首页 > 器件类别 >
DVP-EH
Analog Input Module Instruction Sheet
厂商名称:DELTA
厂商官网:http://www.deltaww.com/
2.3
External wiring
Note 1: Please isolate analog input and other
power wiring.
http://www.delta.com.tw/products/plc.asp
voltage input
-10V~+10V
CH1
*5
DVP-EH
DVP04AD-H
Analog Input Module
Instruction Sheet
WARNING
shielding cable*1
current input
-20mA~+20mA
V+
I+
COM
FG
104.7K
250
104.7K
AG
104.7K
250
104.7K
AG
CH1
Note 2: If connect to current signal, please short
out between V+ and I+ terminals.
Note 3: If noise is significant, please connect FG
to ground.
Note 4: Please connect
terminal of power
CH4
*2
shielding cable*1
*3
terminal of power module
*4
System Grounding
Class 3 Grouning
(100 or less)
V+
I+
COM
FG
CH4
Please carefully read this instruction thoroughly prior to use the DVP04AD-H.
The DC input power must be OFF before any maintenance.
This is an OPEN-TYPE built-in DVP04AD-H, and the DVP04AD-H is certified to meet the safety
requirements of IEC 61131-2 (UL 508) when installed in the enclosure to prevent high
temperature, high humidity, exceessive vibration, corrosive gases, liquids, airbome dust or
metallic particles. Also, it is equipped with protective methods such as some special tool or key to
open the enclosure, in order to prevent the hazard to users and the damage to the DVP04AD-H.
Do not connect the AC power to any of the input/output terminals, or it may damage the
DVP04AD-H. Make sure that all the wiring is well conducted prior to power on.
Do not touch the internal circuit for at least 1 minute after the power OFF.
Make sure that the DVP04AD-H is properly grounded
, to prevent any electromagnetic noise.
24+
24-
DC/DC
converter
+15V
AG
-15V
module and
terminal of analog
input module to system earth point and
make system earth point be grounded
or connects to machine cover.
Note 5: If the noise interference from loaded
wire input terminal is significant, please
connect a capacitor with 0.1~0.47µF
25V for noise filtering.
Warning: DO NOT wire to the No function
terminal
Function Specifications
Analog/ Digital (4A/D) module
Power supply voltage
Analog input channel
Analog input range
Digital conversion range
Resolution
Input impedance
Overall accuracy
Response time
Isolation Method
Absolute input range
Digital data format
Average function
Self diagnose function
Communication mode
(RS-485)
STANDARD SPECIFICATIONS
Voltage input
Current input
24 VDC(20.4VDC~28.8VDC) ( –15%〜+20%)
4 channel / each module
±10V
±20
±8000
±4000
14 bits(1
LSB
=1.25 mV)
13 bits (1
LSB
=5 µA)
200 KΩ or above
250Ω
±0.5%
of full scale of 25℃(77℉)
±1%
of full scale during 0~55℃ (32~131℉)
3 ms
channels
It has isolation between digital area and analog area. There is no
isolation among channels.
±15
±32
2’s complementary of 16-bit, 13 Significant Bits
Yes (CR#2~CR#5 can be set and setting range is K1~K4096)
Upper and lower bound detection / channels
Either in ASCII or in RTU mode, communication rate can be 4800
/9600 /19200 /38400 /57600 /115200. Communication format of ASCII
mode is 7Bit, even bit, 1 stop bit (7 E 1). Communication format of
RTU mode is 8Bit, even bit, 1 stop bit (8 E 1). Can’t use RS-485 if the
connection to PLC MPU is in series.
If DVP04AD-H modules are connected to MPU, the modules are
numbered from 0 – 7. 0 is the closest and 7 is the furthest to the MPU.
8 modules is the max and they do not occupy any digital I/O points of
the MPU.
Power Specification
24 VDC(20.4VDC~28.8VDC) ( –15%~+10%), 2W, supply from
external power
Environment Condition
Follow the DVP-PLC MPU
All places between terminals and ground comply with the spec.
DVP04AD-H analog signal input module
RS-485
CR
Parameter Latched
Register name
No.
address
#13 H 400D
Present value of CH2
input signal
#14 H 400E
Present value of CH3
input signal
#15 H 400F
Present value of CH4
input signal
#16 ~ #17
#18 H 4012
R/W To adjust OFFSET
value of CH1
#19 H 4013
value of CH2
#20 H 4014
value of CH3
#21 H 4015
value of CH4
#22 ~ #23
#24 H 4018
R/W To adjust GAIN value
of CH1
#25 H 4019
of CH2
#26 H 401A
of CH3
#27 H 401B
of CH4
#28 ~ #29
#30 H 401E
Error status
Explanation
b15 b14 b13 b12 b11 b10
b9
b8
b7
b6
b5
b4
b3
b2
b1
b0
Display the present value of CH3~CH4 input signal
Reserved
Offset setting of CH1~CH4. Factory setting is K0 and unit is LSB.
Voltage input: setting range is K-4000 ~K4000
Current input: setting range is K-4000 ~K4000
Reserved
GAIN setting of CH1~CH4. Factory setting is K4000 and unit is LSB.
Voltage input: setting range is K-3200 ~K16000.
Current input: setting range is K-3200 ~K10400.
INTRODUCTION
Model Explanation and Peripherals
Thank you for choosing DELTA’s PLC DVP Series. The analog input module receives external
4-point analog signal input (voltage or current) and converts it into 14 bits digital signal. The
analog input module of DVP04AD-H series can read/write the data of analog input module by
using instructions FROM / TO via DVP-PLC EH Series MPU program. There are 49 CR (Control
Register, each register has 16-bit) in each module.
Software version of DVP04AD-H analog input module can be updated via RS-485 communication.
Users can select input from voltage or current via wiring. Voltage input range is
±10V
DC
(resolution is 1.25 mV). Current input range is
±20
mA (resolution is 5 µA).
Nameplate Explanation
Model Name
Input power supply spec.
Analog input/output module spec.
Barcode
VX.XX
Reserved
The data register used to save all error status. Please refer to fault code chart for
details.
#31 H 401F
R/W Communication
Setting RS-485 communication address. Setting range is 01~255 and factory setting
address setting
is K1
#32 H 4020
R/W Communication baud It is used to set communication baud rate (4800, 9600, 19200, 38400, 57600,
rate setting
115200bps). Communication format: ASCII mode is 7Bit, even bit, 1 stop bit (7 E 1).
Communication format of RTU mode is 8Bit, even bit, 1 stop bit (8 E 1).
b0: 4800 bps (bit/sec).
b1: 9600 bps (bit/sec). (factory setting)
b2: 19200 bps (bit/sec).
b3: 38400 bps (bit/sec).
b4: 57600 bps (bit/sec).
b5: 115200 bps (bit/sec).
b6-b13: reserved.
b14: exchange low and high byte of CRC check code (only for RTU mode)
b15: ASCII / RTU mode selection
#33 H 4021
R/W Reset to factory
b15 b14 b13 b12 b11 b10 b9 b8 b7 b6 b5 b4 b3 b2 b1 b0
setting and set
Reserved
CH4
CH3
CH2
CH1
characteristics
Factory setting is H0000.
adjustable priority
Give CH1 setting for example:
1. When b0=0, user can set OFFSET and GAIN value of CH1 (CR#18, CR#24).
When b0=1, inhibit user to adjust OFFSET and GAIN value of CH1 (CR#18,
CR#24).
2. b1 means if characteristic register is latched. b1=0 (factory setting, latched), b1=1
(not latched).
3. When b2 is set to 1, all settings will reset to factory setting.
#34 H 4022
Software version
It is hexadecimal to display software version. For example: H 010A means 1.0A.
#35~#48
System used
means latched.
means not latched.
R means can read data by using FROM instruction or RS-485.
W means can write data by using TO instruction or RS-485.
LSB (Least Significant Bit): 1. Voltage input: 1
LSB
=10V/8000=2.5mV. 2. Current input: 1
LSB
=20mA/4000=5µA.
20.4VDC ~ 28.8VDC
-10V ~ +10V or -20mA ~+20mA
1.25mV or 5 A
04AD-H0T 4120001
Model Explanation
Model
Serial Number
Connect to DVP-PLC MPU
in series
3.2
Other Specification
Product Series
Input+O utput point
S: for SS series MPU
P: for EP series MPU
H: for EH ser ies MPU
Production week
Production year (2004)
Production place (Taoyuan)
Production Model
Max. Rated Consuming Power
Spec. of Prevent Static Electricity
Model type
AD: Analog input module
DA: Analog output module
PT: Platinum temperatur e sensors(PT-100)
TC: Thermocouple sensor s(Type J/K)
XA: A/D , D/A Functions
RT: Resistor Thermocouple
HC: High speed count input module
PU: single axis positioning unit
CR
No.
#0
#1
RS-485
Parameter Latched
Register name
address
H 4000
Model type
H 4001
R/W Input mode setting
CR (Control Register)
Explanation
b9
b8
b7
b6
b5
b4
b3
b2
b1
b0
2.2
Product Profile and Outline
System used. DVP04AD-H model code =H 400
Reserved
CH4
CH3
CH2
Input mode setting: factory setting is H0000.
Mode 0: input voltage mode (-10V~+10V).
Mode 1: input voltage mode (-6V~+10V).
Mode 2: input current mode (-12mA~+20mA)
Mode 3: input current mode (-20mA~+20mA)
Mode 4: none use.
CH1
Unit: mm
1. DIN rail track (35mm)
2. Mounting hole for wire to connect extension
unit/extension module
3. Model name
4. Indicator for power, error and run status
5. DIN rail clip
6. Terminals
7. Mounting hole
8. Terminal layout
9. Mounting port to connect extension
#2
#3
#4
#5
#6
#7
#8
#9
H 4002
H 4003
H 4004
H 4005
H 4006
H 4007
H 4008
H 4009
R/W
R/W
R/W
R/W
CH1 average times
CH2 average times
CH3 average times
CH4 average times
average value of CH1
input signal
average value of CH2
input signal
average value of CH3
input signal
average value of CH4
input signal
present value of CH1
input signal
The number of readings used for calculating “average” temperature on channels
CH1~CH4. Setting range is K1~K4096 and factory setting is K10.
Display average value of CH1~CH4 input signal
#10 ~ #11
#12 H 400C
Reserved
Display present value of CH1~CH2 input signal
Explanation:
1. CR#0: The content of CR#0 is model type, user can read the data from program to know if there
is extension module.
2. CR#1: CR#1 is used to set 4 internal channels working mode of analog input module. Every
channel has four modes to set and can be set individually. For example: if setting CH1 to mode 0
(b2~b0=000), CH2 to mode 1(b5~b3=001), CH3: mode2 (b8~b6=010), CH4: mode
3(b11~b9=011). It needs to set CR#1 to H0688 and the upper bit (b12~b15) will reserved. The
factory setting of CR#1 is H0000.
3. CR#2 ~ CR#5: it is used to set average times of CH1~CH4. Setting range is K1~K4096 and
4. CR#6 to CR#9 are the average value that calculates according to the value that is set in
CR#2~CR#5 (average time of CH1~CH4 input signal). For example, if CR#2 (the average times
of CH1) is 10, it will calculate the average of CH1 input signal every 10 times.
5. CR#10, CR#11, CR#16, CR#17, CR#22, CR#23, CR#28, CR#29 reserved.
6. CR#12 ~ CR#15: display present value of CH1~CH4 input signal.
7. CR #18~ CR #21: the content is the value of adjusting OFFSET value of CH1~CH4 if analog
input voltage or current is 0 after it transfers from analog to digital. Voltage setting range:
-5V~+5V(-4000
LSB
~+4000
LSB
). Current setting range: -20mA~+20mA (-4000
LSB
~+4000
LSB
8. CR #24~ CR #27: means analog input voltage or current when conversion value from analog
signal to digital is 4000. Voltage setting range: -4V~+20V(-3200
LSB
~+16000
LSB
). Current setting
range: -16mA~+52mA(-3200
LSB
~+10400
LSB
). But please be noticed GAIN VALUE – OFFSET
VALUE = +800
LSB
~+12000
LSB
(voltage) or +800
LSB
~+6400
LSB
(current). When this value under this
range, the resolution of the input signal will be thin and the variation of value will be larger. When
this value exceeds this range, the resolution of input signal will be thick and the variation of value
will be smaller.
9. CR#30 is the fault code. Please refer to the chart below.
Fault description
Content
b15~b8 b7 b6 b5 b4 b3 b2 b1 b0
Power source abnormal
K1(H1)
0 0 0 0 0 0 0 1
Analog input value error
K2(H2)
0 0 0 0 0 0 1 0
Setting mode error
K4(H4)
0 0 0 0 0 1 0 0
Offset/Gain error
K8(H8)
0 0 0 0 1 0 0 0
Reserved
Hardware malfunction
K16(H10)
0 0 0 1 0 0 0 0
Digital range error
K32(H20)
0 0 1 0 0 0 0 0
Average times setting error
K64(H40)
0 1 0 0 0 0 0 0
Instruction error
K128(H80)
1 0 0 0 0 0 0 0
Note: Each fault code will have corresponding bit (b0~b7). Two or more faults may happen at
the same time. 0 means normal and 1 means having fault.
10. CR#31: it is used to set RS-485 communication address. Setting range is 01~255 and factory
setting is K1.
11. CR#32 is used to set RS-485 communication baud rate: 4800, 9600, 19200, 38400, 57600,
115200 bps. b0: 4800bps. b1: 9600bps. (factory setting) b2: 19200bps. b3: 38400 bps. b4:
57600 bps. b5: 115200 bps. b6-b13: reserved. b14: exchange low and high byte of CRC
check code. (only for RTU mode) b15=0: ASCII mode. b15=1: RTU mode. Communication
format: ASCII mode is 7Bit, even bit, 1 stop bit (7 E 1). Communication format of RTU mode
12. CR#33 is used to set the internal function priority, such as characteristic register. Output
latched function will save output setting in the inner memory before power loss.
13. CR#34: software version.
14. CR#35~ CR#48: system used.
15. The corresponding parameters address H4000~H4030 of CR#0~CR#48 are provided for user to
read/write data through RS-485.
A. Communication baud rate: 4800, 9600, 19200, 38400, 57600, 115200 bps.
B. Communication format: ASCII mode is 7Bit, even bit, 1 stop bit (7 E 1). Communication
C. Function code: 03H—read data from register. 06H—write one WORD into register.
10H—write multiple WORD into registers.
M1002
TO
TO
X0
TO
TO
K0
K0
K19
K25
K400
K3600
K1
K1
K0
K0
K1
K33
H18
H0
K1
K1
Writing H18 to CR#1 of analog
input mode no. 0 and set CH2 to
mode 3 (current input: -20 mA ~
+20mA)
Writing H0 to CR#33 and allow to
adjust characteristics of CH4.
When X0 switches from Off to
On, K400
LSB
of OFFSET value will
be wrote in CR#19 and K3600
LSB
of GAIN value will be wrote in
CR#25.
The instruction will be executed when X0=On. The instruction won’t be executed
when X0=Off and the content of previous reading data won’t change.
X0
FROM
K0
K24
D0
K2
API
79
TO
Word device
KnX KnY KnM KnS
Special module CR
data write in
Applicable model
ES
EP
EH
Bit device
m
m
n
Lamp display:
1.
2.
INITIAL PLC START-UP
When power is on, POWER LED will be lit and ERROR LED will be lit for 0.5 second.
Normal run: POWER LED should be lit and ERROR LED should turn off. When power
supply is lower than 19.5V, ERROR LED will blink continuously till the power supply goes
higher than 19.5V.
3. When it connects to PLC MPU in series, RUN LED on MPU will be lit and A/D LED or D/A
LED should blink.
4. After receiving the first RS-485 instruction during controlling by RS-485, A/D LED or D/A
LED should blink.
5. After converting, ERROR LED should blink if input or output exceeds upper bound or lower
than lower bound.
Example:
M1000
FROM
K0
D0
K0
K1
M1002
= H400 D0
TO
TO
= H400 D0
FROM
END
K0
K0
K0
K1
K2
K6
H3030
K32
D20
K1
K2
K4
16-bit instruction (9 STEPS)
Continuous
Pulse
TO
TOP
execution
execution
ADJUST A/D CONVERSION CHARACTERISTIC CURVE
5.1 Adjust A/D Conversion Characteristic Curve
Voltage input mode
+8000
32-bit instruction (17 STEPS)
Note: The usage range of operand m
is 0~7.
Continuous
Pulse
DTOP
: ES/EP: 0-48, DTO execution
execution
EH: 0-254.
Flag: When M1083=On, it allows
The usage range of operand n: ES/EP: n=
to insert interrupt during
1~(49-m2), EH: 1~(255-m2).
FROM/TO.
For ES series, it doesn’t support pulse
Refer to following for detail.
execution instruction (TOP, DTOP)
: the number of special module.
of special module that will be wrote in.
data number to write in one time.
: the number of CR (Control Register)
: the data to write in CR.
: the
mode 0
Mode 0 of CR#1 GAIN=5V (4000
LSB
OFFSET=0V (0
LSB
mode 1
Command
Explanation
Digital
output
+4000
-10V
-6V
Mode 1 of CR#1 GAIN=6V (4800
LSB
OFFSET=2V (1600
LSB
GAIN:
Voltage input value when digital
output is 4000. Setting range is
5V 6V
-4V~+20V (-3200
LSB
~ +16000
LSB
2V
10V
OFFSET:
OFFSET GAIN
output is 0.
-4000
Setting range: -5V~+5V (-4000
LSB
+4000
LSB
GAIN-OFFSET: Setting range is +1V~+15V
(+800
LSB
~ +12000
LSB
-8000
Voltage input
DVP-series PLC uses this instruction to write data into CR of special module.
: When assigning bit operand, K1~K4 can be used for 16-bit and K5~K8 can
be used for 32-bit.
Program
Example
Using 32-bit instruction DTO, program will write D11 and D10 into CR#3 and
CR#2 of special module#0. It only writes a group of data in one time (n=1).
The instruction will be executed when X0=On and it won’t be executed when
X0=Off. The data that wrote in previous won’t have any change.
X0
DTO
K0
K2
D0
K1
The rule of instruction operand:
m1: arrangement number of special module. The number of special module
that connects to PLC MPU. The numbering order of special module from the
near to the distant of MPU is from 0 to 7. The maximum is 8 special modules
and won’t occupy I/O point.
m2: the number of CR. Built in 16-bit of 49 groups memory of special module
is called CR (Control Register). The number of CR uses decimal digital
(#0~#48). All running status and setting values of special module has
included.
If using FROM/TO instruction, the unit of read/write of CR is one number for
one time. If using DFROM/DTO instruction, the unit of read/write of CR is two
numbers in one time.
Upper 16-bit Lower 16-bit
Current input mode:
+4000
mode 3
Mode 2 of CR#1 GAIN = 20mA (4000
LSB
OFFSET=4mA (800
LSB
Footnote
Digital
output
-20mA
-12mA
4mA
OFFSET
Mode 3 of CR#1 GAIN = 20mA (4000
LSB
mode 2
OFFSET=0mA (0
LSB
Current input value when digital
output is +4000. Setting range is -20
mA~+20 mA (-4000
LSB
~ +4000
LSB
OFFSET:
output value is 0. Setting range is-16
mA ~+52 mA (-3200
LSB
~ +10400
LSB
GAIN-OFFSET: Setting range is +4mA ~ +32mA
(800
LSB
~ +6400
LSB
GAIN:
Explanation:
Read the data of model type from extension module K0 and distinguish if the data is H400
(DVP04AD-H model type).
If the model type is DVP04AD-H, M11 is on and the setting input mode is (CH1, CH3)= mode 0,
(CH2, CH4)= mode 3.
Set the number of times for average of CH1 and CH2 are K32.
Read the input signal average value of CH1~CH4 (4 data) and saved into D20~D23.
20mA
GAIN
-4000
current input
Using charts above to adjust A/D conversion characteristic curve of voltage input mode and
current input mode. Users can adjust conversion characteristic curve by changing OFFSET values
(CR#18~CR#21) and GAIN values (CR#24~CR#27) depend on application.
LSB(Least Significant Bit): 1. voltage input: 1
LSB
=10V/8000=1.25mV. 2. current input:
LSB
=20mA/4000=5µA.
API
RELATED INSTRUCTIONS EXPLANATION
78
FROM
Read special module
CR data
Applicable model
ES EP EH
CR #10
CR #9
Specified CR number
(Access16-bit if n=2, or 32-bit if n=1. Same controlled registers are accessed).
Specified device
D0
D1
D2
D3
D4
D5
Specified CR
CR #5
CR #6
CR #7
CR #8
CR #9
CR #10
Specified device Specified CR
D0
D1
D2
D3
D4
D5
CR #5
CR #6
CR #7
CR #8
CR #9
CR #10
5.2. Program Example for Adjusting A/D Conversion Characteristics Curve
Example 1: setting OFFSET value of CH1 to 0V(=K0
LSB
) and GAIN value of CH1 to 2.5V(=K2000
LSB
M1002
TO
TO
X0
TO
TO
K0
K0
K18
K24
K0
K2000
K1
K1
K0
K0
K1
K33
H0
H0
K1
K1
Writing H0 to CR#1 of analog
input module no. 0 and set CH1
to mode 0 (voltage input
-10V~+10V)
Writing H1 to CR#33 and allow to
adjust characters of CH1~CH4.
On, K0
LSB
be wrote in CR#18 and K2000
LSB
CR#24.
Bit device
Word device
X Y M S K H KnX KnY KnM KnS T C D E F
Continuous
Pulse
FROM
FROMP
m
execution
execution
m
n
Continuous
Pulse
DFROM
DFROMP
is 0~7.
execution
execution
: ES/EP:
Flag: When M1083=On, it allows to
0-48, EH: 0-254.
FROM/TO.
ES series model doesn’t support pulse
execution instruction (FROMP, DFROMP).
Command
Explanation
In ES series models, flag M1083 is not provided. When FROM/TO instruction is
executed, all interrupts (including external or internal interrupt subroutines) will be
disabled. All interrupts will be executed after completing FROM/TO instruction.
Besides, FROM/TO instruction also can be executed in the interrupt subroutine.
The function of the flag M1083 (FROM/TO mode exchange) provided in EP/EH
series models:
a.
When M1083=Off, all interrupts (including external or internal interrupt
subroutines) will be disabled when FROM/TO instruction is executed. The
Interrupts will resumed after FROM/TO instruction complete. Please be
advised FROM/TO instruction can be executed in the interrupt subroutine.
When M1083=On, if an interrupt enable occurs while FROM/TO
instruction are executing, the interrupt FROM/TO instruction will be
blocked till the requested interrupt finish. Unlike M1080 off situation,
FROM/TO instruction cannot be executed in the interrupt subroutine.
16-bit command when n=6
32-bit command when n=3
Example 2: setting OFFSET value of CH2 to 2mA(=K400
LSB
) and GAIN value of CH2 to 18 mA
(=K3600
LSB
: the number for special module.
: the number of CR (Control Register) of
special module that will be read.
: the location to save reading data.
: the
data number of reading one time.
DVP-series PLC uses this instruction to read CR data of special module.
: When assigning bit operand, K1~K4 are used for 16-bit and K5~K8 are used
for 32-bit.
Please refer the footnote below for the calculation of special module number.
To read the content of CR#24 of special module#0 to D0 of PLC and to read the
content of CR#25 of special module#0 to D1 of PLC. It can read 2 data in one time
(n=2).
b.
Program
Example