首页 > 器件类别 >
AH7416
Cooper-Wheelock AS/AH Serles
厂商名称:Gamewell-FCI ( Honeywell )
厂商官网:http://www.gamewell-fci.com
Cooper-Wheelock
AS/AH Series
Single & Multi-Candela
AS Series Audible Strobe &
AH Series Audible Appliances
The 2-wire Cooper-Wheelock AS Series audible/
visual and AH Series audible notification appliances
offer many features with low current draws.
Strobe options for wall-mounted models include
15/75 cd or field-selectable Multi-Candela strobes
that may be set to 15, 30, 75, or 110 cd.
Ceiling mounted models incorporate field-selected
strobe settings of 15, 30, 75 or 95 cd.
The audible notification appliances provide a field-
selectable choice of either a continuous horn tone or
temporal pattern (per ANSI S3.41) when constant
voltage is supplied by the notification appliance cir-
cuit. Each tone has three dBA settings to choose
from. Additionally, the audible tone may be silenced
while maintaining strobe activation.
All models may be synchronized when the models
are used in conjunction with the Cooper-Wheelock
SM and DSM Sync Modules.
The synchronization of the continuous horn tone
provides the temporal pattern mandated by NFPA
72 for fire evacuation signaling. This ensures a
clearly distinguishable temporal pattern when two or
more audible devices are within hearing distance. If
the horn tones are not synchronized, the temporal
patterns may overlap. At the same time, the strobes
will also be synchronized. This process is in compli-
ance with ADA recommendations regarding photo-
sensitive epilepsy and NFPA and UFC standards
required when installing two or more visual appli-
ances within a common field of view.
Only two wires are required to achieve these se-
quences of operation. Separate circuits for audible
and visual devices are not necessary.
Series AS
Series AH
Approvals include:
- UL Standard 1971
- New York City (MEA)
- UL Standard 464
- California State Fire
Marshall (CSFM)
ADA/NFPA/UFC/ANSI compliant
Wall-mounted models are available with field multi-
candela settings of 15, 30, 75, or 110 cd
Ceiling mounted models are available with field select-
able multi-candela settings of 15, 30, 75, or 95 cd
Single candela models are available in 15/75 cd
Weatherproof models are available for outdoor use
(ASWP)
Selected continuous horn or temporal pattern
(ANSI 3.41)
Three (3) field dBA settings adjusted to 90, 95, or 99
dBA for both tones
Silenceable horns and non-silenceable strobes
installed over the same wires
Strobes flash once per second over the regulated volt-
age range
12 & 24 VDC models with wide UL “regulated voltage
range” using filtered DC or unfiltered FWR input
voltage
Synchronize with SM or DSM synchronization
modules
Fast installation with In/Out screw terminals using 12 to
18 AWG wires
An ISO 9000-2000 Company
GAMEWELL-FCI
12 Clintonville Road, Northford, CT 06472 - Tel: (203) 484-7161 - Fax: (203) 484-7118
2008
Specifications are for information only, are not intended for installation purposes, and are subject to change without notice. No responsibility is assumed by Gamewell-FCI for their use.
Gamewell-FCI. All rights reserved.
9020-0572 Rev. C1 page 1 of 4
Description (Continued)
General Notes:
Strobes are designed to flash at one flash per second
minimum over the Regulated Voltage Range. Note that
NFPA-72 (1999) specifies a flash rate of one to two
flashes per second and ADA guidelines specify a flash
rate of one to three flashes per second.
All candela ratings represent minimum effective strobe
intensity based on UL Standard 1971.
Series AS strobe products are Listed under UL Standard
1971 for indoor use with a temperature range of 32° F to
120° F (0° C to 49° C) and a maximum humidity of 93%
(+/- 2%).
Series AH horns are Listed under UL Standard 464 for
audible signal appliances (indoor use only).
Series AH-24WP audible appliances are Listed under UL
Standard 464 for indoor/outdoor use with a temperature
range of –31° F to 150° F
(-35° C to 66° C) and a maximum humidity of 95%.
“Regulated Voltage Range” is the state-of-the-art technol-
ogy used by UL to identify the voltage range. Prior to this
technology, UL used the term, “Listed Voltage Range.”
Table 3: Average Mean Current * Series
AH-24R/W & AH-12-R/W * W P (Horn only)
High
Medium
16.0 VDC
0.035
0.020
24.0 VDC
0.050
0.026
33.0 VDC
0.089
0.035
8.0 VDC
0.093
0.037
12.0 VDC
0.108
0.049
17.5 VDC
0.128
0.069
Low
0.14
0.017
0.021
0.080
0.085
0.042
Table 4: Avereage RM* Current Series AS0241575
16.0 VDC
24.0 VDC
33.0 VDC
High
0.130
0.107
0.105
Medium
0.114
0.085
0.075
Low
0.108
0.075
0.060
Table 5:dBA Ratings for 12 VDC & 24 VDC Series
AS/AH 12 & 24 VDC Horns
Reverberant dBA
per UL 464 @
Description Volumn 10 pt.
Continuous
High
91
Horn
Medium
88
Low
83
Temporal
High
87
Pattern
Medium
84
Low
79
Anchoic
dBA @
10 pt.
99
95
90
99
95
90
Table 1: Ratings per UL 1971
Input
VDC
Model
AS-24MCW-FA 24
AS-241575W-FR 24
AS-121575W-FR 12
AS-24M C C –FW
24
AS WP-2475W-FR
24
Regulated Voltage
Range VDC/FW R
160-330
160-330
80-175
160-330
160-330
Strobe
Candela (cd)
15/30/75/110
15 (75 or Axis)
15 (75 or Axis)
15/30 /75 /95
75 @ -31° F
Table 2: Average RMS Current* fir AS-24 MCW Wall-
Models @ each Candela Setting
Average Current with High dBA Setting (99 dBA)
15 cd
30 cd
75 cd
110 cd
16.0 VDC 0.099
0.135
0.219
0.308
24.0 VDC 0.093
0.114
0.157
0.197
33.0 VDC 0.098
0.108
0.138
0.166
Average Current with Medium dBA Setting (95 dBA)
16.0 VDC 0.078
0.116
0.203
0.282
24.0 VDC 0.065
0.088
0.133
0.179
33.0 VDC 0.065
0.078
0.106
0.134
Average Current with Low dBA Setting (90dBA)
16.0 VDC 0.070
0.111
0.201
0.279
24.0 VDC 0.052
0.077
0.126
0.169
33.0 VDC 0.046
0.063
0.063
0.121
Table 6: Average RM S Current* for AS-24 M CC Ceil-
ing Models @ each Candela Setting
15 cd
30 cd
75 cd
95 cd
16.0 VDC
0.105
0.145
0.226
0.314
24.0 VDC
0.097
0.120
0.161
0.202
33.0 VDC
0.101
0.113
0.139
0.168
16.0 VDC
0.084
0.126
0.222
0.309
24.0 VDC
0.069
0.094
0.145
0.195
33.0 VDC
0.068
0.083
0.114
0.145
Average Current with Low dBA Setting (90 dBA)
0.121
0.220
0.306
16.0 VDC
0.076
24.0 VDC
0.069
0.084
0.138
0.185
33.0 VDC
0.049
0.068
0.102
0.132
Table 7: Average Mean Current* Series AS-241575
High
Medium Low
8.0 VDC
0.320
0.276
0.286
12.0 VDC
0.250
0.195
0.175
17.5 VDC
0.205
0.105
0.130
GAMEWELL-FCI
9020-0572 Rev. C1 page 2 of 4
SYNC MODULES
MODEL
SM-12/24-R #
SM-12/24-R ##
ORDER
CODE
6369
6374
INPUT
VOLTAGE (VDC)
24VDC
24VDC
AVERAGE MEAN
CURRENT@ 24VDC
0.028A
0.035A
# SM Sync Module is rated for 3.0 amps @ 24 VDC
## DSM Sync Module is rated for 3.0 amps per circuit.
The maximum number of interconnected
DSM Modules is 20.
WIRING DIAGRAMS
SERIES AS APPLIANCES NON-SYNCHRONIZED
FROM
PRECEDING
APPLIANCE
OR FACP
TO NEXT
APPLIANCE
OR EOLR
SERIES AS APPLIANCES SYNCHRONIZED
WITH SM MODULE SINGLE CLASS "B" NAC
CIRCUIT WITH AUDIBLE SILENCE FEATURE
STROBE
NAC
CIRCUIT
AUDIBLE
NAC
CIRCUIT
SM
+ STROBE
- STROBE
WITH DSM MODULE SINGLE CLASS "A" NAC
CIRCUIT WITH NO AUDIBLE SILENCE FEATURE
STROBE
NAC
CIRCUIT
OUT
AS
+ AUDIBLE
EOLR
- AUDIBLE
AS
WITH MUTIPLE DSM MODULES
AUDIBLE
NAC
CIRCUIT
STROBE
NAC
CIRCUIT
DSM
+ SYNC
- SYNC
+ OUT 1
+ IN 1
DSM #1
+ SYNC
- SYNC
AS
AS
AS
AS
AS
AUDIBLE
NAC
CIRCUIT
STROBE
NAC
CIRCUIT
AUDIBLE
NAC
CIRCUIT
STROBE
NAC
CIRCUIT
DSM #2
+ SYNC
- SYNC
STROBE
NAC
CIRCUIT
RETURN
MINUS 1
+ AUDIBLE
- AUDIBLE
MINUS 2
+ IN 2
+ OUT 2
AS
AS
DSM #3
+ SYNC
- SYNC
AS
AS
AS
AS
AS
DSM INTERCONNECTING WIRING SHOWN.
MAXIUMUM OF TWENTY (20) MODULES
GAMEWELL-FCI
9020-0572 Rev. C1 page 3 of 4
Architects and Engineers Specifications
The notification appliances shall be Cooper-Wheelock Series AS audible/strobe appliances and Series AH audible appliances or
approved equals. The Series AS appliance shall be listed under UL Standard 1971 (Emergency Devices for the Hearing Impaired)
for indoor Fire Protection Service. The Series AH Audible shall be UL Listed under Standard 464 (Fire Protective Signaling). Both
shall meet the requirements of FCC Part 15 Class B. All inputs shall be compatible with standard reverse polarity supervision of
circuit wiring by a fire alarm control panel (FACP).
The audible portion of the appliance shall have a minimum of three (3) field selectable settings for dBA levels and shall have a
choice of continuous or temporal pattern audible output.
The strobe portion of the appliance shall produce a flash rate of one (1) flash per second over the Regulated Voltage Range and
shall incorporate a Xenon flashtube enclosed in a rugged Lexan
lens. The series AS shall be of low current design. Where Multi-
Candela appliances are specified, the strobe intensity shall have a minimum of four (4) field selectable settings and shall be rated
per UL Standard 1971 at: 15, 30, 75, and 110 candela for wall mount, or 15, 30, 75, and 95 candela for ceiling mount. The selector
switch for selecting the candela shall be tamper resistant and not accessible from the front of the appliance. The 15/75 candela
strobe shall be specified when 15 cd UL Standard 1971 Listing with 75 cd on-axis is required (e.g. ADA compliance).
When synchronization is required, the appliance shall be compatible with Cooper-Wheelock’s SM and DSM Sync Modules. The
strobes shall not drift out of synchronization at any time during operation. If the sync module fails to operate, i.e. contacts remain
closed), the strobe shall revert to a non-synchronized flash-rate. The appliance shall also be designed so that the audible signal
may be silenced while maintaining strobe activation.
The Series AS audible/strobe and Series AH audible shall incorporate a patented universal mounting plate that shall allow mount-
ing on a single-gang, double-gang, 4-inch square, 100 mm European type backbox, or the SHBB surface backbox. If required, an
NATP (Notification Appliance Trimplate) shall be provided.
All notification appliances shall be backward compatible.
Strobe
Non-Sync
Sync w SM/
24
or DSM
Candela
VDC VDC
AS-24MCW-FR
15/30/75/110
AS-24M CW –FW
15/30/75/110
AS-241575W - FR 15 (75 on Axis)
AS-121575W –FR
15 (75 on Axis)
AS-24MCC –FW
15/30/75/95
ASW-P-2475W –FR 75 @ -31° F
AH –24-R
AH –24W P-R
AH –12W P-R
Model
Wall Ceiling
Mount Mount
UL MEA CSFM FM BFP
Ordering Information
9025
7405
7410
3162
9012
7892
7891
7416
7415
AS-24MCW-FR
AS-24M CW –FW
AS-241575W - FR
AS-121575W –FR
AS-24MCC –FW
ASW-P-2475W –FR
AH –24-R
AH –12-R
AH –24W P-R
AH –12W P-R
GAMEWELL-FCI
9020-0572 Rev. C1 page 4 of 4
参数对比
与AH7416相近的元器件有:AS7410、AS9024、AS9025、AH7891、AH7892、AH7415。描述及对比如下:
型号 AH7416 AS7410 AS9024 AS9025 AH7891 AH7892 AH7415
描述 Cooper-Wheelock AS/AH Serles Cooper-Wheelock AS/AH Serles Cooper-Wheelock AS/AH Serles Cooper-Wheelock AS/AH Serles Cooper-Wheelock AS/AH Serles Cooper-Wheelock AS/AH Serles Cooper-Wheelock AS/AH Serles
