首页 > 器件类别 > 电路保护
LFCL0250ZC1
Specialty Fuses 600 Volts AC Cable Limiters
器件类别:电路保护
厂商名称:Littelfuse
厂商官网:http://www.littelfuse.com
下载文档
LFCL0250ZC1 在线购买
供应商:
器件:LFCL0250ZC1
价格:-
最低购买:-
库存:点击查看
点击购买
器件参数
参数名称
属性值
产品种类
Product Category
Specialty Fuses
制造商
Manufacturer
Littelfuse
RoHS
No
产品
Product
Cable Limiters
电压额定值 AC
Voltage Rating AC
600 VAC
安装风格
Mounting Style
Cable
端接类型
Termination Style
Cable to Cable
Fuse Type
Time Delay / Slow Blow
Indicator Style
Without Indicator
系列
Packaging
Bulk
Interrupt Rating
200 kA at 600 VAC
工厂包装数量
Factory Pack Quantity
类型
Cable Limiter
文档预览
Special Purpose Fuses
Cable Limiters
600 Volts AC
Cable limiters are fusible devices that provide very fast short-circuit
protection, primarily to faulted cables, but also to other conductors such
as busway. Cable limiters do not have an ampere rating, and cannot be
used to provide overload protection. They are instead selected by cable
size; for example, a 500 kcmil cable requires a 500 kcmil cable limiter.
Their main use is to isolate faulted cables in circuits containing three or
more parallel conductors per phase. They may be installed on the line
side of the main service to provide short-circuit protection to the service
conductors. This is especially important when service conductors are
tapped from large low voltage networks or from large low impedance
transformers.
Cable limiters have terminals which permit them to be installed in a
variety of equipment. The most common configuration is the offset
blade on one end and the crimp terminal on the other end. This permits
the limiter to replace a cable terminal (lug).
Service entrance conductors
Between transformer or network bus and busway terminal boxes
Large feeders with three or more conductors per phase
• Current-limiting characteristics provide protection to conductor
insulation and reduce damage when faults occur.
• Properly applied cable limiters may permit the use of equipment with
reduced withstand ratings
• Wide variety of terminations and cable ratings permit use in almost
every situation.
Termination
Cable Size
4/0
250MCM
350MCM
500MCM
750MCM
4/0
250MCM
350MCM
500MCM
750MCM
4/0
250MCM
350MCM
500MCM
750MCM
4/0
250MCM
350MCM
500MCM
750MCM
4/0
250MCM
350MCM
500MCM
750MCM
Catalog Number
Cable Type
Copper
Aluminum
LFCL4/0C1
LFCL4/0A1
LFCL250C1
LFCL250A1
LFCL350C1
LFCL350A1
LFCL500C1
LFCL500A1
LFCL750C1
LFCL750A1
LFCL4/0C3
LFCL4/0A3
LFCL250C3
LFCL250A3
LFCL350C3
LFCL350A3
LFCL500C3
LFCL500A3
LFCL750C3
LFCL750A3
LFCL4/0C5
LFCL250C5
LFCL350C5
LFCL500C5
LFCL750C5
LFCL4/0C6
LFCL4/0A6
LFCL250C6
LFCL250A6
LFCL350C6
LFCL350A6
LFCL500C6
LFCL500A6
LFCL750C6
LFCL750A6
LFCL4/0C8
LFCL250C8
LFCL350C8
LFCL500C8
LFCL750C8
Specifications
Voltage Rating:
Interrupting Rating:
Cable Size Range:
600 volts AC
200,000 Amperes
4 ⁄0
– 750MCM Copper or Aluminum
Cable to Cable
Cable to Offset
Bus
Note: For Type 5 and Type 8 Aluminum cable limiters, use the Copper Type C5
and C8.
Ordering Information
LFCL - 500 - C - 1
Littelfuse
Cable Limiter
Conductor Size
Terminal Material
(Aluminum or Copper)
Straight Bus to
Offset Bus
Mole to Cable
Mole to Offset
Bus
Type of
Termination
108
www.littelfuse.com
© 2005 Littelfuse
POWR-GARD
Products Catalog
查看更多>
参数对比
与LFCL0250ZC1相近的元器件有:LFCL04-0ZC8、LFCL0750ZC6、LFCL04-0ZA6、LFCL0750ZA3、LFCL0500ZC3、LFCL0750ZC3、LFCL0500ZC1、LFCL0250ZC8。描述及对比如下:
型号 LFCL0250ZC1 LFCL04-0ZC8 LFCL0750ZC6 LFCL04-0ZA6 LFCL0750ZA3 LFCL0500ZC3 LFCL0750ZC3 LFCL0500ZC1 LFCL0250ZC8
描述 Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters Specialty Fuses 600 Volts AC Cable Limiters
产品种类
Product Category
Specialty Fuses Specialty Fuses Specialty Fuses Specialty Fuses Specialty Fuses Specialty Fuses Specialty Fuses Specialty Fuses Specialty Fuses
制造商
Manufacturer
Littelfuse Littelfuse Littelfuse Littelfuse Littelfuse Littelfuse Littelfuse Littelfuse Littelfuse
RoHS No No No No No No No No No
产品
Product
Cable Limiters Cable Limiters Cable Limiters Cable Limiters Cable Limiters Cable Limiters Cable Limiters Cable Limiters Cable Limiters
电压额定值 AC
Voltage Rating AC
600 VAC 600 VAC 600 VAC 600 VAC 600 VAC 600 VAC 600 VAC 600 VAC 600 VAC
安装风格
Mounting Style
Cable Cable Cable Cable Cable Cable Cable Cable Cable
端接类型
Termination Style
Cable to Cable Mole to Bolt Down Mole to Cable Mole to Cable Cable to Bolt Down Cable to Bolt Down Cable to Bolt Down Cable to Cable Mole to Bolt Down
Fuse Type Time Delay / Slow Blow Time Delay / Slow Blow Time Delay / Slow Blow Time Delay / Slow Blow Time Delay / Slow Blow Time Delay / Slow Blow Time Delay / Slow Blow Time Delay / Slow Blow Time Delay / Slow Blow
Indicator Style Without Indicator Without Indicator Without Indicator Without Indicator Without Indicator Without Indicator Without Indicator Without Indicator Without Indicator
系列
Packaging
Bulk Bulk Bulk Bulk Bulk Bulk Bulk Bulk Bulk
Interrupt Rating 200 kA at 600 VAC 200 kA at 600 VAC 200 kA at 600 VAC 200 kA at 600 VAC 200 kA at 600 VAC 200 kA at 600 VAC 200 kA at 600 VAC 200 kA at 600 VAC 200 kA at 600 VAC
工厂包装数量
1 1 1 1 1 1 1 1 1
类型
Cable Limiter Cable Limiter Cable Limiter Cable Limiter Cable Limiter Cable Limiter Cable Limiter Cable Limiter Cable Limiter
JLINK V8 新版中文用户手册(免芯币下载)
最新版本,内含JLINK在各主流开发环境中的应用指导! JLINK V8 新版中文用户手册(免芯币...
weor001 嵌入式系统
OSMutexPend
低优先级任务占用互斥信号量,高优先级调用OSMutexPend,设置超时时间。当超时时间到了,高优...
cspwj 嵌入式系统
创意!谁说烤红薯的没文化?
谁说烤红薯的没文化? 创意!谁说烤红薯的没文化? 微信上看到一个比这还牛的。 居然没把二维码画...
qwqwqw2088 创意市集
TI miniDSP Codec 初始化方法及示例代码
Texas instruments 推出的超低功耗miniDSP 音频Codec 集成了miniDS...
德仪DSP新天地 DSP 与 ARM 处理器
盘点晶体振荡器实际应用优势
当下很多设备上都离不开振荡器的使用,而其中晶体振荡器的应用更为常见。在采购振荡器的时候自然要根据...
YXC扬兴晶振 分立器件
【Follow me第二季第2期】+项目总结
文章中各任务均由图片中物料实现 物料清单: 厂商 厂商料号 ...
superw DigiKey得捷技术专区
热门器件
热门资源推荐
器件捷径:
S0 S1 S2 S3 S4 S5 S6 S7 S8 S9 SA SB SC SD SE SF SG SH SI SJ SK SL SM SN SO SP SQ SR SS ST SU SV SW SX SY SZ T0 T1 T2 T3 T4 T5 T6 T7 T8 T9 TA TB TC TD TE TF TG TH TI TJ TK TL TM TN TO TP TQ TR TS TT TU TV TW TX TY TZ U0 U1 U2 U3 U4 U6 U7 U8 UA UB UC UD UE UF UG UH UI UJ UK UL UM UN UP UQ UR US UT UU UV UW UX UZ V0 V1 V2 V3 V4 V5 V6 V7 V8 V9 VA VB VC VD VE VF VG VH VI VJ VK VL VM VN VO VP VQ VR VS VT VU VV VW VX VY VZ W0 W1 W2 W3 W4 W5 W6 W7 W8 W9 WA WB WC WD WE WF WG WH WI WJ WK WL WM WN WO WP WR WS WT WU WV WW WY X0 X1 X2 X3 X4 X5 X7 X8 X9 XA XB XC XD XE XF XG XH XK XL XM XN XO XP XQ XR XS XT XU XV XW XX XY XZ Y0 Y1 Y2 Y4 Y5 Y6 Y9 YA YB YC YD YE YF YG YH YK YL YM YN YP YQ YR YS YT YX Z0 Z1 Z2 Z3 Z4 Z5 Z6 Z8 ZA ZB ZC ZD ZE ZF ZG ZH ZJ ZL ZM ZN ZP ZR ZS ZT ZU ZV ZW ZX ZY
需要登录后才可以下载。
登录取消