoltage
Protection
ƒ
Isolation Voltage
Withstands overvoltage up
to ±35 V
3,000 V
DC
ƒ
ƒ
ƒ
ƒ
ƒ
Protection
ƒ
Fault and
Overvoltage
to ±35 V
Protection
ƒ
Isolation Voltage
3,000 V
DC
ƒ
Filter function
Yes
ƒ
Built-in TVS/ESD Protection
Ordering Information
ƒ
ADAM-5017UH
Analog Input Module
ƒ
ADAM-5018
ƒ
ADAM-5018SK
Module
ADAM-5018 with CJC kit/
external
ƒ
ADAM-5018P
7-ch Thermo. Input Module
w/ Ind. Input Range
Programmable Automation Controllers
All product specifications are subject to change without notice
Last updated : 28-Aug-2013
参数对比
与ADAM-5018SK相近的元器件有:ADAM-5017_14。描述及对比如下:
型号 ADAM-5018SK ADAM-5017_14
描述 8-ch Ultra High Speed Analog Input Module 8-ch Ultra High Speed Analog Input Module
