首页 > 器件类别 > 电源/电源管理 > 电源电路
LSM-1.8/10-D12
DC-DC Regulated Power Supply Module, 1 Output, Hybrid, SMT-6
器件类别:电源/电源管理    电源电路
厂商名称:C&D
是否无铅
含铅
是否Rohs认证
不符合
厂商名称
C&D
零件包装代码
MODULE
包装说明
针数
unknow
ECCN代码
EAR99
模拟集成电路 - 其他类型
DC-DC REGULATED POWER SUPPLY MODULE
最大输入电压
13.2 V
最小输入电压
10.8 V
标称输入电压
12 V
JESD-30 代码
R-XDMA-X6
JESD-609代码
e4
最大负载调整率
0.25%
功能数量
输出次数
端子数量
60 °C
-40 °C
最大输出电压
1.98 V
最小输出电压
1.62 V
标称输出电压
1.8 V
封装主体材料
UNSPECIFIED
封装形状
RECTANGULAR
封装形式
MICROELECTRONIC ASSEMBLY
峰值回流温度(摄氏度)
NOT SPECIFIED
认证状态
Not Qualified
表面贴装
NO
技术
HYBRID
温度等级
OTHER
端子面层
GOLD
端子形式
UNSPECIFIED
端子位置
DUAL
处于峰值回流温度下的最长时间
NOT SPECIFIED
微调/可调输出
YES
INNOVATION and EXCELLENCE
Single Output
LSM-10A D12 Models
Non-Isolated, 12V
IN
, 0.8-5V
OUT
10 Amp DC/DC’s in SMT Packages
Step-down buck regulators for new
distributed 12V power architectures
12V input (10.8-13.2V range)
0.8/1/1.2/1.5/1.8/2/2.5/3.3/5V
OUT
@10A
Non-isolated, fixed-frequency,
synchronous-rectifier topology
Tape and reel SMT package
±1.25% setpoint accuracy
Efficiencies to 96% @ 10 Amps
Noise as low as 50mVp-p
Stable no-load operation
Remote on/off control
Sense pin and output voltage trim
No derating to +65°C with 100 lfm
UL/IEC/EN60950 certified
EMC compliant
LSM Series D12 SMT's (surface-mount packages) are ideal building blocks for
emerging, on-board power-distribution schemes in which isolated 12V buses deliver
power to any number of non-isolated, step-down buck regulators. LSM D12 DC/DC's
accept a 12V input (10.8V to 13.2V input range) and convert it, with the highest
efficiency in the smallest space, to a 0.8, 1, 1.2, 1.5, 1.8, 2, 2.5, 3.3 or 5 Volt output
fully rated at 10 Amps.
LSM D12's are ideal point-of-use/load power processors. They typically require
no external components. Their surface-mount packages occupy a mere 1.3" x 0.53"
(33.0 x 13.5mm), and are only 0.34 inches (8.6mm) high.
The LSM's best-in-class power density is achieved with a fully synchronous,
fixed-frequency, buck topology that also delivers: high efficiency (96% for 5V
OUT
models), low noise (50mVp-p typ.), tight line/load regulation (±0.1%/±0.25% max.),
quick step response (100µsec), stable no-load operation, and no output reverse
conduction.
The fully functional LSM’s feature output overcurrent detection, continuous
short-circuit protection, over-temperature protection, a remote on/off control pin
(pull low to disable), an output-voltage trim function, and a sense pin. High
efficiency enables the LSM D12's to deliver rated output currents of 10 Amps at
ambient temperatures to +65°C with 100 lfm air flow.
If your new system boards call for three or more supply voltages, check out the
economics of on-board 12V distributed power. If you don't need to pay for multiple
isolation barriers, DATEL's non-isolated LSM D12 SMT's will save you money.
+INPUT
(2)
+OUTPUT
(4)
+SENSE
(6)
COMMON
(3)
CURRENT
SENSE
ON/OFF
CONTROL
CC
PWM
CONTROLLER
COMMON
(3)
REFERENCE &
ERROR AMP
OUT
TRIM
(5)
Figure 1. Simplified Schematic
DATEL, Inc., Mansfield, MA 02048 (USA) · Tel: (508)339-3000, (800)233-2765 Fax: (508)339-6356 · Email: sales@datel.com · Internet: www.datel.com
LSM-10A D12 Series
N O N - I S O L AT E D , 1 0 - 5 0 W S M T D C / D C C O N V E R T E R S
Performance Specifications and Ordering Guide
Output
Model
LSM-0.8/10-D12
LSM-1/10-D12
LSM-1.2/10-D12
LSM-1.5/10-D12
LSM-1.8/10-D12
LSM-2/10-D12
LSM-2.5/10-D12
LSM-3.3/10-D12
LSM-5/10-D12
Input
Efficiency
Full Load
½ Load
Min.
80.5%
83%
85%
86.5%
88%
89%
90%
92%
93.5%
OUT
(Volts)
0.8
OUT
(Amps)
R/N (mVp-p)
Typ.
45
75
75
75
75
75
75
Regulation (Max.)
Line
Load
±0.1%
±0.1%
±0.1%
±0.1%
±0.1%
±0.1%
±0.1%
±0.1%
±0.1%
±0.375%
±0.25%
±0.25%
±0.25%
±0.25%
±0.25%
±0.25%
±0.25%
±0.25%
IN
Nom.
(Volts)
Range
(Volts)
10.8-13.2
10.8-13.2
10.8-13.2
10.8-13.2
10.8-13.2
10.8-13.2
10.8-13.2
10.8-13.2
10.8-13.2
IN
(mA/A)
30/0.84
35/1.02
40/1.19
50/1.47
55/1.75
55/1.9
60/2.3
70/3
85/4.5
Typ.
82.5%
85%
87%
88.5%
90%
91%
92.5%
94%
96%
Typ.
85%
86%
88%
89.5%
90.5%
91.5%
92%
93.5%
95.5%
Package
(Case,
Pinout)
C45, P63
C45, P63
C45, P63
C45, P63
C45, P63
C45, P63
C45, P63
C45, P63
C45, P63
Typical at T
= +25°C under nominal line voltage and full-load conditions, unless otherwise
noted. All models are tested and specified with external 22µF tantalum input and output
capacitors. These capacitors are necessary to accommodate our test equipment and may
not be required to achieve specified performance in your applications. See I/O Filtering and
Noise Reduction.
Ripple/Noise (R/N) is tested/specified over a 20MHz bandwidth and may be
reduced with external filtering. See I/O Filtering and Noise Reduction for details.
These devices have no minimum-load requirements and will regulate under no-load conditions.
Regulation specifications describe the output-voltage deviation as the line voltage or load is
varied from its nominal/midpoint value to either extreme.
Nominal line voltage, no-load/full-load conditions.
M E C H A N I C A L
S P E C I F I C A T I O N S
1.30
(33.02)
P A R T
N U M B E R
S T R U C T U R E
L SM
1.8
D12
Output
Configuration:
= Unipolar
Low Voltage
Non-Isolated SMT
Nominal Output Voltage:
or 5 Volts
Input Voltage Range:
D12
= 10.8 to 13.2 Volts
(12V nominal)
0.34
(8.64)
SMT COPPER LEADS
COPLANAR 0.004
0.085
(2.16)
Maximum Rated Output
Current in Amps
0.310
(7.87)
0.570 (14.48)
3 EQ. SP. @
0.190 (4.83)
(34.54)
0.062
(1.57)
TYP.
Case C45
0.05
(1.27)
0.53
0.48
(12.19) (13.46)
BOTTOM VIEW
0.55
(13.97)
0.112
(2.84)
TYP.
0.075
(1.91)
0.048
(1.22)
1.177
(29.90)
0.570 (14.48)
3 EQ. SP. @
0.190 (4.83)
0.010
(0.254)
0.570 (14.48)
3 EQ. SP. @
0.190 (4.83)
0.60
(15.24)
0.297
(7.54)
0.310
(7.87)
0.310
(7.87)
0.375
(9.53)
0.052
(1.32)
0.405
(10.29)
(10.92)
(1.57)
(1.32)
RECOMMENDED PAD LAYOUT
Recommended Pad Size: 0.15 x 0.10 (3.81 x 2.54)
0.112 TYP.
(2.84)
0.049
(1.24)
0.047
(1.19)
BOTTOM VIEW
LSM WITH REMOVEABLE HEAT SHIELD
FOR HIGH TEMPERATURE SOLDER
Refer to the last page for
Tape and Reel information.
CAUTION
PRESS TO REMOVE
THE HEAT SHIELD
AFTER THE SOLDER
PROCESS
Pin
I/O Connections
Function P63
On/Off Control
+Input
Common
+Output
OUT
Trim
+Sense
LSM-10A D12 Models
Performance/Functional Specifications
Typical @ T
= +25°C under nominal line voltage and full-load conditions unless noted.
Absolute Maximum Ratings
Input Voltage:
Continuous or transient
On/Off Control
(Pin 1)
Input Reverse-Polarity Protection
Output Overvoltage Protection
Output Current
Input Voltage Range
Input Current:
Normal Operating Conditions
Inrush Transient
Standby/Off Mode
Output Short-Circuit Condition
Input Reflected Ripple Current
➁ ➅
Input Filter Type
Undervoltage Shutdown
On/Off Control
➁ ➂
Input
10.8-13.2 Volts (12V nominal)
See Ordering Guide
0.08A
sec
1.5mA
12-40mA average (model dependent)
40mAp-p
Capacitive (44µF)
None
None
None
On = open (internal pull-up to +V
IN
Off = 0 to +0.4V (1mA max.)
15 Volts
+V
IN
None
None
Current limited. Devices can
withstand sustained output short
circuits without damage.
–40 to +125°C
See Reflow Solder Profile
Storage Temperature
Lead Temperature
These are stress ratings. Exposure of devices to any of these conditions may adversely
affect long-term reliability. Proper operation under conditions other than those listed in the
Performance/Functional Specifications Table is not implied.
Output
OUT
Accuracy
(50% load)
±1.25% maximum
Minimum Loading
No load
Maximum Capacitive Load
1000µF (low ESR, OSCON)
OUT
Trim Range
±10% (0.8V not trimmable)
Ripple/Noise
(20MHz BW)
➀ ➁ ➃
See Ordering Guide
Total Accuracy
3% over line/load/temperature
Efficiency
See Ordering Guide
Overcurrent Detection and Short-Circuit Protection:
Current-Limiting Detection Point
17 (12-23.5) Amps
Short-Circuit Detection Point
98% of V
OUT
set
SC Protection Technique
Hiccup with auto recovery
Short-Circuit Current
120-400mA average (model dependent)
Dynamic Characteristics
Transient Response
(50% load step) 100µsec to ±2% of final value
Start-Up Time:
IN
to V
OUT
and On/Off to V
OUT
75msec for V
OUT
= 1V and 0.8V
50msec for V
OUT
= 1.2V to 5V
Switching Frequency:
0.8V, 1V/1.2V Models
105/120kHz ±10%
1.5V/1.8V, 2V Models
160/177kHz ±10%
2.5V, 3.3V, 5V Models
195kHz ±10%
Environmental
Calculated MTBF
2.3 -1.8 million hours (1V
OUT
to 5V
OUT
Operating Temperature:
(Ambient)
Without Derating (Natural convection) –40 to +48/64°C (model dependent)
With Derating
See Derating Curves
Thermal Shutdown
Dimensions
Pin Dimensions/Material
Weight
Flamability Rating
+115°C (110 to 125°C)
T E C H N I C A L
N O T E S
All models in the LSM D12 Series are tested and specified with external
22µF tantalum input and output capacitors. These capacitors are necessary
to accommodate our test equipment and may not be required to achieve?
desired performance in your application. The LSM D12's are designed with
high-quality, high-performance
internal
I/O caps, and will operate within spec
in most applications with
no additional external components.
In particular, the LSM D12's input capacitors are specified for low ESR
and are fully rated to handle the units' input ripple currents. Similarly, the
internal output capacitors are specified for low ESR and full-range frequency
response. As shown in the Performance Curves, removal of the external 22µF
tantalum output caps has minimal effect on output noise.
In critical applications, input/output ripple/noise may be further reduced using
filtering techniques, the simplest being the installation of external I/O caps.
External input capacitors serve primarily as energy-storage devices. They
minimize high-frequency variations in input voltage (usually caused by IR
drops in conductors leading to the DC/DC) as the switching converter draws
pulses of current. Input capacitors should be selected for bulk capacitance (at
appropriate frequencies), low ESR, and high rms-ripple-current ratings. The
switching nature of modern DC/DC's requires that the dc input voltage
source have low ac impedance at the frequencies of interest. Highly inductive
source impedances can greatly affect system stability. Your specific system
configuration may necessitate additional considerations.
TO
OSCILLOSCOPE
Physical
1.3" x 0.53" x 0.34" (33.02 x 13.46 x 8.64 mm)
0.112" x 0.062" (2.84 x 1.57mm) rectangular
copper with gold plate over nickel underplate
0.28 ounces (7.8g)
UL94V-0
All models are tested and specified with external 22µF tantalum input and output capacitors.
These capacitors are necessary to accommodate our test equipment and may not be
required to achieve specified performance in your applications. All models are stable and
regulate within spec under no-load conditions.
See Technical Notes and Performance Curves for details.
The On/Off Control (pin 1) is designed to be driven with open-collector logic or the appli-
cation of appropriate voltages (referenced to Common, pin 3). Applying a voltage to On/Off
Control when no input voltage is applied to the converter may cause permanent damage.
Output noise may be further reduced with the installation of additional external output
filtering. See I/O Filtering and Noise Reduction.
MTBF’s are calculated using Telcordia SR-332(Bellcore), ground fixed, T
= +25°C, full
power, natural convection, +67°C pcb temperature.
Input Ripple Current is tested/specified over a 5-20MHz bandwidth with an external 33µF
input capacitor and a simulated source impedance of 220µF and 12µH. See I/O Filtering,
Input Ripple Current and Output Noise for details.
CURRENT
PROBE
BUS
+INPUT
IN
BUS
IN
COMMON
IN
= 33µF, ESR < 700mΩ @ 100kHz
BUS
= 220µF, ESR < 100mΩ @ 100kHz
BUS
= 12µH
Figure 2. Measuring Input Ripple Current
LSM-10A D12 Series
Output ripple/noise (also referred to as periodic and random deviations
or PARD) may be reduced below specified limits with the installation of
additional external output capacitors. Output capacitors function as true filter
elements and should be selected for bulk capacitance, low ESR, and appro-
priate frequency response. Any scope measurements of PARD should be
made directly at the DC/DC output pins with scope probe ground less than
0.5" in length.
Input Overvoltage and Reverse-Polarity Protection
LSM D12 SMT Series DC/DC's do not incorporate either input overvoltage
or input reverse-polarity protection. Input voltages in excess of the specified
absolute maximum ratings and input polarity reversals of longer than "instan-
taneous" duration can cause permanent damage to these devices.
Start-Up Time
The V
IN
to V
OUT
Start-Up Time is the interval between the time at which a
ramping input voltage crosses the lower limit of the specified input voltage
range (10.8 Volts) and the fully loaded output voltage enters and remains
within its specified accuracy band. Actual measured times will vary with input
source impedance, external input capacitance, and the slew rate and final
value of the input voltage as it appears to the converter.
The On/Off to V
OUT
Start-Up Time assumes the converter is turned off via the
On/Off Control with the nominal input voltage already applied to the converter.
The specification defines the interval between the time at which the converter
is turned on and the fully loaded output voltage enters and remains within its
specified accuracy band. See Typical Performance Curves.
Remote Sense
LSM D12 SMT Series DC/DC converters offer an output sense function on
pin 6. The sense function enables point-of-use regulation for overcoming
moderate IR drops in conductors and/or cabling. Since these are non-isolated
devices whose inputs and outputs usually share the same ground plane,
sense is provided only for the +Output.
The remote sense line is part of the feedback control loop regulating the
DC/DC converter’s output. The sense line carries very little current and
consequently requires a minimal cross-sectional-area conductor. As such, it
is not a low-impedance point and must be treated with care in layout and
cabling. Sense lines should be run adjacent to signals (preferably ground),
and in cable and/or discrete-wiring applications, twisted-pair or similar tech-
niques should be used. To prevent high frequency voltage differences between
OUT
and Sense, we recommend installation of a 1000pF capacitor close to
the converter.
The sense function is capable of compensating for voltage drops between the
+Output and +Sense pins that do not exceed 10% of V
OUT
[V
OUT
(+) – Common] – [Sense(+) – Common]
10%V
OUT
Power derating (output current limiting) is based upon maximum output cur-
rent and voltage at the converter's output pins. Use of trim and sense func-
tions can cause the output voltage to increase, thereby increasing output
power beyond the LSM's specified rating. Therefore:
(V
OUT
at pins) x (I
OUT
rated output power
The internal 10.5Ω resistor between +Sense and +Output (see Figure 1)
serves to protect the sense function by limiting the output current flowing
through the sense line if the main output is disconnected. It also prevents
output voltage runaway if the sense connection is disconnected.
Note: If the sense function is not used for remote regulation, +Sense
(pin 6) must be tied to +Output (pin 4) at the DC/DC converter pins.
+SENSE
+OUTPUT
COPPER STRIP
C1
C2
SCOPE
LOAD
COMMON
COPPER STRIP
C1 = NA
C2 = 22µF TANTALUM
LOAD 2-3 INCHES (51-76mm) FROM MODULE
Figure 3. Measuring Output Ripple/Noise (PARD)
All external capacitors should have appropriate voltage ratings and be located
as close to the converters as possible. Temperature variations for all relevant
parameters should be taken into consideration.
The most effective combination of external I/O capacitors will be a function
of your line voltage and source impedance, as well as your particular load and
layout conditions. Our Applications Engineers can recommend potential solu-
tions and discuss the possibility of our modifying a given device’s internal filter-
ing to meet your specific requirements. Contact our Applications Engineering
Group for additional details.
Input Fusing
Most applications and or safety agencies require the installation of fuses
at the inputs of power conversion components. LSM D12 Series DC/DC
converters are not internally fused. Therefore, if input fusing is mandatory,
either a normal-blow or a fast-blow fuse with a value no greater than 20 Amps
should be installed within the ungrounded input path to the converter.
As a rule of thumb however, we recommend to use a normal-blow or slow-
blow fuse with a typical value of about twice the maximum input current,
calculated at low line with the converters minimum efficiency.
Safety Considerations
LSM D12 SMT's are non-isolated DC/DC converters. In general, all DC/DC's
must be installed, including considerations for I/O voltages and spacing/
separation requirements, in compliance with relevant safety-agency speci-
fications (usually UL/IEC/EN60950).
In particular, for a non-isolated converter's output voltage to meet SELV
(safety extra low voltage) requirements, its input must be SELV compliant.
If the output needs to be ELV (extra low voltage), the input must be ELV.
LSM-10A D12 Models
On/Off Control
The On/Off Control pin may be used for remote on/off operation. LSM D12
Series DC/DC converters are designed so that they are enabled when the
control pin is left open (open collector) and disabled when the control pin is
pulled low (to less than +0.4V relative to Common). As shown in Figure 4, all
models have an internal 14kΩ pull-up resistor to V
IN
(+Input).
Dynamic control of the on/off function is best accomplished with a mechanical
relay or open-collector/open-drain drive circuit (optically isolated if appropri-
ate). The drive circuit should be able to sink appropriate current when
activated and withstand appropriate voltage when deactivated.
+INPUT
14kΩ
10kΩ
EXTERNAL
OPEN
COLLECTOR
INPUT
COMMON
External Input Open: On/Off pin Low = DC/DC converter Off
External Input Low: On/Off pin High = DC/DC converter On
+INPUT
14kΩ
ON/OFF
CONTROL
Figure 5. Driving the External Power-Up Open Collector
Output Overcurrent Detection
Overloading the power converter's output for an extended time will invariably
cause internal component temperatures to exceed their maximum ratings and
eventually lead to component failure. High-current-carrying components such
as inductors, FET's and diodes are at the highest risk. LSM D12 SMT Series
DC/DC converters incorporate an output overcurrent detection and shutdown
function that serves to protect both the power converter and its load.
If the output current exceeds it maximum rating by typically 70% (17 Amps) or
if the output voltage drops to less than 98% of it original value, the LSM D12's
internal overcurrent-detection circuitry immediately turns off the converter,
which then goes into a "hiccup" mode. While hiccupping, the converter will
continuously attempt to restart itself, go into overcurrent, and then shut down.
Under these conditions, the average output current will be approximately
400mA, and the average input current will be approximately 40mA. Once the
output short is removed, the converter will automatically restart itself.
Output Voltage Trimming
Allowable trim ranges for each model in the LSM D12 SMT Series are ±10%.
Trimming is accomplished with either a trimpot or a single fixed resistor. The
trimpot should be connected between +Output and Common with its wiper
connected to the Trim pin as shown in Figure 6 below.
A trimpot can be used to determine the value of a single fixed resistor
which can then be connected, as shown in Figure 7, between the Trim pin
and +Output to trim down the output voltage, or between the Trim pin and
Common to trim up the output voltage. Fixed resistors should have absolute
TCR’s less than 100ppm/°C to ensure stability.
The equations below can be starting points for selecting specific trim-resistor
values. Recall, untrimmed devices are guaranteed to be
±1.25%
accurate.
Adjustment beyond the specified ±10% adjustment range is not recommended.
When using trim in combination with Remote Sense, the maximum rated power
must not be exceeded (see Remote Sense).
COMMON
ON/OFF pin open: Logic High = DC/DC converter On
ON/OFF pin <0.4V: Logic Low = DC/DC converter Off
Figure 4. Driving the On/Off Control Pin with an Open-Collector Drive Circuit
Applying an external voltage to the On/Off Control pin when no input power is
applied to the converter can cause permanent damage to the converter. The
on/off control function, however, is designed such that the converter can be
disabled (control pin pulled low) while input voltage is ramping up and then
"released" once the input has stabilized (see also power-up sequencing).
Power-up sequencing
If a controlled start-up of one or more LSM D12 Series DC/DC converters
is required, or if several output voltages need to be powered-up in a given
sequence, the On/Off control pin can be driven with an external open collector
device as per Figure 5.
Leaving the input of the external circuit open during power-up will have the
output of the DC/DC converter disabled. When the input to the external open
collector is pulled low, the DC/DC converters output will be enabled.
LSM D12 SMT Series DC/DC converters do not incorporate output overvolt-
age protection. In the extremely rare situation in which the device’s feedback
loop is broken, the output voltage may run to excessively high levels (V
OUT
IN
). If it is absolutely imperative that you protect your load against any and
all possible overvoltage situations, voltage limiting circuitry must be provided
external to the power converter.
参数对比
与LSM-1.8/10-D12相近的元器件有:LSM-0.8/10-D12、LSM-1.2/10-D12。描述及对比如下:
型号 LSM-1.8/10-D12 LSM-0.8/10-D12 LSM-1.2/10-D12
描述 DC-DC Regulated Power Supply Module, 1 Output, Hybrid, SMT-6 DC-DC Regulated Power Supply Module, 1 Output, Hybrid, SMT-6 DC-DC Regulated Power Supply Module, 1 Output, Hybrid, SMT-6
是否无铅 含铅 含铅 含铅
是否Rohs认证 不符合 不符合 不符合
厂商名称 C&D C&D C&D
零件包装代码 MODULE MODULE MODULE
针数 6 6 6
Reach Compliance Code unknow unknown unknown
ECCN代码 EAR99 EAR99 EAR99
模拟集成电路 - 其他类型 DC-DC REGULATED POWER SUPPLY MODULE DC-DC REGULATED POWER SUPPLY MODULE DC-DC REGULATED POWER SUPPLY MODULE
最大输入电压 13.2 V 13.2 V 13.2 V
最小输入电压 10.8 V 10.8 V 10.8 V
标称输入电压 12 V 12 V 12 V
JESD-30 代码 R-XDMA-X6 R-XDMA-X6 R-XDMA-X6
JESD-609代码 e4 e4 e4
最大负载调整率 0.25% 0.375% 0.25%
功能数量 1 1 1
输出次数 1 1 1
端子数量 6 6 6
最大输出电压 1.98 V 0.81 V 1.32 V
最小输出电压 1.62 V 0.79 V 1.08 V
标称输出电压 1.8 V 0.8 V 1.2 V
封装主体材料 UNSPECIFIED UNSPECIFIED UNSPECIFIED
封装形状 RECTANGULAR RECTANGULAR RECTANGULAR
封装形式 MICROELECTRONIC ASSEMBLY MICROELECTRONIC ASSEMBLY MICROELECTRONIC ASSEMBLY
峰值回流温度(摄氏度) NOT SPECIFIED NOT SPECIFIED NOT SPECIFIED
认证状态 Not Qualified Not Qualified Not Qualified
表面贴装 NO NO NO
技术 HYBRID HYBRID HYBRID
端子面层 GOLD GOLD GOLD
端子形式 UNSPECIFIED UNSPECIFIED UNSPECIFIED
端子位置 DUAL DUAL DUAL
处于峰值回流温度下的最长时间 NOT SPECIFIED NOT SPECIFIED NOT SPECIFIED
微调/可调输出 YES NO YES
