首页 > 器件类别 > 半导体 > 电源管理
SDN5-24-100RED
线性与开关电源 120w 24vdc 5A redund
器件类别:半导体    电源管理
厂商名称:Sola
SDN™ Series Redundant Options
Power Supplies
The SDN Series standard options allow for operation in a
wide variety of applications. With the addition of an exter-
nal redundancy module, the SDN can also be used for true
redundant operation including 2N and N+x configurations.
All SDN units include built in current sharing for parallel and
redundant operation. All models ending in P also include
a DC OK status relay contact. The external modules
SDN 2.5-20RED and SDN 30/40RED increase the reliability
by isolating the supplies and adding more signal options.
Paralleling for increased power does not require the use of
these modules.
Module Compatibility
Two separate modules are available to provide the maximum
flexibility in size, cost and signaling capability. Refer to the
chart below for information on which module can be used for
each SDN power supply.
Power Rating
– A simple Yes or No indication that this module
can or cannot handle the power rating of that power supply.
Input/Output Signals
– Yes indicates that each power supply
would have an independent relay contact to provide power
supply status, and the DC bus output from the redundant
module has it’s own DC OK relay contact. Output only
indicates that only the output of the redundant module
would have a DC OK relay contact.
DC OK Relay Contact
True Isolation
High availability
SDN features and quality
EMC and
Low Volt.
Directive
Related Products
• SDN™ Series
• SFL Series
• Process Control
• Remote Location
• Critical Production
Redundancy Module Compatibility Chart
Single Phase SDN Series
Power Rating
Input / Output Signals
Power Rating
SDN 2.5-24-100P*
Yes
Yes
Yes
Yes
SDN 5-24-480
Yes
Output Only
Yes
Yes
SDN 4-24-100P*
Yes
Yes
Yes
Yes
SDN 10-24-480
Yes
Output Only
Yes
Yes
SDN 5-24-100P
Yes
Yes
Yes
Yes
SDN 20-24-480
Yes
Output Only
Yes
Yes
SDN 10-24-100P
Yes
Yes
Yes
Yes
SDN 30-24-480
No
N/A
Yes
Yes
SDN 20-24-100P
Yes
Yes
Yes
Yes
SDN 40-24-480
No
N/A
Yes
Yes
SDN 2.5-20RED
SDN 30/40RED
Three Phase SDN Series
Power Rating
Power Rating
SDN 2.5-20RED
SDN 30/40RED
* Paralleling will violate Class 2 current limits.
114
Visit our website at www.solahd.com or
contact Technical Services at (800) 377-4384 with any questions.
Power Supplies
SDN™ Redundant Series Specifications for SDN2.5-20RED and SDN 30/40RED
Catalog Number
SDN 2.5-20RED
SDN 30/40RED
Concept
By means of a separate redundancy module, you can interconnect several identical SDN power supply units in a N+1 redundant mode. These external
modules decouple the power supply outputs from each other so that, in case of failure, one power supply unit cannot overload the other units. The
modules incorporate DC OK relay contacts. The switch on front of the SDN power supply should be placed in parallel mode (not single mode) when
power supplies are used with redundant module.
Electrical Characteristics
-Nominal Value
-Max. Rated
Voltage Drop
-V
in
-> V
out
Current Handling Capacity
-Maximum Value
Inverse Battery Protection
Connection
20 A
Yes
Via captive screw terminals
Solid: 16-10 AWG (1.5 - 6 mm
Stranded: 16-12 AWG (1.5 - 4 mm
Solid: 16-5 AWG (1.5 - 16 mm
Stranded: 16-8 AWG (1.5 - 10 mm
40 A
Typ. 0.6 V
24 Vdc
35 V
-Connector size range
GND must be connected to module for voltage monitor to operate properly.
See Connectors and Wiring diagrams on next page.
Relay Contacts
(1) V
out
“OK” - N.O. Contact
(2) V
in
“OK” - N.O. Contact
> 18 Vdc ±5%
30 Vdc @ 2A / 250 V @ 2A
out
“OK” Green LED
> 18 Vdc ±5%
Dimensions
4.88 in x 1.97 in x 4.55 in
(124 mm x 50 mm x 116 mm)
4.88 in x 2.56 in x 4.55 in
(124 mm x 65 mm x 116 mm)
DC Okay Contacts (qty) description
-Voltage Set Point
-Contact Rating
DC OK LED
-Voltage Set Point
(1) V
out
“OK” - N.O. & N.C. Contact
H x W x D - inches (mm)
Free Space for Ventilation -
inches (mm)
Weight lbs (kg)
Above/Below: 0.39 in. (10 mm) recommended
Left/Right: 0.39 in. (10 mm) recommended
1.38 (625)
General
1.43 (646)
Ambient Temperature
Storage: -25°C...+85°C Operation: -10°C...+60°C full power with operation to 70°C possible with a
linear derating to half power from 60°C to 70°C (Convection cooling, no forced air required). Operation up
to 50% load permissible with sideways or front side up mounting orientation. The relative humidity is
< 90% RH, noncondensing.
115
Wiring Diagram for SDN 2.5-20RED
Power Supplies
Single
Parallel
Single
Parallel
Notes:
1. The Common (marked “COM -“) connection to the module is required for voltage monitoring (DC OK Contacts), and is not meant to be
part of the current path from the power supply to the load.
2. Protective earth connection only provides protective ground to the metal case of the module. This connection is isolated from the
positive and common connections.
116
Power Supplies
Wiring Diagram for SDN 30/40RED
Single
Parallel
Single
Parallel
Notes:
117
参数对比
与SDN5-24-100RED相近的元器件有:。描述及对比如下:
型号 SDN5-24-100RED
描述 线性与开关电源 120w 24vdc 5A redund
